Hello all. I'll be very grateful if you could answer my queries and clear my concepts in the process.
I work in an oil & gas plant as a Trainee Electrical engineer. The power source that we use is a Caterpillar's G3508 (SITA) 630KVA/505kW natural gas engine which runs at only 40-50% load, as our load is limited. The thing is that the genset frequently trips on "Earth Fault" as displayed by the generator PLC panel in the control room. According to my supervisor, this earth fault is due to the 1-phase loads that are unevenly distributed on the 3-phases of the generator. In other words, 'our load in unbalanced'. It is observed that when the there is some difference in the load between the three phases, the earth current rises!
For e.g. if the load b/w the three phases L1: L2: L3 is 220 A: 210 A: 230 A, the earth current is around 10A-40A (which is considered safe or OK). However, if the load on the three phases is 200 A: 250 A: 270A, the earth current rises to 70A and keeps increasing as the difference b/w the phases (load) increases. If it rises to 150A, the genset trips on 'Earth Fault' and plant shuts down. To prevent this we usually cut some load on the phase which is high and add some load on the phase which is low in order to decrease the difference b/w the phases, plus we water the earthing pit where the generators' neutral is connected.
What I don't understand is that:
1) Isn't the earth fault the fault that is caused when any phase or phases come in contact with the ground and a huge amount of current flows b/w the phase and the ground? If yes, then what kind of fault this really is??
2) When load is unbalanced, current flows from the load's star point (node) to the generator's star point (node) and from there, it is earthed. Right? If this is so, what harm would such a current do and to what, if we bypass this Earth Fault tripping safety? What if we leave it rising?
3) Our genset runs on 40-50% load since we have limited load. Running on half its capacity, shouldn't the genset be able to bear this fault?
4) This tripping also occurs when we are taking another genset (of same make, type and rating) online via synchronizing both. When the synchrocope needle centers, we cut the load from the previous genset (by opening its breaker) and at the same instance we put on-load the incoming genset (by closing its breaker). My Incharge says that this fast-action of cutting one genset and putting the other on-load at the same time prevents any earth current rise. Otherwise this action should normally be taken when the load is distributed equally (50%-50%) b/w the both gensets. Is this theory right?
5) Does watering the neutral's earth pit helps? Would adding a current limiter (inductor) on the neutral wire b/w the 2 nodes OR b/w the node and the earth (as shown in the diagram) help?

I would be extremely thankful if you could answer these problems (point-wise) that I'm facing. Thanks