Derating Factor

07/08/2010 2:54 PM

what is the grouping factor value for a 4 core cable from the transformer to the MDB?

ambient temp. factor if it is buried "underground"?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#1

Re: Derating Factor

07/08/2010 3:06 PM

According to NEC-2008,
If more than three current carrying conductors are installed in a raceway or in a cable for a distance greater than 24 in or 600mm the allowable ampacity of such conductors shall be derated by the factors listed in artical 310.15(B)(2)(a) and Table 310.15(B)(2)(a).

conductors in ambient temperatures, exceeding 86 F are required to be derated according to the correction factor of table 310.16. The derating factors are in the ampacity correction factor chart below table 310.16 and are selected based on the ambient temperature srrounding the conductors and based on the type of insulation and the correction factors are based on the material, insulation and size of the conductors utilized.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Derating Factor

07/09/2010 3:39 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Derating Factor

07/09/2010 7:47 AM

It depends upon the depth of burial, soil temperature, thermal conductivity of soil, grouping factors, etc. Better to refer to the cable manufacturer's catalogues for these de-rating factors and arrive at the net-derating factor.

Register to Reply