Wall Thickness

07/07/2010 10:52 AM

Dear all,

I am designing a piping for a fire water system using the API 5L GR B, the wall thickness according to ASME B31.3 is 4.39mm, so can I opt for the nearest thickness which is 4.4mm, or should I go to the schedule 40 (STD)?

Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Jul 2010
Posts: 3
#1

Re: Wall Thickness

07/07/2010 12:32 PM

which NPS you have ?

Register to Reply
Commentator

Join Date: May 2009
Location: UAE
Posts: 80
Good Answers: 3
#2
In reply to #1

Re: Wall Thickness

07/07/2010 12:57 PM

make sure to consider corrosion allowance & mill tolerance in your calculations

__________________
RK
Register to Reply
Member

Join Date: Jul 2010
Posts: 6
#3

Re: Wall Thickness

07/07/2010 2:16 PM

It's 6 inch.

The corrosion allowance and the mill tolerance, are included.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Wall Thickness

07/07/2010 2:50 PM

If each alternative satisfies the specifications, then it makes sense to use the most economical. The Sch 40 might be heavier than you need, but it might cost less as a more commonly available size.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator
Engineering Fields - Piping Design Engineering - New Member

Join Date: Apr 2010
Posts: 66
Good Answers: 1
#5

Re: Wall Thickness

07/08/2010 12:34 AM

It's better adopting the standard sizes available. Go for 6" SCh. 40

Regards,

Ashfaq Anwer

http://thepetrostreet.com

Register to Reply
Anonymous Poster
#6

Re: Wall Thickness

07/08/2010 12:35 AM

Does the wall thickness calcualted by you includes the corrosion allowance and 12.5% mill tolerance.

If the above discussed has been included in your calculations then go for the schedule just immediatly high from your calculated thickness that is available in the market.

This is the engineering practice which is normally followed.

Best Regards

Ikram Ali Khan

Register to Reply
Guru

Join Date: Oct 2007
Location: Tulare, CA
Posts: 1783
Good Answers: 35
#7

Re: Wall Thickness

07/08/2010 9:23 AM

Pipe has a pretty good tolerance allowance.

4.39mm and 4.4mm is pretty much the same thing. I would assume that the 4.4mm is just the 4.39mm rounded up. You should be able to use 6" STD Black pipe.

__________________
Why is there never enough time to do it right the first time but always enough time to do it over?
Register to Reply
Member

Join Date: Jul 2010
Posts: 6
#8

Re: Wall Thickness

07/08/2010 10:47 AM

But why are you chosing the STD whitch is at 7.1mm wall thickness, however there is five wall thicknesses(4.4, 4.8, 5.2, 5.6, 6.4mm) before this STD.

Register to Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#9

Re: Wall Thickness

07/08/2010 11:18 AM

You can use the thickness which covers the min. required per code, taking into consideration the corrosion and erosion allowances. For more details, see a solved examples through the following CR4 Threads:

In service pipe thickness limits (Post #4),

Schedule of pipe,

Maximum Wall Thickness for Seamless Pipe,

Pipe minimum allowable thickness,

Significance of "-Mill Tolerance" in the Piping Stress Analysis &

Pipe Wall Thickness.

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply
Associate

Join Date: Jun 2008
Location: India,Pune
Posts: 46
Good Answers: 1
#10

Re: Wall Thickness

07/11/2010 7:21 AM

sir,

as the pressure is low enough, you can use the designed pipe. In this application you can use it without further calculations.

kiran

__________________
if you are a managment professional or youth who wants to start business contact for free help for your project including financial assistance through NGO in and around Pune India
Register to Reply
Member

Join Date: Jul 2010
Posts: 6
#11

Re: Wall Thickness

07/11/2010 9:39 AM

Thank you guys for your answers,

I think I'll opt for (4.8mm), whitch satisfied the requirment of the code, and be cheapper than the STD wall.

Any comment?