Frequent Tripping of 30kW Motor

07/13/2010 4:47 AM

These is a motor of rating 30kW, FLC=50A connected to a DOL. This motor is connected to facility to transfer spent caustic to through a 6'' line . The pump is a vertical pump. There is a standby for the subject motor , which is of the same kW rating. Recently the motor is found to tripp very often.

The following checks were conducted for the motor:

a. No-Load test ( recorded 30% of FLC)

b.L-R values of the motor.( found OK and within acceptable limits)

c.Meggar value of the connected cable. (OK)

d. Continuity of the starter panel wiring ( OK)

e. Load current being drawn is found to be 38Amps at a discharge rate of 9 kG /m2& stand by pump is 23 Amp at 7 kG/m2.

Mechanical:

The pump is tested for vibration , free movement etc and found OK.

Still, the subject motor is tripping. Iam suspecting any choking of the discharge line of the motor. Please advice.

Pratap

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: May 2010
Posts: 10
#1

Re: Frequent tripping of 30kW motor.

07/13/2010 5:30 AM

Is any protection relay provided for the motor. In such case pl. provide the setting details.

Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 15
#5
In reply to #1

Re: Frequent tripping of 30kW motor.

07/13/2010 7:52 AM

this is a old starter, the BMR is set at 44 amps-trip.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #5

Re: Frequent tripping of 30kW motor.

07/14/2010 3:51 AM

If the motor full-load current of the motor is 50A, why is the trip set to only 44A?

What is the supply voltage?

What is the rise in pressure across the pump?

What is the volumetric flowrate through the pump?

<subscribes to discussion>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#16
In reply to #11

Re: Frequent tripping of 30kW motor.

07/14/2010 5:53 AM

Setting of trip at 95% is a general practice here, it shall go up to 105%. Motor can withstand up to how much percentage of the FLC for LT < 160kW and HT upto 3MW ?

Supply Voltage:415+/-5.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#24
In reply to #16

Re: Frequent tripping of 30kW motor.

07/15/2010 2:37 AM

<...it shall go up to 105%...>

Not recommended.

Set the motor overload device to the same full load current as is stated on the motor rating plate, otherwise there is a risk of the motor becoming damaged and unusable due to overheating. Manufacturers do put these things on their ratings plates for a reason!

In the original poster's case, the trip current needs to be 50A. The question as to why it is set to only 44A remains unanswered at this point, as do several other questions that, when answered, would enable the forum to advise quickly.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Power-User

Join Date: Nov 2009
Posts: 296
Good Answers: 27
#2

Re: Frequent tripping of 30kW motor.

07/13/2010 5:43 AM

"Iam suspecting any choking of the discharge line of the motor".

Assuming you mean that you suspect a restriction in the discharge of the pump, then this is probably wrong, as a restriction in the discharge will reduce flow and therefore require less power (lower Amps).

Your units for flow are not correct, but if the standby pump pumps 7 ? and this pump pumps 9 ? then the current drawn on this motor should be 9/7 x 23 = 29 amps. Why a motor of FLC of 50 amps is tripping at 38 amps I do not know.

I will let others give advice on the electrical side, but some comments on the pump:

If your system for both pumps is the same and the pumps are identical and there is no mechanical "rubbing" then you have to look at recirculation or some other hydraulic disturbance.

This can be caused by excessive clearances at wear rings or neck bushes (if no wear rings then excessive clearance between back of impeller and casing), recirculation from discharge back to suction (API Plan 11 or similar), erosion of cutwater, or a very often underestimated source of power consumption, roughness of the volute or impeller.

__________________
I have no special talent. I am only passionately curious. Albert E
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#18
In reply to #2

Re: Frequent tripping of 30kW motor.

07/14/2010 11:40 AM

Hi,

The 9/7 ratio is not applicable here because the pump curve is not linear. If he has the the pump curves for Q/H and power it might help him to see if the amps are within order.

I think the OP is talking about kg/cm² .

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#19
In reply to #2

Re: Frequent tripping of 30kW motor.

07/14/2010 11:57 AM

Sorry, We know now that the units used are m³/Hour.

In this case, the increase in amps is proportional to the square of the Volume increase, therefore, (9/7)² x 23 =38.02 A which is correct and consistant with the measured value.

Register to Reply
Anonymous Poster
#28
In reply to #19

Re: Frequent tripping of 30kW motor.

07/16/2010 3:24 AM

Is this correct? - I thought that power varies as the cube of the flow, but do the affinity laws apply as the pumps are presumed identical?

Hydraulic power = pgHQ

Given, the head will also vary, but it will be lower so using the ratio 9/7 is a reasonable case (efficiency at the two flow is also an unkown but would commonly be higher at the higher flow). Or do I not understand this correctly?

Register to Reply
Anonymous Poster
#29
In reply to #28

Re: Frequent tripping of 30kW motor.

07/16/2010 3:45 AM

Affinity laws do not apply here directly (I think).

The best way is to use the pump curves which we do not have.

The Power curve is not exactly linear at the points he is writing about.

Looking at the values, he should probably be having a high pressure (~ 350 m H2O)?? with the 7m3/h and 23A loading...? We can only guess when no curve or values for pressures.

He should check why the flow is 9m3/h and bring it down to the same 7 as the other and check the current before assuming that something is wrong with the motor or the assembly...

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#30
In reply to #28

Re: Frequent tripping of 30kW motor.

07/16/2010 4:26 AM

<...power varies as the cube of the flow...>

Not in a pump. Power is the volumetric flowrate multiplied by the rise in pressure divided by the efficiency. Which is why, without these data, the forum cannot determine whether the motor is correctly sized and, from that, advise the original poster on the electrical arrangements that drive it. Which is what the original poster asked for help with.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 296
Good Answers: 27
#31
In reply to #28

Re: Frequent tripping of 30kW motor.

07/16/2010 9:22 AM

You understand it correctly except that power varies directly as the flow. Hence the use of the ratio of 9/7. The formula for hydraulic power is correct.

The affinity laws do not necessarily apply here unless the impellers are of different diameters.

Power varies as the cube of the diameter.

__________________
I have no special talent. I am only passionately curious. Albert E
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#26
In reply to #2

Re: Frequent tripping of 30kW motor.

07/15/2010 2:42 AM

If the discharge line is blocked then the flowrate will be low-to-zero, in which case the pump isn't doing any work (apart from heating the fluid in its case) and the current should fall back.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jul 2010
Location: India
Posts: 8
#3

Re: Frequent tripping of 30kW motor.

07/13/2010 5:50 AM

eloborate the details of motor protection device.

Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 15
#4
In reply to #3

Re: Frequent tripping of 30kW motor.

07/13/2010 7:50 AM

As this starter is of old type, the protection is via a switch, contactor and a BMR.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#21
In reply to #4

Re: Frequent tripping of 30kW motor.

07/14/2010 7:56 PM

I honestly don't understand this. Why is additional information from the Original Poster considered off-topic?

Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#22
In reply to #21

Re: Frequent tripping of 30kW motor.

07/14/2010 10:01 PM

Because the poster himself marked it OT, though I don't know why.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Frequent Tripping of 30kW Motor

07/13/2010 1:53 PM

It seems that the 44A trip setting of the BMR is too low for a motor of FLC = 50A. Perhaps whenn it was new, the pump motor never drew more than 44A, so you got by. But now there may be some inefficiencies as have been mentioned.

One other thing I can think of would be loose wiring connections at or near the BMR. This could create extra heat, leading to nuisance tripping. If need be, clean and tighten the wiring connections.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Apr 2006
Location: Texas, by God! Houston for precision
Posts: 167
Good Answers: 2
#8
In reply to #6

Re: Frequent Tripping of 30kW Motor

07/13/2010 11:19 PM

Yes indeed. 44 amps for run can easily escalate to a greater load. You're running caustics through the puppy. Look for caustic-type failures. When you hear hoofbeats, think horses, not zebras. Look for crud (technical term, that) on your contacts.

__________________
If all else fails, read the directions. That's if, and only if.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#25
In reply to #8

Re: Frequent Tripping of 30kW Motor

07/15/2010 2:39 AM

What truth is there in the rumour that crud is an acronym for Chemical Reaction, Unidentified Deposit?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Frequent Tripping of 30kW Motor

07/13/2010 2:06 PM

Assuming BMR = Bi-Metal Relay???

Is that what is tripping? You keep saying the motor is tripping, but motors do not trip. It is either the overload relay (BMR?) or a circuit breaker or a fuse clearing, or there is some other protective device that is tripping, such as a vibration relsy, torque relay etc.. Please let us know which. Also, when you recorded the current as being 30% FLC, was that recorded when the "motor tripped"? Or was that recorded as part of a normal operation?

To effectively troubleshoot this, you need to know exactly what is happening at exactly when. Anything else is an exercise in futility.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Nov 2009
Location: Mumbai
Posts: 17
Good Answers: 1
#9

Re: Frequent Tripping of 30kW Motor

07/14/2010 12:11 AM

You are running 30 kW on DOL? What is the inrush current drawn by the motor?

