We have an Induction motor (7 KW, 400 V, 50 Hz, Delta, 15.5 A, P.F 0.75, 1465 RPM ) driving a conveyor belt. Motor is connected to the VFD ( ACS-800-01-0016-3, 8.1 KW, 3 X 400 VAC, 12 A, 50 Hz). Some values taken from the LCD of VFD at different times at different load
Power (in Percentage) Current (A), Frequency(Hz),Speed ( RPM)
1. 25.57 %, 13.24 A, 28.49 Hz, 857 RPM
2. 29.21 %, 12.72 A, 32.79 Hz, 966.6 RPM
3. 31.22 %, 13.08 A, 34.95 Hz, 1031.1 RPM
4. 34.88 %, 13.20 A, 39.25 Hz, 1160.0 RPM
How the Power (%) is being calculated by the drive in the above four reading?
Drive name plate shows 12 A, but on Display panel we have current 13 A. Is it due to Delta connection?
What will be my V/f ratio in this 7 KW motor case?Is it will be fix or have some range?
Often we observe that low power rating motors when operated under no load condition they consume 30-40 % of the rated Power but here why power is below 30-40 % even at loaded conditions?
if I assume V/f ratio to be 8 (400/50). then at 13.24 A, Voltage will be equal to 228 V ( V= 28.49*8 = 228 V) and P = 1.732*228*13.24*0.75*0.9173 = 3.6 KW which is 51 % of 7 KW.
Kindly help me in understanding this LCD display information of ACS 800