Earth Fault Tripping

06/26/2010 1:44 PM

Hello all. I'll be very grateful if you could answer my queries and clear my concepts in the process.

I work in an oil & gas plant as a Trainee Electrical engineer. The power source that we use is a Caterpillar's G3508 (SITA) 630KVA/505kW natural gas engine which runs at only 40-50% load, as our load is limited. The thing is that the genset frequently trips on "Earth Fault" as displayed by the generator PLC panel in the control room. According to my supervisor, this earth fault is due to the 1-phase loads that are unevenly distributed on the 3-phases of the generator. In other words, 'our load in unbalanced'. It is observed that when the there is some difference in the load between the three phases, the earth current rises!

For e.g. if the load b/w the three phases L1: L2: L3 is 220 A: 210 A: 230 A, the earth current is around 10A-40A (which is considered safe or OK). However, if the load on the three phases is 200 A: 250 A: 270A, the earth current rises to 70A and keeps increasing as the difference b/w the phases (load) increases. If it rises to 150A, the genset trips on 'Earth Fault' and plant shuts down. To prevent this we usually cut some load on the phase which is high and add some load on the phase which is low in order to decrease the difference b/w the phases, plus we water the earthing pit where the generators' neutral is connected.

What I don't understand is that:

1) Isn't the earth fault the fault that is caused when any phase or phases come in contact with the ground and a huge amount of current flows b/w the phase and the ground? If yes, then what kind of fault this really is??

2) When load is unbalanced, current flows from the load's star point (node) to the generator's star point (node) and from there, it is earthed. Right? If this is so, what harm would such a current do and to what, if we bypass this Earth Fault tripping safety? What if we leave it rising?

3) Our genset runs on 40-50% load since we have limited load. Running on half its capacity, shouldn't the genset be able to bear this fault?

4) This tripping also occurs when we are taking another genset (of same make, type and rating) online via synchronizing both. When the synchrocope needle centers, we cut the load from the previous genset (by opening its breaker) and at the same instance we put on-load the incoming genset (by closing its breaker). My Incharge says that this fast-action of cutting one genset and putting the other on-load at the same time prevents any earth current rise. Otherwise this action should normally be taken when the load is distributed equally (50%-50%) b/w the both gensets. Is this theory right?

5) Does watering the neutral's earth pit helps? Would adding a current limiter (inductor) on the neutral wire b/w the 2 nodes OR b/w the node and the earth (as shown in the diagram) help?

I would be extremely thankful if you could answer these problems (point-wise) that I'm facing. Thanks

Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Earth Fault Tripping

06/26/2010 11:03 PM

i feel that the unbalanced current flowing through the neutral is NOT an earth fault current, and is not unhealthy. The relay should not trip for any magnitude of this current up to its max rating. The output of the CT sensing the current in the neutral should not go to the EF relay. In fact, the CT should not be there. On the contrary, there should be a SUMMATION CT or CORE-BALANCE CT (CBCT) through which ALL three phases AND the neutral must pass. This way, under healthy conditions, the vector sum of all the currents is always zero, and the EF Relay will not act. In the event of an earth fault, the vector sum of the 4 currents is no longer zero, and that should cause the EF to trip.

For more information on this, please check out this superb paper from Schneider Electric:

schneider-electric ect114.pdf

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
2
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: Earth Fault Tripping

06/27/2010 12:56 AM

You have given a very good diagram at the end of your text, let us analyze it together as follows:

Any out of balance phase current has to go through the Neutral wire the same has been shown connected to the generator star point.

The current transformer for the earth fault relay has been installed on the distinctly seperate earth continuety conductor so it must remain unaffeted due to whatever is going through the Neutral wire during any of the described scenerios.

There can only be two reasons for the inadvertant trippng;

(1) Neutral conductor has been practically connected below the current transformer instead of above the CT at the star point as is in the diagram, thus out of balance currents in the Neutral are sensed by the CT causing relay to act (It is a common mistake).

(2) Neutral conductor of the plant is either broken or defective giving high impedence thus the imbalance current now follows through earth continuety conductor and the CT is sensing it.

Earth fault relay itself seems normal since you have tried two different gensets while watering the earth pit is meaningless in the state of described affairs.

____________________________________________

Sharing knowledge is a WIN-WIN situation

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#3
In reply to #2

Re: Earth Fault Tripping

06/27/2010 3:27 AM

GA.I was searching for the right words, I could not find them because you had already placed them here in the right order!!If his diagram is correct, it would appear to be missing an earth wire connecting the neutral point at the Generator, to any frames/housings of the equipment being supplied, via the earth in the supply cable.

