What are all the points to be checked in the basic design description of DCS?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Mar 2010
Posts: 50
#1

Re: DCS

07/06/2010 2:47 AM

Dear ,

You have to check first how much the IO points or tags should your DCS handle?

How many cards do u require for DI, DO, AI and AO. may be there are some relay outputs so these have to be considered too.

Then you will send all these details to vendor who will give you his own specifications of DCS. For Example, CPU, cards, power consumption, cabinet style and their installation etc.

Reply
Anonymous Poster
#2
In reply to #1

Re: DCS

07/06/2010 3:13 AM

The document contains basic description of the DCS system hardware, software and some main function, not a complete DCS specification... I have to review the same.. can you help me

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: DCS

07/06/2010 4:50 AM

Has the vendor been issued with an I/O list and a drawing showing the overall system high-level architecture?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#5
In reply to #3

Re: DCS

07/06/2010 6:44 AM

I/O list & drawings were not enclosed with the document. Its a 15 page brief description

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: DCS

07/08/2010 4:26 AM

Well, for a fuller proposal and as a basis for evaluation, send the vendor the above documents!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#4

Re: DCS

07/06/2010 6:20 AM

Compare with Clients /Companys Functional Specification Document (FSD)

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #4

Re: DCS

07/08/2010 4:28 AM

This document is only really needed to begin the programming. The original poster is currently upstream from that point.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply