Anonymous Poster

Limit Switch Connection to Micrologix PLC

07/13/2010 11:38 AM

Can anybody tell me about how to connect a 2 wire, namur type, proximity limit switch to the digital input module of micrologix PLC. Because the digital input module on the micrologix PLC does not support the output of that limit switch.

Thanks,

Karthik

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Limit switch connection to Micrologix PLC

07/13/2010 11:56 AM

Brown of limit sensor to +24V,

Blue of limit sensor to Micrologix input,

Common of Micrologix input to 0V.

Job done.

(If the common of your Micrologix inputs is already connected to +24V,

connect Brown of sensor to the Micrologix input, and Blue of sensor to 0V).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2
In reply to #1

Re: Limit switch connection to Micrologix PLC

07/13/2010 12:32 PM

May have to re-think that!

Please give the manufacturer and part number of your sensor.

Check out this link: http://www.tektron.ie/namur1.htm

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3
In reply to #1

Re: Limit switch connection to Micrologix PLC

07/13/2010 4:48 PM

You're answering the implied question and not the actual question. The OP will have to use more wire and preferably a few keyed connectors to connect the sensor and the PLC together. It would be helpful to locate a multiconductor cable that has an identical color collection as the sensor's wires to keep the color coding the same. Since this is just a limit switch, I do not see a need for shielded wire, but if you have it you can use it.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#4
In reply to #3

Re: Limit switch connection to Micrologix PLC

07/13/2010 7:01 PM

Have you looked into Namur type sensors? I'm pretty sure it's not just a wiring problem! Too tired to check it out tonight.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5
In reply to #4

Re: Limit switch connection to Micrologix PLC

07/13/2010 7:30 PM

Yes I have looked into NAMUR limit switches and found that the NAMUR designation makes the switch suitable for a harsh chemical environment, but does not specify any particular electrical condition. (You'll notice my switch has different signal options than your citation.) So a two wire sensor will probably just be a switch contact but it could actually be any electrical signal characteristic known to somebody. While this remains unknown, no further help can be given. Regardless of what it is, one will still connect this directly or indirectly to the PLC using a combination of electrically conductive and non-conductive material known as wire.

Now if the OP wishes more help than this, they will have to produce more information about the proximity limit switch, like a model number and manufacturer.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#6
In reply to #5

Re: Limit switch connection to Micrologix PLC

07/14/2010 9:58 AM

Good morning, guys.

If you would indulge me, I would treat this as an educational opportunity for the Doorman as well.

I am unfamiliar with this type of sensor, and as I research the varied sites available it appears the digital interface (input in OP) module (mentioned in the OP) needs to be compatible with the sensor (sites reviewed indicate they should be the same brand. Were I the manufacturer, that is what I would tell someone as well.). Is this perhaps the trouble: incompatible components?

Here is one site that seems to have some good info. Am I being steered in the wrong direction?

__________________
Semper Ubi Sub Ubi
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7
In reply to #6

Re: Limit switch connection to Micrologix PLC

07/14/2010 11:04 AM

Good Morning,

This is a classic problem here at CR4. A guest posts a question asking for a specific engineering design choice to be explained. The trouble comes in that the guest does not provide sufficient information that we can help. You see NAMUR standards are a broad collection of European based manufacturing company standards for equipment used in chemically hazardous environments. These manufacturers have banded together to in essence say that if assemblers choose from our collection of products, no hazardous configuration can be assembled if you follow our directions. But without knowing which switch Karthik has in his/her hands, nobody can say with any certainty if a particular interface device will work.

Now you and JohnDG have found on the web one of the companies with an interface module to sense a switch and posted that link. This company's product may or may not be exactly what Karthik needs to interface between switch and PLC. It certainly won't hurt either device, but unless we get a return visit by Karthik we will never know if it works.

The only lesson one can get here, is that there are hundreds of "standards" out there that are buried under bureaucratic red tape. It is good to follow one of these standards and even better to be certified as following the relevant standard for your field. But just stating that you follow one of the many standards does not identify what you are doing sufficiently to anyone outside of that standard.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 4)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#8
In reply to #7

Re: Limit switch connection to Micrologix PLC

07/14/2010 11:17 AM

Fair enough, redfred, and thank you for the explaination.

After reading your post, I checked the link offered by JohnDG and discover we have linked to the same website. Sorry JohnDG, I did not intend to step on you. I should have checked your offering before I posted.

__________________
Semper Ubi Sub Ubi
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#9
In reply to #8

Re: Limit switch connection to Micrologix PLC

07/14/2010 11:34 AM

No prob.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply Off Topic (Score 5)
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#10

Re: Limit Switch Connection to Micrologix PLC

07/14/2010 12:55 PM

It is possible that the proximity switch you have is not compatible with the input of the PLC. You may have a NPN proximity switch and your plc inputs may be wired for PNP. Check the Com 1 terminal of the PLC if it has +24vdc going to it your PLC inputs are wired for sinking inputs. If it has 0vdc going to it your PLC inputs are wired for sourcing inputs. You then have to make sure that your Proximity switch is compatible. Banner makes an excellent test box to determine this, (part #DBQ5) if you don't have the proximity switches manufacturers information.

__________________
Knowledge makes what was impossible, seem easy.
Reply Score 1 for Good Answer
Active Contributor

Join Date: Mar 2010
Posts: 24
Good Answers: 2
#11

Re: Limit Switch Connection to Micrologix PLC

07/14/2010 4:31 PM

The NUMAR switch operates at a lower voltage than some digital inputs on PLC's. I know it seems old school, but I just used a separate low voltage to power the prox switch and fed it to a low voltage relay to power the digital input. ...FrankenPLC :)

Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#12

Re: Limit Switch Connection to Micrologix PLC

07/15/2010 7:57 AM

This link may help.

www.tektron.ie/namur1.htm

Good luck

__________________
Knowledge makes what was impossible, seem easy.
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#13
In reply to #12

Re: Limit Switch Connection to Micrologix PLC

07/15/2010 10:48 AM

Try reading the thread. You're the third person to post that link!

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply Off Topic (Score 5)
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#14

Re: Limit Switch Connection to Micrologix PLC

07/15/2010 12:52 PM

An active converter/adapter is needed.

Namur is designed for I/S operation. It requires 8.3V but is current activated, so you need a converter to run on 24Vdc.

The link to Tektron shows a typical converter. Pepperl & Fuchs and Phoenix Contact have "NAMUR switch amplifiers" that convert the Namur change of state into PNP/NPN active or passive. I'm sure other vendors do as well.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15

Re: Limit Switch Connection to Micrologix PLC

03/25/2025 7:16 AM

An interposing relay would do it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bud (1); Doorman (2); Elroy (2); illya Leonov (1); JohnDG (5); PWSlack (1); redfred (3)