Earthing Without Salt, Cu, Coal

06/30/2010 7:59 AM

Can any scholar tell me how could someone earth without copper, coal, salt its a question asked by my friend.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Earthing without salt,cu,coal

06/30/2010 8:10 AM

It's difficult to earth without first having solar systemed.

Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#2

Re: Earthing without salt,cu,coal

06/30/2010 8:25 AM

Dear all,

If the question is how to make earth electrode without copper, coal, salt, you can use underground steel pipe or reinforcing bars of a concrete foundation as earthing electrodes.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #2

Re: Earthing without salt,cu,coal

07/01/2010 9:16 AM

Nooooooo - not under BS7671!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#3

Re: Earthing without salt,cu,coal

06/30/2010 8:26 AM

I think connecting to any other devices previously earthed can solve your problem.Use low resistance conductors like aluminum if copper is not available.:-)

Reply
Anonymous Poster
#4

Re: Earthing without salt,cu,coal

06/30/2010 8:43 AM

Foxes seem to manage.

___________________

69

Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#5

Re: Earthing Without Salt, Cu, Coal

06/30/2010 1:02 PM

It can be a single wire or mesh of G.I. wires (galvanized iron) burried direct in soil about one meter deep and augumented with G.I. earth rods/plates at corners and some other prime locations if required.

copper, coal, salt is not mandatory at all.

BS7430 gives formulas for the calculation and detail design.

Practically in large electrical projects horizontal wire mesh electrodes (usually copper wire without coal and salt) are extensively exercised.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#6

Re: Earthing Without Salt, Cu, Coal

06/30/2010 1:09 PM

If you are asking about grounding to earth, I can't imagine why you mentioned coal. There are a number of references in Google including this one:

http://whatis.techtarget.com/definition/0,,sid9_gci861575,00.html

If that is not what you meant, then please rephrase your question.

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #6

Re: Earthing Without Salt, Cu, Coal

06/30/2010 3:31 PM

Coal, carbon and other exotic backfill materials are used in certain situations like substation earth grids when the substation is built on solid (very poor conductor) rock. It is not the sort of thing you come across every day (and depends on local standards) but I know of at least one remote substation site done like this in New Zealand. As a side note the earth pits had watering systems to keep them moist and so the earth resistance low.

__________________
jack of all trades
Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#7

Re: Earthing Without Salt, Cu, Coal

06/30/2010 1:48 PM

The OP can use domestic water pipe in his house as an earth, no need to worry about cu, salt and coal.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9

Re: Earthing Without Salt, Cu, Coal

06/30/2010 3:32 PM

It depends on the application. Can you please elaborate as your original question is unclear.

__________________
jack of all trades
Reply
Member

Join Date: Oct 2012
Posts: 9
#13
In reply to #9

Re: Earthing Without Salt, Cu, Coal

10/10/2012 6:11 AM

The ACTUAL QUESTION: since the dry earth resistance here is really high, we are required to make an earth pit with SALT & charcoal. except there is no coal available. salt takes long to come by. what is the solution if i have already put an earth mat?

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#14
In reply to #13

Re: Earthing Without Salt, Cu, Coal

10/10/2012 2:36 PM

Well you don't have to use salt and charcoal (unless the local standards specifically specify it), there are other earthing pit backfill materials available - for example

Link 1

etc. However these are most likely going to take longer to obtain than salt or coal (and be more expensive).

You may be able to get by temporally with some sort of 'wet' earth solution where you set up a system to constantly ensure the ground in and around the earth is wet (to reduce the resistance), but there is no guarantee that this will work or be electrically safe.

__________________
jack of all trades
Reply
Member

Join Date: Oct 2012
Posts: 9
#15
In reply to #14

Re: Earthing Without Salt, Cu, Coal

10/10/2012 3:47 PM

the earth resistance here, on average is greater than 60. Following your idea, i'm thinking of going deeper with a pipe alongside. Do you think it will hold for a few days?

Thanks for the quick reply

Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#16
In reply to #15

Re: Earthing Without Salt, Cu, Coal

10/10/2012 6:41 PM

Please don't confuse coal and charcoal, which has little, if anything, to do with coal.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#17
In reply to #16

Re: Earthing Without Salt, Cu, Coal

10/10/2012 8:13 PM

Good spotting, I missed that single mention of charcoal.

__________________
jack of all trades
Reply Off Topic (Score 5)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#18
In reply to #15

Re: Earthing Without Salt, Cu, Coal

10/10/2012 8:18 PM

Possibly, if you are careful and make sure the ground doesn't dry out.

A second temporary pit (or more) connected in parallel may also be a good idea to consider to help reduce the risk of possible electrocution or equipment damage further.

__________________
jack of all trades
Reply
Member

Join Date: Oct 2012
Posts: 9
#19
In reply to #18

Re: Earthing Without Salt, Cu, Coal

10/11/2012 6:39 AM

now thats more like it. Thanks, simple yet effective.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10

Re: Earthing Without Salt, Cu, Coal

06/30/2010 6:31 PM

I have done it with urine, but that counts as salt I suppose.

Back story: Diesel generator set high in the mountains being used to run a mobile rock crushing plant. The VFD in the feeder would not operate without a ground reference, but the earth was so dry and rocky we couldn't get ground continuity. So I had the backhoe operator dig a pit, I attached the ground cable to a steel plate and threw it in, then had everyone pee into the pit. Worked like a charm.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Earthing Without Salt, Cu, Coal

07/01/2010 9:18 AM

Well, one possibility is to wire it to the largest pin, the earth pin, of a BS1363 13A plug, and insert the plug in a domestic 13A socket.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 19 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (1); Anonymous Poster (2); hithuanand (1); jack of all trades (5); JohnDG (1); JRaef (1); mountk2 (2); polarcamel (3); PWSlack (2); StandardsGuy (1)