Deatection of Neutral Missing

07/07/2010 2:12 AM

Please let us know how to detect the neutral wire missing in a 3 phase balanced and unbalanced load.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#1

Re: Deatection of Neutral missing

07/07/2010 2:43 AM

Switch off some single phase loads like lighting from one of the phases, use a v meter between neutral and ground.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
2
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#2

Re: Deatection of Neutral Missing

07/08/2010 1:32 AM

The Question should be very specific as what is exactly required, because neutral missing in a balanced or unbalanced load means, the load is an industrial equipment.

Since neutral missing in a domestic usage is no meaning as if it is missing no single phase equipment works.

Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5
In reply to #2

Re: Deatection of Neutral Missing

07/08/2010 2:48 PM

GA for a good common sense (and accurate!) answer......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Deatection of Neutral Missing

07/08/2010 3:14 AM

Connect a single-phase load between one of the phases and neutral. If the load does not operate, then neutral is disconnected between the supply and the load point.

"Simples! ξ"

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4

Re: Deatection of Neutral Missing

07/08/2010 5:42 AM

Missing neutral? From Where? You can't find the neutral wire or there is none connected ?

really, your question is unanswerable unless by someone with the same kind of environment logic!!?

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

amarnath.sn (1); Andy Germany (1); LAA_Lucke (1); mountk2 (1); PWSlack (1)

Previous in Forum: Instrument and Electrical Earth Bars   Next in Forum: VFD Motor

Advertisement