I personally would NEVER work on a system with an earth return via "mother earth" as under the wrong circumstances this could allow the frame of a faulty equipment to become live and kill/injure anyone touching it.

Something like this:-

It would therefore appear that someone was saving money on cables....I get the impression (here at least) that some people take the term "Earth" a little too simply......maybe we should call it something else to identify it as being required....?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#4
In reply to #3

Re: Earth Fault Tripping

06/27/2010 5:11 AM

No Andy,

Protective earth wire could not be wired to the neutral point of generator, you are short-circuiting the earth-neutral resistor.

I agree an earth wire is missed but it should be wired to the neutral point of the star at load side, any current, including ground fault current, have to flow back to the reference point of the generator which is the neutral of the generator star connection.

in case of a ground fault the current will flow back through the earth wire to the neutral thru the resistor.

A CT should be installed there to detect it and trip the main breaker.

the neutral current resulti of an unbalance will not flow thru the resistor so there is no trip . Cheers

__________________
dont say it, write it
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Earth Fault Tripping

06/27/2010 7:38 AM

Hi Andy and Le Noble.

i have seen this in that paper from Schneider. It seems to be ok as per IEC to use one wire for Neutral and Earth (PEN)...please check this out, and if possible the ECT 114 also.

Rather than putting a CT on the Earth conductor, would it not be simpler (and more economical too) to use a CBCT ? i would welcome your views, thanks.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#6
In reply to #5

Re: Earth Fault Tripping

06/27/2010 1:38 PM

Yes it is ok for PEN arrangement, but it is not the case elaborated by the OP, he does have an IT arrangement, so the PE should be connected the the earth side of the resistor ( as shown in schneider document) not to star neutral point as Andy suggested.

A CBCT can detect a non zero vectorial sum of the 3 currents, but it may trip in case of unbalance occure or single phase loading, a resisor in the neutral-earth link will reduce also the fault current, the CT installed in this link is not sensible to unbalance

B/R

__________________
dont say it, write it
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Earth Fault Tripping

06/27/2010 11:33 PM

The CBCT must encompass all four wires...then, unbalance will not trigger the RCBO/RCCB.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#8
In reply to #7

Re: Earth Fault Tripping

06/27/2010 11:45 PM

but it still not limit the fault current,

as shown in the diagram, there is resistor connecting the generator neutral to the earth, the purpose of this resistor is to limit the fault current

__________________
dont say it, write it
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Earth Fault Tripping

06/27/2010 11:49 PM

Oh, earth fault vs earth leakage....ok. Thanks.

Anyway, coming to the op's issuem he needs to put that neutral CT somewhere else, to prevent nuisance tripping.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#10
In reply to #9

Re: Earth Fault Tripping

06/27/2010 11:58 PM

I agree. the CT is misplaced, it should be installed somewhere between earth pit and generator star node..

__________________
dont say it, write it
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#13
In reply to #8

Re: Earth Fault Tripping

06/28/2010 11:44 AM

In Europe, I do believe that we are limited to having a max of 1 ohm resistance from earth to neutral. I have not heard that this has been changed.....

Someone who knows the European codes better than I should chime in here please......

I am very surprised to hear that some countries put resistors in the earth/neutral path.......to reduce fault current!

Surely one needs ANY earth fault to blow fuses for safety reasons....

Of course, if an ELCB is installed, then one can detect a minor short far better and quicker and safer, but nobody mentioned having an ELCB as far as I remember....here I have ELCBs and a neutral/earth link connection only in my house.

From the substation I only get 3 phases and neutral......no earth. It looks something like this as far as I remember:-

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#12
In reply to #4

Re: Earth Fault Tripping

06/28/2010 11:23 AM

Not here in Europe at least, no resistor and a link is to be made at the substation between earth and neutral AND ONLY THERE. NOWHERE ELSE.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Earth Fault Tripping

06/28/2010 3:32 AM

Neutral is there to carry the imbalance current between the three phases.

Earth is the protective conductor, intended to operate the circuit protective device(s) in the event of a fualt occurring.

If the earth fault detector is operating, then there is current in the earth conductor in excess of the trip current setting. Find out where it is coming from and fix it! Get the Megger out and use it!!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14
In reply to #11

Re: Earth Fault Tripping

06/28/2010 11:47 AM

GA from me...

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#15
In reply to #11

Re: Earth Fault Tripping

06/28/2010 12:00 PM

There seems to be NO earth current. To quote the OP...

