Voltage Improvement By Using Capacitor Bank

07/20/2010 6:12 AM

An induction motor is designed to run at rated voltage of 440volt but the supply voltage is of 380volt due to which it is taking more than its full load current. So is there any possibility of improving the voltage by using capacitor bank in series with transmission line. If yes then how. Please explain?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#1

Re: vOLTAGE IMPROVEMENT

07/20/2010 6:21 AM

Pl. specify rating of motor.

Any way, as voltage is 440 V, assuming motor rating to be less then 200 KW.

Series connection of capacitor can only compensate for inductive voltage drop in lines which may not be substantial.

Instead think of reactive power compensation and reducing voltage drop in lines.

__________________
When was last time you did something for first time.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: vOLTAGE IMPROVEMENT

07/20/2010 6:49 AM

Please:

  1. turn off Caps Lock
  2. Reduce the motor overload protective device(s) trip setting(s) immediately to the full load current of the motor at 380V, which may be stated on its rating plate or may be obtained from the motor manufacturer, before an overload causes breakdown, process revenue interruption costs, personal injury or fire at the facility. If the motor is operating beyond its full-load current, is it adequately sized for the job at hand [rhetorical question]?

A capacitor bank in series with the transmission line cannot increase the line voltage.

An increase in the supply voltage can be achieved in several ways:

  1. Altering the tapping point of the local distribution transformer to operate at a higher line voltage.
  2. Installing an additional transformer to step-up the line voltage to the required level.
  3. Deriving power from an alternative source that is running at a higher voltage.
  4. If serious consideration is being given to capacitor banks in parallel with the supply so as to operate the feeder cable at a higher field-end voltage (though it is usually done to lower feeder cable losses and reduce tariff charges on the basis of presented power factor to the local utility supply company), then one of the possibilities is that the supply cable is undersized and requires upgrading and/or replacement.

In all cases, consult a qualified Electrical Engineer locally, who will inspect the facility and advise on the most appropriate course of action in this case.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#3

Re: vOLTAGE IMPROVEMENT

07/20/2010 6:59 AM

guest; sound like you have 50 HZ! you could try boost transformers. perry