Conversion

07/07/2010 9:36 AM

Dear All HVAC expert here,

Canyou help me convert the Cooling KW to Electrical Power KW? Our Supplier is selling us a Chiller (4 units) with 1000 KW capacity each. I want to convert it to electrical KW so that I can decide the Size of ACB & cables including Transformer to supply those Chillers. My power supply is 3 phase, 380 volts, 60 Hertz.

I initially size it to 4000 KW but my friend told that is cooling KW. the Power Kw is lesser. but he dont know the convertion too.

Thanks to all

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Conversion

07/07/2010 10:53 AM

Very roughly, each chiller will use about 300 kw, or 1200 kw total. A real calculation would depend on the refrigerant and its evaporating and condensing temperatures. Even better for your instance is to get the electrical ratings from the chiller supplier. They should have a data sheet with motor size (hp or kw), voltage, and amperage.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#3
In reply to #1

Re: Conversion

07/08/2010 1:51 AM

thanks! our supplier is from Belgium. We are oly dealing with our Consultant frm Belgium too. They informed us of Cooling KW to prepare the power rquirements.

Register to Reply
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#2

Re: Conversion

07/08/2010 12:29 AM

The electrical load will depend upon the efficiency of the cooling system. Typically 1kW elec power gives 3kW of cooling.

The only way to really know is to ask the manufacturer. Then size the cables to get the permissible voltage drop as specified by the local supply authority.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Register to Reply
Anonymous Poster
#4
In reply to #2

Re: Conversion

07/08/2010 1:59 AM

thanks. our supplier is from belgium. our consultant sent us this info and they are in belgium too. we are only preparing fo power rquirement. one manufacturer here locally told me it is 3.5 kw cooling to 1 kw power. but the conversion sent to us by our consultant dont tally with this conversion factor. 1300 kw cooling he computed to 540 kw electrical power. i think 1 kw to 3 is nearer x effeciency.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#5
In reply to #4

Re: Conversion

07/08/2010 5:23 AM

As a rule of thumb, and considering that you are using pumps etc ,

your best guess will be half the coolink capacity: 1kw cooling will definitely be more confortable with 0.5kW electric. The efficiencies and auxiliaries will prove that it could be nearer for your comfort.

At best, the manufacturer will have to give you the required electric power required per chiller and the auxiliaries... don't forget.

Register to Reply
2
Associate

Join Date: Dec 2007
Posts: 42
Good Answers: 1
#6

Re: Conversion

07/08/2010 8:18 AM
  • 1 TR = 3.517KW.(Total 1300KW, TR=1300/3.517=370)
  • TR is Ton of Refrigeration.
  • This may be cooling or Heating capacity not Electrical KW.
  • Say if the Chiller is Air Cooled For 1 TR it will consume around 1.5KW electrical.
  • Say if the Chiller is Water Cooled For 1 TR it will consume around 1KW electrical.
  • Air Cooled Chiller means 370x1.5=555KW
  • Water Cooled Chiller means 370x1=370KW
  • Better we can get from manufactures
Register to Reply Good Answer (Score 2)
Associate

Join Date: Nov 2009
Posts: 42
#7
In reply to #6

Re: Conversion

07/08/2010 10:42 AM

thanks sir, good information.

i dont knew the manufacturer yet. we are in Saudi and it's our consultant which in contact withthe manufacturer. my job is to prepare for power supply. i only want to knew where he got this 540 kw electrical power required for his chiller with 1300 kw capacity. i also wanted to know if their is a standard conversion factor for cooling KW to electrical power KW,

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8
In reply to #7

Re: Conversion

07/09/2010 7:34 PM

There is no standard conversion ratio for this.

It all depends on the efficiency of the whole chiller system including pumps and Fans etc. Every manufacturer will be slightly different.

I have already given you a good rule of thumb to be on the safe side. It also matches the #6 (instead of 1.5kW per ton of refrigeration, I would take 1.8 kW which is equivalent to dividing the cooling kW by 2 to get the electric kW).

Still I insist: if you want to be very accurate you must check with the manufacturer. The rule to divide by 2 will give you the best security to avoid under estimating the requirement and is the most safe.

Good luck

(by the way, 1TR = 12,000 BTU/h = 12,667 kJ/h = 3.518 kW cooling power which I recommend to divide by 2 = 1.76 kW electric power if you have no other info from the manufacturer of the package and you might need to add circulating pumps etc..?)

Register to Reply Score 1 for Good Answer
Associate

Join Date: Nov 2009
Posts: 42
#9
In reply to #8

Re: Conversion

07/10/2010 2:02 AM

Dear Mr. LAA,

Now I got it. Our consultant use the 2 in conversion.

Thanks a lot.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #9

Re: Conversion

07/10/2010 5:01 AM

You are welcome.

Register to Reply
Member

Join Date: May 2010
Location: Kuala Lumpur
Posts: 5
#11

Re: Conversion

07/17/2010 5:10 AM

You need to find out what is the COP ( Coefficient of Performance ) of the chiller unit.

Typical figures range from 2 - 3.5 and depending on the type of chiller unit ( vane, centrifugal, reciprocating, absorption).

Once you have the typical COP, take the chiller capacity ( kw) and divide by the COP and that gives you the absorbed power in electrical kw into the chiller compressor.

Hope that helps

Register to Reply Score 1 for Good Answer
Associate

Join Date: Nov 2009
Posts: 42
#12
In reply to #11

Re: Conversion

07/17/2010 8:14 AM

Thanks Sir, Now it is more clearer to me. Most probably we will use the vane type. We dont received yet the Chiller manual hence we are still negotiating with our prospective supplier.

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Dalton (3); deekay (1); ffej (1); LAA_Lucke (3); maglak (1); Tornado (1)