Paralleling of Transformer

07/15/2010 1:28 AM

If we are using 2 no's of 200 kVA UPS system in redundant configuration , and connect independent transformer at the bypass ( Automatic Change over from UPS to bypass) . In this case if both UPS fails then how the load sharing will happen at bypass end . Load shall be shared by each transformer depend upon transformer Impedances ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Paralleling of Transformer

07/15/2010 3:06 AM

What is the probability of simultaneous failure of both UPSs?

If a UPS has failed, then isn't it really an IPS?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#2

Re: Paralleling of Transformer

07/15/2010 3:08 AM

you need to consider frequency+vector group+voltage rating also for the intended transformers, not only the impedance

Register to Reply
Active Contributor
Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Fans of Old Computers - UNIVAC - New Member Hobbies - Automotive Performance - New Member Popular Science - Genetics - New Member Safety - ESD - New Member

Join Date: Jun 2010
Posts: 23
#3

Re: Paralleling of Transformer

07/15/2010 8:06 AM

Conditions for parellel operation are,
Same voltages at two sides, vector group and impedance ratio is must for parellel operation of transformers.
The load is shared between two transformers according to its kVA
If UPS 1 failed you have UPS2
If UPS1 and 2 failed you have Transformer 1
If UPS1 and 2, Transformer 1 failed you have Transformer 2
So select the transformer size for any failure
If UPS 1&2 and Transformer 1 & 2 failed you have nothing

Register to Reply Score 1 for Good Answer
Anonymous Poster
#4
In reply to #3

Re: Paralleling of Transformer

07/15/2010 12:44 PM

If he himself failed then ?

Register to Reply
Associate

Join Date: May 2008
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
Posts: 54
Good Answers: 1
#5

Re: Paralleling of Transformer

07/15/2010 11:37 PM

In case of Parallel UPS Architecture (Whether for Capacity OR Redundancy); the Automatic Bypass Supply to the Paralleled UPS Output Bus (2X200 KVA in ur case) should be fed from single transformer and not two independent transformers i.e. 200 KVA bypass transformer rating is required if the Paralleing of UPSs is done for Redundancy and 400 KVA bypass transformer rating is required if the paralleling of the UPSs is done for Capacity.

The architecture conceptualized / installed by you is not recommended considering variations in the impedenace of cables/lug-contacts, switchgears etc.

Rgds

Sanjeev

__________________
Karma is Dharma
Register to Reply
Member

Join Date: Jul 2010
Posts: 7
#6
In reply to #5

Re: Paralleling of Transformer

07/16/2010 1:46 AM

Thanks , Paralleling is done for redundancy purpose only , and transformer connected separately is also to achieve redundancy . ( I.e if one UPS along transformer fails , very very rare occurrence )

Thanks for your reply

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7
In reply to #6

Re: Paralleling of Transformer

07/16/2010 7:21 PM

Sudhir199,

I understood you will be using this redundant UPS system for extremely critical loads. You didn't provide the detail configuration of the UPS system and I assume each of the bypass transformers is connected to the individual UPS and there is static transfer switch to transfer the load to/from the bypass transformer and both of the UPS systems are synchronized. In case of the both UPS's fail (very rare scenario though but is considered for extremely critical loads such as hospital ICU), the bypass transformers supply the power to the load.

Are both of the bypass transformers fed from same source or different source? The extreme redundant nature of your UPS made me feel they are from different sources. If they are from same source, then you are right – the load will be shared by each transformer depending on their impedances including the cable impedances (if cable length differs significantly). If they are from different sources, then the load will be shared by each transformer depending on their impedances (including cable impedances) and differences of the voltages (though it is very small) of the two sources.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Member

Join Date: Jul 2010
Posts: 7
#8
In reply to #7

Re: Paralleling of Transformer

07/27/2010 4:32 AM

Thanks for reply ,

2 different sources used for bypass supply.As load connected to UPS systems are veru very critical user would like to go for such type of configuration .

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); chhotu1990 (1); kabeerta (1); msamad (1); PWSlack (1); sudhir199 (2)

Previous in Forum: Busbar Extensions   Next in Forum: Capacitive Load

Advertisement