Anonymous Poster

Leakage Voltage at Neutral

07/21/2010 9:31 PM

I have rewound a 3 phase 415 v delta 115 v star 4 wire 15 kva transformer .I have tested the transformer at no load , the input and out put are getting correct rated voltages. But I am getting a 8 v at body to star point which is not recommended to use in our system who demands less than 3 v the item has to be used on board ship for special purpose .It was rechecked for all cold checks like insulation, resistance inductance etc.Can any body suggest or explain the reason.we cannot earth the neutral point.because of the unbalanced earth condition of ship.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Jan 2010
Location: Bharuch , Gujarat , India
Posts: 17
#1

Re: Leakage Voltage at Neutral

07/21/2010 11:38 PM

dear , kindly check your nearest Eearthing Pit .If it is ok you will get 3v w.r.t ground .

__________________
jayesh b sathwara
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Leakage Voltage at Neutral

07/22/2010 2:01 AM

<...cannot earth the neutral point.because of the unbalanced earth condition of ship....>

This doesn't make sense. If the neutral point were to be earthed then there would be no voltage between neutral and earth at the transformer.

Please check out the Wikipedia article on earthing and advise further.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#3

Re: Leakage Voltage at Neutral

07/22/2010 2:54 AM

Since the equipment has qualified the tests there is no need to worry.

You may use Restricted Earth Fault Relay (64) to initiate an alarm above the threshold to circumvent the anamoly if that is your consideration.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Member

Join Date: Jul 2010
Posts: 5
#5
In reply to #3

Re: Leakage Voltage at Neutral

07/22/2010 1:03 PM

thank u 4 ur valid response . really I am not full filled with ur reply.further I have recnnected the primary as y connection and earthed the primary Y point to a good earth.still I couldnot attain the customer demand of less than 3 volt .As I mentioned earlier the secondary neutral cannot be earthed due to Ship is not having valid earth point or in built established nuetral points. Only when the ship is fed with shore suply, the nuetral may be available and hull of ship cannot be cosidered as a good earth.I have introduced screen earthing after primary winding and after secondary winding and connected to the body of the transformer.Still ,the problem exists. as u suggested introduction of EFR is not reccomended by the OEM of the system. which is installed by BEL bangalore.

any way thank u for the response and expecting more.

joseph

Reply
2
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#6
In reply to #5

Re: Leakage Voltage at Neutral

07/22/2010 2:54 PM

Anomily exists in the orignal discription (by OP) as he describes 415 v Delta & 115 v Star where as now you say that primary is Y with good neutral point earth and secondary neutral cannot be earthed due to ship ...

(I mean delta winding should not have Neutral, any tertiary winding you did not mention? and also how did the primary got good earth while on the same ship?).

There is a functional difference between REF and EFR you have mentioned but since I am unaware of BEL (or Banglore) practices I take your clarification as binding.

To my assessment voltage gradient between tank and neutral could have emerged due to leakage reactance cused by some careless workmanship or quality of the material used in one of the phase windings.

I am not after GA score and look forward to having a clear and unambiguos discription of the matters from your end accordingly I will again try to give you some satisfactory response if I can but please do not get disappointed there are other people better qualified than me on this subject.

__________________
Knowledge sharing is a WIN-WIN situation
Reply Good Answer (Score 2)
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#7
In reply to #6

Re: Leakage Voltage at Neutral

07/22/2010 4:19 PM

You are correct a Delta connection has no neutral.

On a boat it is common to use the star point of a Y generator system to "earth" the boat and the isolation transformer should have compatable wiring.

Galvanic isolators are also often used on boats to control the floating sacrificial anode and the inclusion of one of these items will lower the voltage between "earth" and neutral by a small amount ( I think they are just a few diodes in an expensive box.)

And yes the question does not explain enough.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Reply
Member

Join Date: Jul 2010
Posts: 5
#11
In reply to #6

Re: Leakage Voltage at Neutral

07/23/2010 11:11 PM

hai everybody,

thanku u for ur helpul suggessions .I regret, that Imentioned in description that neutral was earthed at primary. this is true that for a trial and errorr expiriment ,I re arranged the primary connection to star and neutral was earthed.

Reply Off Topic (Score 5)
Member

Join Date: Jul 2010
Posts: 5
#13
In reply to #6

Re: Leakage Voltage at Neutral

07/23/2010 11:56 PM

thank u mountk2

(I mean delta winding should not have Neutral, any tertiary winding you did not mention? and also how did the primary got good earth while on the same ship?).

my response:-I have rearranged the primary connection to Y for testing purpose and connected the Y to earth .All these tests are done on shop floor .Only after the Qc checked is passed we could install to on board ship.