Cheers,

RRV

www.econserve.in

__________________
Cheers, RRV
Register to Reply
2
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#10

Re: Frequent Tripping of 30kW Motor

07/14/2010 2:41 AM

You dont indicate how the pump is installed or where it pumps to. However a point to bear in mind, especially with DOL is that if you pump upwards to a height and the the liquid runs back ( reversing the pump) the motor will trip on start if the non return valve does not close. If the pump starts from empty( empty line), the m,otor will only trip if the protection relay/system have become tired or the motor itself have become less efficient due to, perhaps rewinds.If the motor have had rewinds, when did the problem start, straight after? Does the standby motor do the same? Is there a possibility of cavitation on startup? Cavitation will also play havoc on an old DOL, with current spikes maybe just making the trip criteria. Certainly a number of near trips will become a trip sooner than supposed to due to continuous partial heatup of the o/load.

Also remember that every trip slightly reduces the rated trip current on bi-metal overloads, thus if yours (motor) trip often, tripping will start occurring sooner even if the load is not excessive. Change the o/loads and test again. Also make sure that the caustic you are pumping now have not changed consistency. (higher SG or more crystaline stucture changing spec)

__________________
Always learning
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Frequent Tripping of 30kW Motor

07/14/2010 3:55 AM

<...discharge rate of 9 kG /m2& stand by pump is 23 Amp at 7 kG/m2...>

The units are not a flowrate. Please explain these units.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 15
#13
In reply to #12

Re: Frequent Tripping of 30kW Motor

07/14/2010 4:46 AM

M3 / hr...any more doubts please??

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #13

Re: Frequent Tripping of 30kW Motor

07/14/2010 4:48 AM

That's better. m3/h is a volumetric flowrate.

No doubts, just a need for more information:

  • What is the rise in pressure at these flowrates?
  • What is the supply voltage?
  • if the motor full-load current is 50A, then why is the trip set to 44A?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#27
In reply to #14

Re: Frequent Tripping of 30kW Motor

07/15/2010 2:43 AM

When the forum gets answers to these questions, it can advise as to whether the motor is correctly sized......

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#15

Re: Frequent Tripping of 30kW Motor

07/14/2010 5:31 AM

Assuming that this particular motor is sq.cage induction motor& starting current is as a standard is 6*FLC. You have not mentioned the L-L voltages. As a thumb rule in general 2% voltage difference( L-L ) is allowed to restrict negative sequence current produced due to unbalance voltages. For example if there is 2% difference, and stg. current is 6*FLC, negative sequence current will be apprrox. 12% of main line current.Also heating effect of this current will be nine times higher than main line current, which may generate additional heat to BMR and effected tripping.Also after frequent tripping calibration of BMR may be lost and it suggested that BMR should be replaced appropriately.Also check condition of the bearings( bearing temp. may be indicative. ). Sometimes due to high frictional effect in bearings, motor current may increase.In general in BMR, current setting is done 105% of FLC.

__________________
Manindra
Register to Reply Score 1 for Off Topic
Anonymous Poster
#17

Re: Frequent Tripping of 30kW Motor

07/14/2010 10:14 AM

Things I would do from experience: 1. I would put ac drives on both pumps and set these drives by the nameplate specs on the motor and the rpm of the pump. 2. Replace the pump and motor that is tripping. 3. Pumps need to be primed before pumping starts. 4. Make sure that when you do your motor rework/repair, that your motor is dynamically balanced. 5. Make sure that when you do your pump rework/repair that the pump housing is magnafluxed and that the pump is dynamically balanced. 6. If you can not afford an ac drive, update your starter to a solid state starter(an older bimetallic starter can cause problems). 7. Do lazer alignment on both pumps and motors setups.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#20

Re: Frequent Tripping of 30kW Motor

07/14/2010 12:22 PM

After you indicated that the volumes pumped are different: 9 compared to 7 m³/h then:

1- It is normal that the current goes up from 23 to 38 Amps because the power consumption is proportional to the current and proportional to the Square of the volume change:

Amps at 9m³/h compared to the 23A for 7m³/h= (9/7)² x 23 = 38.02A (consistant with your measurement).

2- If you check properly, you will find that this pump discharge valve has been opened to allow more flow hence the increase in Amperage. This seems normal unless you want to reduce the flow rate and reduce the motor current back to 23A (going from 7 to 9 cubic metre per hour is 28.5% increase ).

