CT Polarity Test

07/15/2010 1:36 AM

how we check ct polarity

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Jul 2010
Location: India
Posts: 8
#1

Re: ct test

07/15/2010 2:39 AM

Polarity can be tested using the flick test. Connect an analog ammeter (hand‐held

multi‐meter) to the secondary terminals of the CT, meter positive to X1 and

negative to X2. Using a suitable low‐voltage battery, connect the negative terminal

to H2 of the CT. While watching the analog ammeter, apply a current pulse to the

CT by connecting and disconnecting the battery positive to H1 of the CT. If the

polarity is correct, the meter needle gives a positive flick on closing and a negative

flick on breaking the circuit

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: ct test

07/15/2010 9:00 PM

See also this thread http://cr4.globalspec.com/thread/33197

- MS