(To my assessment voltage gradient between tank and neutral could have emerged due to leakage reactance cused by some careless workmanship or quality of the material used in one of the phase windings.)

my response:-this wiil be rechecked

Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#4

Re: Leakage Voltage at Neutral

07/22/2010 4:29 AM

If you can measure primary voltage with respect to earth, measure for all three phases and see if it is equal in all the three phases.

The problem of this shifting may be reflected from primary.

__________________
When was last time you did something for first time.
Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#8

Re: Leakage Voltage at Neutral

07/22/2010 11:01 PM

I think you are seeing very low current leakages, try measuring it with an old fashioned analogue meter, I'll bet it goes away.

Reply
Member

Join Date: Jul 2010
Posts: 5
#12
In reply to #8

Re: Leakage Voltage at Neutral

07/23/2010 11:46 PM

thanks baxterm. this is true that if it is measure by an analog meter we cannot identify any voltage which means that current may be very low, but with a digital meter it exists. still we have to find out the acual reasons and remedies. I have introduced screen windings of copper foil of 0.25mm thick and 150 mm width of one turn after primary and seccondary winding earthed to frame and frame to good earth.

still no progress

Reply Off Topic (Score 4)
Anonymous Poster
#9

Re: Leakage Voltage at Neutral

07/22/2010 11:49 PM

Your point floating not to earth When connect to ships point it not or a shift the problem away. You seem be worried about something that is directly related to the way you are testing. Try connecting it to earth & then measure the volts again.

Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#10

Re: Leakage Voltage at Neutral

07/23/2010 7:24 AM

During manufacturing/ rewinding work, a thin copper foil ( covering 3/4th. perifery of LV winding with insulation) is wound over LV winding and is connected to transformer body to compensate the effect of voltage generation ( between Tr. neutral to body)due to leakage flux. In this particular case please check whether the same has been done.

__________________
Manindra
Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#14

Re: Leakage Voltage at Neutral

07/24/2010 2:45 AM

Please carry out Polarization Index Test (PI) using megger.

(PI is defined as a ratio of 10 minute insulation resistance to 1 minute insulation resistance. For class A insulation value of 1.5 or more and for class B insulation minimum 2.0 is satisfactory)

Please also carry out Dummy load test at different loading conditions to observe the voltage values at neutral.

I will try to Google out any code or standard reference favoring you against the client's set limitation.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#15
In reply to #14

Re: Leakage Voltage at Neutral

07/24/2010 4:00 AM

I want to add:

When isolation transformer is employed, to create isolation between ship and shore power supply, it is done by establishing a new ground on board your vessel. The shore ground is terminated at the shield between the primary and secondary windings of the isolation transformer.

At Google, information at following sites might be of your interest:

http//shop.pkys.com/isolation transformers.aspx

I agree with manindra post # 10

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#16
In reply to #15

Re: Leakage Voltage at Neutral

07/24/2010 6:13 AM

I want to add more on this issue. I am working in Port sector for long time as Electrical Engineer and from my working experience I have seen sometimes voltage between neutral point to transformer body increased beyond tolerable limit which is detrimental for operation of sophisticated electronic instruments/ equipments. In most of the cases it is seen that earthing connection from shield to transformer body snapped due corrosion( saline weather); and if the connection is remade the problem is solved.

__________________
Manindra
Reply
Anonymous Poster
#17
In reply to #14

Re: Leakage Voltage at Neutral

07/25/2010 7:58 AM

PI test with HV break down tester (0 - 10 KV) has been conducted giving 3KV for 1 minute between primary sheild (disconnected from body) and primary winding read 0.003micro A,between primary winding and body is 0.005micro A and primary and srcodary is 0.005micro A. We are using class 'H' insulation( Nomex) for the inter layer separation (12mill X 2 layer) 3 layer between sheild and winding

Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#18
In reply to #17

Re: Leakage Voltage at Neutral

07/25/2010 11:24 AM

I am not aware of PI test to have been done with an 'HV break down tester'. I had given requirement of megger.

Refering to one part in your orignal post I mean the toppest one, "Can any body suggest or explain the reason.we cannot earth the neutral point.because of the unbalanced earth condition of ship" Portugal philip's post # 7 has indicated one of the possible reasons.

Since the transformer has not left the workshop, please consider jayesh100375 post #1

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Reply to Forum Thread 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); baxterm (1); Happy singh (1); jayesh100375 (1); manindra (2); mountk2 (5); portugalphilip (1); PWSlack (1); pxjosaaa3 (4)

Previous in Forum: Performance of Motors   Next in Forum: Substation Layout

Advertisement