3- Therefore, if you do not need the increase in flow rate, then go back and reduce the flow rate: then you might not have a tripping pronblem with the same setting (44A on breaker O/load).

Otherwise, increase the setting to 50A (motor nameplate rating) and this should clear your problem. The reason for tripping even at 44A setting might be due to ambiant temperature being high and a derating necessity(?).

Basis of reasoning: The breaker contacts and connections look to be OK (you should and maybe have already done a check...?) because the current drawn by the motor at the flowrate mentioned is consistent with expectation.

4- If at 50A, the tripping continues, then the O/Load device could be defective and needs changing.

Cheers and good luck.

Register to Reply
Anonymous Poster
#23

Re: Frequent Tripping of 30kW Motor

07/14/2010 10:29 PM

clear the Caustic line which is accumulated in dwn side

Register to Reply
Anonymous Poster
#32

Re: Frequent Tripping of 30kW Motor

07/16/2010 10:31 PM

dear friend,

Sometimes the relays and contractors starts abnormal functioning due to prolong use. So you may change them temporarily and have a test. Also check the CT's.

Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#33

Re: Frequent Tripping of 30kW Motor

07/21/2010 3:36 AM

Everything it appears is alright with motor and pump. Still it trips on overcurrent. I suggest the following line of action:

1) Please interchange the motor with the standby and run both and check their parametrs particularly the current drawn. This would pinpoint problem area - pump or motor.

2) On the pump side since you have cheked on vibration and free movement only, I would suggest to have the pump impeller examined for its blade erosion at tips.

BB Raina

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#34

Re: Frequent Tripping of 30kW Motor

07/21/2010 4:06 AM

The forum is still waiting for pump pressure rise and volumetric flowrate information several days later, with a view to advising on whether the motor is correctly sized................

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 15
#35
In reply to #34

Re: Frequent Tripping of 30kW Motor

07/21/2010 6:38 AM

THE PROBLEMATIC MOTOR WAS ELECTRICALLY RELEASED FOR OPERATION AFTER INCREASING THE SETTING OF THE BMR TILL 95% AND IS FOUND TO RUN HEALTHY. REFERENCE TO VARIOUS DISCUSSIONS AND SUGGESTIONS FROM THE FIRM , IF (IN FUTURE) THE MOTOR TRIPS OR FUSES ARE BLOWN, I WILL REPLACE THE BMR. WHICH I UNDERSTOOD TO BE THE FAULT CAUSING ELEMENT. THE CONNECTIONS OF THE CT ETC ARE ALSO CHECKED FOR TIGHTNESS.

STILL FURTHER IF THE PROBLEM OF TRIPPING ARISES,AS SUGGESTED, THE PROBLEMS IN PUMP SHALL BE CHECKED.

THANK YOU.

Register to Reply Score 1 for Off Topic
Commentator

Join Date: Jun 2010
Posts: 75
#36
In reply to #35

Re: Frequent Tripping of 30kW Motor

07/21/2010 7:26 AM

I would still request you to interchange the motors and check the amperage of the problematic motor by running it on the standby pump.

BB Raina

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#37
In reply to #35

Re: Frequent Tripping of 30kW Motor

07/21/2010 8:50 AM

....and do also quote the pressure increase and volumetric flowrate in this forum, so that others may advise on whether the motor is undersized for the load. The problem may still be a hydraulic one, and not an electrical one.

Do turn off Caps Lock before posting again. It costs nothing to be polite. Take the risk!

<unsubscribes from discussion>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#38
In reply to #37

Re: Frequent Tripping of 30kW Motor

07/22/2010 12:26 AM

He may not be knowing what it means by posting in capitals.

BB Raina

Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 15
#39
In reply to #37

Re: Frequent Tripping of 30kW Motor

07/22/2010 11:15 PM

Dear Bar Man Sir,

I do accept yr suggestion, what is the prob if the letters are in caps lock. The motor is not undersized and is correctly sized. Hence motor sizing is not a problem.

Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#40
In reply to #39

Re: Frequent Tripping of 30kW Motor

07/23/2010 3:36 AM

Dear Pratapji

In email communications writing in capitals is equivalent to shouting at a person. You may not be knowing. Nothing wrong as such.

BB Raina

Register to Reply
Register to Reply 40 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (7); BB Raina (4); JRaef (1); jvrj (1); Kaisan (2); kanmano (1); ktel60 (1); LAA_Lucke (3); manindra (1); nmpratap (5); PWSlack (10); rrv (1); sachin230 (1); Tornado (2)