Short Circuit Calculation

02/28/2007 8:48 AM

It is of general knowledge how to calculate short circuit currents by uisng the symetrical components.

But when a delta wye transformer is inserted in the circuit, the model imposes a 0 transfer impedance and a defined zero sequence impedance on the wye side.

But how to cope withe the fase difference due to the group connection of the transformer? Shoul this phase shift be considered inthe calculation?

And how to consider this?

Register to Reply
Pathfinder Tags: Short circuit calculations
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate
United Kingdom - Member - New Member Fans of Old Computers - ZX-81 - Dragon 32

Join Date: Feb 2007
Posts: 36
#1

Re: Short Circuit Calculation

02/28/2007 1:15 PM

Hi,

It depends on the position of the short circuit.

Is it between phases or one phase going to ground on the "wye" star side or on the delta side?

I touched on single phase "wye" star side short circuit calculations in my electrical course some 24 years ago!! Showing my age now. :-(

It takes into account the "earth fault loop impedance" to calculate the fault current and thus the disconnection time based on the protective device used and the characteristics of the same, be it a fuse or a circuit breaker or an earth-leakage ( r.c.d ) device.

Regards,

Dr M.

Register to Reply
Commentator

Join Date: Feb 2007
Posts: 60
#2
In reply to #1

Re: Short Circuit Calculation

02/28/2007 2:00 PM

Dear Dr. Marten

Thank you for your answer.

The problem is as follows:

in a 230-13.8KV substation, I need to set the relay downstream to a power transformer.

This transformer is delta(230) wye(13.8) connected and the impedance is 8%.

In order to calculate the short circuit, I have two possibilities

-consider z t = j 0,08 + 0 and neglect transformer phase shifting(30 degrees)

-or consider the phase shift and will have a different value of the current (zt = 0,08 L(90-30)

My question is: is it valid to neglect the phase shift, for calculation purposes?

The difference will be that I will have a resistive and a reactive current.

Kind regards

Register to Reply
Commentator

Join Date: Feb 2007
Posts: 60
#4
In reply to #1

Re: Short Circuit Calculation

03/01/2007 8:36 AM

Dear Dr

A single phase to earth fault is being examined.

Kind regards

Emmanuel

Register to Reply
Participant

Join Date: Jul 2008
Location: Philippines
Posts: 3
#6
In reply to #1

Re: Short Circuit Calculation

07/29/2008 3:31 AM

How does the fault current calculated? Please provide a useful formulas to find the exact value of current required if it is really a fault current or not.

Register to Reply
Anonymous Poster
#3

Re: Short Circuit Calculation

03/01/2007 8:25 AM

You can sure do components, but why go to that trouble? It's much easier to calc the fault current from the XFMR MVA, Z% and secondary Voltage. If you must do compenents, then perform a delta - wye transform then reduce every thing to per unit per phase (pu pp).

Register to Reply
Commentator

Join Date: Feb 2007
Posts: 60
#5
In reply to #3

Re: Short Circuit Calculation

03/01/2007 11:15 AM

Dear dr

The transformation into symetrical components does not take into consideration the phase displacement between prymary and secondary, i.e., the current reflected to the secondary will be in phase with the secondary current.

Therefore, the question remais open.

Register to Reply
Anonymous Poster
#7

Re: Short Circuit Calculation

07/29/2008 6:59 AM

Dear folks

I finally discovered how to cope with this matter.

One just need to convert the delta impedances into star impedances.

Then use the impedance obtained in this way and shift it by the delta wye angle between the two windings of the transformer.

After this, the system may be dealt with as a regular symmetrical components circuit.

Thank you again for your efforts in helping me.

Regards

Emmanuel