How many 2 ton AC does a 125kva gen. Set can power?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: AC With 125kva DG

06/30/2010 9:13 AM

Power can set. gen 125kva a does AC ton 2 many how.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #1

Re: AC With 125kva DG

07/01/2010 9:21 AM

Window the in doggie that is much how?

Tail waggly the with one the.....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Off Topic (Score 5)
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#5
In reply to #1

Re: AC With 125kva DG

07/01/2010 9:26 AM

Master Yoda!!!! Shame on you!!!! You keep reprimanding me for playing pranks on people and now you're mocking someone else's English when your's is no better!!!!

__________________
If only you knew the power of the Dark Side of the Force
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: AC With 125kva DG

01/24/2023 9:59 AM

A prosecution for the third apostrophe is not out of the question...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Off Topic (Score 5)
Associate

Join Date: Dec 2007
Location: Kochi, Kerala, India
Posts: 27
#2

Re: AC With 125kva DG

06/30/2010 9:50 AM

Usually Generator will deliver maximum efficiency at 0.8 Load Power Factor. The design of the generator should be such a way that, it must carry 20% over load. So, the Generator can carry 125 x 0.8 x 1.2 = 120kW

You refer the AC manufacturer's Literature and find the kW rating of the AC unit. Usually 1ton is taken as 1.25kW. I don't know, whether in your side it is correct. Then, you count the number of units to reach 120kW

__________________
Assistant Electrical Inspector, Govt. of Kerala, India
Reply Score 1 for Good Answer
Anonymous Poster
#3
In reply to #2

Re: AC With 125kva DG

06/30/2010 8:38 PM

Thank you sir i am a B.Tech fresher from kerala.

Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); DVader1000 (1); PWSlack (2); user-deleted-1098 (1)