Anonymous Poster

AB PLC 5 Source Or Sink

07/07/2010 10:28 PM

This could be simple question but would like to get clarity for my information.

We have AB PLC with standard instrument/transmitter to be either 2 wire (loop powered) or 4 wire. How is source and sinking works on this?

My real question is another instrument we have to use is 3 wire only with selection on the transmitter as source or sink. The 3wire transmitter supplier told me that it is the same as 4wire by simply getting back the oV as common to make it 4wire as were use to for our Differential Analogue input card.

Hope to hear explanation on this.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#1

Re: AB PLC 5 Source Or Sink

07/08/2010 12:08 AM

4-20mA signals are definitely "active" or "passive". Us analog guys have trouble thinking of them as sourcing or sinking.

Active 4-20mA signals are powered from an internal power supply in the device. Connect a load to an active output and the current flows. Active devices are 4 wire devices; 2 wires for power, 2 wires for the 4-20mA signal. Some people consider an active 4-20mA output to be a sourcing signal, because the 4-20mA signal requires no external power supply and the current flows as soon as a continuity in the loop is established. This is very typically an output on a chemical analyzer.

Passive 4-20mA signals are powered by an external power supply in series in the loop circuit, using the signal wires for power wires. Without an external power supply in the loop wiring, no signal is available from the transmitter.

This is done to avoid running more than 2 wires over long distances and to avoid ground loop problems that can occur when the ground for the power supply in a 3 or 4 wire device is at a different ground potential than the receiver device.

A loop powered 2 wire transmitter might be called a sinking device since it controls the current signal but that's sort of a stretch for a definition.

Could a receiver device with a 4-20mA input, like a panel meter, recorder or PLC AI be called a sinking device, because it consumes voltage in the loop? Pretty weak . . .

Here's graphic of the 3 types of wiring, 2 wire, 3 wire and 4 wire:

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: AB PLC 5 Source Or Sink

07/08/2010 4:06 AM

.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#5
In reply to #1

Re: AB PLC 5 Source Or Sink

07/17/2010 6:49 AM

differntiate properly between active & passive sink & sourcing signal 2 wire & 4 wire tx

Reply
Anonymous Poster
#3

Re: AB PLC 5 Source Or Sink

07/08/2010 6:53 PM

Thanks for the informative response.

This gives me better understanding how active and passive works.

For simplicity per your explanation 4 wire is active while 2 wire is passive, which from my original question as the 3 wire instrument has a selection (dip switch), I should select sourcing (active).

Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#4

Re: AB PLC 5 Source Or Sink

07/08/2010 7:50 PM

There's no pat answer. Wiring is specific to the AI card and the field device.

What brand and model field instrument? Link to its manual with power requirements and a wiring diagram: www. ? ?

Which model A-B analog input card? 17__-____ ? ? ? ? ?

What other kinds of field devices are connected to the A-B input card? 2 wire transmitters on the same power supply?

Can the power supply for existing field devices support yet another field device?

Reply