For e.g. if the load b/w the three phases L1: L2: L3 is 220 A: 210 A: 230 A, the earth current is around 10A-40A (which is considered safe or OK). However, if the load on the three phases is 200 A: 250 A: 270A, the earth current rises to 70A and keeps increasing as the difference b/w the phases (load) increases. If it rises to 150A, the genset trips on 'Earth Fault' and plant shuts down. To prevent this we usually cut some load on the phase which is high and add some load on the phase which is low in order to decrease the difference b/w the phases, plus we water the earthing pit where the generators' neutral is connected

Seems to be a case of wrong wiring...the CT on the neutral (need not have been there actually) is wired to trip the EF relay...naturally it is sensing unbalance and tripping ... all he has to do is to relocate the neutral CT to sense the EF current.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#16
In reply to #15

Re: Earth Fault Tripping

06/28/2010 11:13 PM

KVSRHIDAR,

I agree with you, there is NO FAULT

This assembly is done by caterpillar as understood from OP, and there is little chances to be done wrongly, I dont think Caterpillar misplaced the CT-dispite what a said before- and not clear from the OP that there is a CT, may be y are using another arrangement, if it is an Holgrem connection to detect the earth current, sure it will sensitive to big unbalanced current

If the original poster is still following the discussion, please to send more information if there is neutral CT and how it is connected

B/R

__________________
dont say it, write it
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#18
In reply to #16

Re: Earth Fault Tripping

06/28/2010 11:20 PM

Yes, you are quite right that the neutral CT would be correctly wired if done by Cat. i think therefore that the wiring of the single phase loads (which the user would have to do) may have ignored some conventions. For example the housing of an appliance may have been connected to the neutral rather than being earthed ? As you say, the OP needs to come back and tell us more.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#19
In reply to #18

Re: Earth Fault Tripping

06/28/2010 11:28 PM

Yes , it could be,

people some time connect their loads to PE in place of Neutral wire, especially if done by unqualified persons, and this will be seen as a earth current.

But the OP talks about a Oil and Gas plant, they should follow the highest standards...

OP should come back, or let the Admin close this discussion

__________________
dont say it, write it
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#17
In reply to #11

Re: Earth Fault Tripping

06/28/2010 11:19 PM

Good explanation, you Got a GA vote!! Thanks to Andy!!

But the OP is clear, they do have trip when they have current unbalance more than 25%.... there is NO EARTH FAULT and the megger will not find anything....

The problem is that the normal neutral current is seen by earth fault detection circuit where it should not...

we were guessing about neutral CT, but unless the OP elaborate more how the fault detection circuit is wired, we can do nothing but guessing

__________________
dont say it, write it
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20

Re: Earth Fault Tripping

06/29/2010 3:59 AM

Has the earth fault gone yet?

What were the Megger insulation test readings?

Which item was causing the earth fault and has it been replaced yet?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#21
In reply to #20

Re: Earth Fault Tripping

06/29/2010 12:16 PM

This is an interesting thread. Finally, I took my time to read it – lot of good comments here. Let me add few more.

Some concerns:

(1) In the drawing, the OP showed two CT's – one in neutral and another one in grounding (earthing) but he didn't mention which one feed to the ground (earthing) fault protection.

(2) The OP showed the generator grounding but it is not clear that it is solidly grounding or Low Resistance Grounding (LRG) or High Resistance Grounding (HRG)

(3) OP didn't mention the type of earth fault device

It is already clearly pointed out by other participants that the unbalance current flowing through the neutral and ground fault current flowing through the ground wire is different. The ground fault device should trip only when the ground fault current flows through the ground system, not because of the unbalance current flowing through the neutral.

Now come to the answers to the OP's points:

(1) Yes but the magnitude of the earth fault current depends on the grounding system (solidly or LRG or HRG)

(2) This concept is wrong – as it is already pointed (in above bold text) out the load unbalance current and the earth fault current are not same.

(3) Earth fault current setting and its tripping doesn't relate to the generator loading. If there is an earth fault, it should trip even if the generator runs at no load.

(4) This is also a wrong concept. There should not be any effect on earth fault how the generators are synchronized.

(5) There shouldn't be any effect on earthing system if the earth pit is watered. If it does, the earthing is not done properly and the system is in danger.

Suggestions:

It seems to me, people around you are having the wrong concepts and I would suggest hiring good electrical consulting engineer for the thorough checking of the system and find the proper reason of the trip.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#22
In reply to #21

Re: Earth Fault Tripping

06/30/2010 2:08 AM

That is a good post with a lot of common sense.....thanks.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (5); kvsridhar (6); Le_Noble (7); mountk2 (1); msamad (1); PWSlack (2)

Previous in Forum: Current Carrying Capacity of Solid Bus Bar   Next in Forum: Electrical Q

Advertisement