Regulator - Hunting Downstream

07/18/2010 3:12 AM

i have a pressure reducing valve. it is regulating from 9barg (131psig) to 0.35barg (5psig) for seal gas pressure for the compressor. My spring range is 2-6 psig. the regulator cannot stabilize my outlet pressure causing my compressor to trip. The PCV is hunting on downstream pressure. Any reason for why this is happening? Any suggestions you can provide to avoid this problem?

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: Regulator - Hunting downstream

07/18/2010 6:48 AM

I would suspect that it's from pressure waves. Is there an accumulator nearby? If not, try adding one with small orfices to minimize pressure fluctuations, and put the pressure regulating valve in that circuit.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Active Contributor

Join Date: Dec 2009
Posts: 15
#2
In reply to #1

Re: Regulator - Hunting downstream

07/18/2010 8:00 AM

thanks.

What do you mean accumulator?

Also, can you help me in expanding the "hunting" downstream? what causes it?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Regulator - Hunting downstream

07/18/2010 11:43 AM

Four possibilities:

1. The PCV is oversized for the application.

2. Something internal is sticking.

3. The valve passage/seat/plug/disc/etc. is eroded.

4. Leaking diaphragm.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#4
In reply to #2

Re: Regulator - Hunting downstream

07/18/2010 2:05 PM

Accumulator means nothing more than a tank or other relatively large volume buffer to minimize pressure fluctuations. (In refrigeration systems, it's a tank to collect liquid and has enough volume to allow part of the liquid to return to a gaseous state before it returns to the compressor.) Don't think much about my use of the term -- it just means tank.

On the other hand, the flow of compressed air into the tank should be restricted so that rapid pressure fluctuations cannot occur. The main tank is usually close by the compressor and very large with respect to the volume of the compressor cylinder(s) and performs such a function more or less automatically. From your description, it sounds like you may not even have a "main tank," or if so, it isn't located near the compressor.

Hope that clarifies.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
2
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#5

Re: Regulator - Hunting Downstream

07/18/2010 11:14 PM

I believe your TRUE problem is in the level of pressure drop you are trying to make. The final target pressure is well past "critical" drop of 45% of absolute pressure.

Try putting another pressure regulator upstream and go to 2 or 3 BAR, then use your regulator to finish the drop.

The accumulator won't hurt either- It will give the regulator a chance to stabilize without triggering the over pressure on you seal.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: May 2010
Posts: 11
Good Answers: 1
#6

Re: Regulator - Hunting Downstream

07/19/2010 3:00 AM

I suspect Energygod is correct, use 2 PCV's the pressure drop range is to great for one PCV to handle, I also suggest you check the capacity, because if the capacity of is the valve is to large then you will get instability

Register to Reply
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#7

Re: Regulator - Hunting Downstream

07/19/2010 4:45 AM

You dont say if your valve is pilot regulated or just a run of the mill pressure reducer. Either way your upstream pressure is enormous in comparison to your down stream. I would rather use a common ( run of the mill ) pressure reducer to drop the pressure down to, 2-2.5 bar, and then a pilot regulated, good quality, reducing valve for the final low oressure. Make sure that there is no moisture in your line. Moisture will play havoc with any low pressure regulator, good quality or not.

__________________
Always learning
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#8
In reply to #7

Re: Regulator - Hunting Downstream

07/19/2010 4:48 AM

I see Energygod have given similar advice. Nice to be in like minded company at opposite ends of the world.

__________________
Always learning
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Dec 2009
Posts: 15
#9

Re: Regulator - Hunting Downstream

07/19/2010 7:11 AM

Thank you all for the help ;-)

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#10
In reply to #9

Re: Regulator - Hunting Downstream

07/19/2010 7:16 AM

Thank you for the thank you, however we would like to know whether any of the advice solved your problem.

__________________
Always learning
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#11

Re: Regulator - Hunting Downstream

07/19/2010 8:39 AM

Energygod is correct, use a second regulator supplied from the first preferably one with a large diaphragm to give it good control for such a small pressure range. Or a dual stage regulator might do the trick.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Active Contributor

Join Date: May 2010
Posts: 11
Good Answers: 1
#12
In reply to #11

Re: Regulator - Hunting Downstream

07/19/2010 10:07 AM

stick with the tried and trusted use 2 PCV's in series, the 2nd one to regulate down to 0.35barg should ideally be a pilot operated one for such low pressures. After reading all the posts and asimilating the knowledge put forward by all the esteemed gentlemen, I am pretty sure this solution will do the trick and provide you with a stable pressure and feed for your seal gas service

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#15
In reply to #11

Re: Regulator - Hunting Downstream

07/20/2010 11:10 AM

"everybody" says that I am right on, but I only got one GA. Come on guys, it's a matter of pride.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Off Topic
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#16
In reply to #15

Re: Regulator - Hunting Downstream

07/20/2010 12:16 PM

You cant ask for that, I have given lots of good answers and not had one GA for them, at least you recieved one

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#17
In reply to #15

Re: Regulator - Hunting Downstream

07/21/2010 1:41 AM

I said you were and I GA'd you

__________________
Always learning
Register to Reply
Active Contributor

Join Date: Dec 2009
Posts: 15
#13

Re: Regulator - Hunting Downstream

07/20/2010 12:59 AM

Thank you again for all the suggestions. I'm considering all your inputs and will let you know of the results soon.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#14

Re: Regulator - Hunting Downstream

07/20/2010 5:40 AM

You don't say what causes the compressor to trip. Is there a pressure sensor protecting the seal from over pressure (or under-pressure).

You talk of a pressure reducing valve. In a primitive form this could be nothing more than a 'tap' (a restrictor that limits the flow by pressure drop). This type of reducer has no ability to regulate the pressure except under one set of flow conditions. At no-flow the outlet pressure equals the supply pressure.

Or maybe something slightly more elaborate like a spring loaded piston that closes as pressure rises. This type of valve usually leaks across the seat allowing outlet pressure to rise, but being primitive it cannot relieve the excess pressure. Normally the leak is minimal compared to the total flow and can be ignored.

Except in your case I guess there is no flow (pressuring a static seal) - so leakage is important - and outlet pressure rises - maybe that is why the compressor trips - until maybe the valve shuts so tight that there is no more leakage. But by then it is too late.

A more sophisticated design is required. A spring-loaded or pilot loaded diaphragm valve - or rather a 'pressure regulator' - is much more sensitive to pressure changes and usually with an exhaust relief that dumps excess pressure.

As others have said, this is what you need.

Normally to select a pressure regulator, you need to specify the outlet pressure (range), the inlet pressure (range), the flow (range) and accuracy.

I hope this helps.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bill (2); energygod (2); garth (2); horace40 (1); jvrj (4); plutonium (3); richard f. (2); Tornado (1)

Previous in Forum: Wireless instrumentation in thermal power plant?   Next in Forum: Lightning & Surge Protection Methods

Advertisement