I received a transmitter as per our requirement
process data : pressure normal/design (psig): 47/150
temperature normal/design : 200deg F/-20 to 250 deg F
Instrument range (psid) - 0 to 8
calibration range (psid) - 0 to 5
process fluid : glycol
sensor element - diaphram
but recived transmitters nameplate is having : URL is 160 KPa
LRL is -160 KPa
that means upper range lmit of the sensor is 160KPa =23.20 but our process normal pressure is 47 psig , my doubt is ULR is less than process normal pressure which is not crrect.
as static pressure for the diaphram is not mentioned.
model no is 2600T series ABB 264DS
please kindly clarify my doubt
thanks
Re: DP Transmitter URL
07/22/2010 9:42 AM
Hello Guest,
The -160 to 160 kPa ( -23.2 to 23.2 psid) Span Limit will certainly handle your 0 - 5 psid calibration span.
If you look at the Datasheet, page 3 for sensor code H (that is yours) shows Overpressure Limit of
– 21MPa, 210bar, 3045psi
Your 47 psig is well within these limits, so it looks like you're good to go.
For confirmation, call ABB. Contact info is on the last page of the datasheet.
07/23/2010 12:50 AM
I swear, my time spent here is just a freaking waste of time.
07/23/2010 2:29 AM
Don't give up!
It's just that guest doesn't understand the difference between the line pressure and the differential pressure specifications on this type of instrument. It's whether guest is adequately trained to assess the manufacturer's specifications against the user requirements that is in question. Everyone has to start somewhere.
07/23/2010 5:44 AM
CR4 - Deleted Post
Abuse/Attack:
This post was deleted because it was an attack on another user. Please review the CR4 Site FAQ and the CR4 Rules of Conduct.
07/23/2010 5:48 AM
CR4 - Deleted Post
Abuse/Attack: This post was deleted because it was an attack on another user. Please review the CR4 Site FAQ and the CR4 Rules of Conduct.
07/23/2010 9:28 AM
Thanks for the encouragement, PW.
Looks like you got scorched for your kind words though.
Still, I appreciate it.