MCCB application in TNS System

07/22/2010 4:28 PM

In the TNS AC Power Distribution System, how is the 4P MCCB and 3P MCCB differ in each other in terms of application to protect the circuit, please to explain and share your explanations. Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: MCCB application in TNS System

07/22/2010 7:03 PM

I think you are referring to IEC 60364 (312.2.1.1) for the TNS system.

In the TNS system, there are 3 line conductors, 1 neutral conductor (N) and 1 protective conductor (PE). In the electrical system, only the current carrying conductors are required to connect to the breakers for protection. So, the PE is not connected to the MCCB; however the neutral (N) conductor may or may not be connected to the MCCB. If your system has many non-linear loads and/or the loads are merely unbalanced, there is possibility of having 3rd harmonics current, as well as the unbalance current flows through the neutral. It may happen that the neutral can carry even more current than the line conductors in this case and it is good idea to connect the neutral to the MCCB so that the neutral circuit is also protected. Use 4P MCCB in this case. Otherwise, you don't need to connect the neutral to the MCCB and 3P MCCB is sufficient without the neutral protection.

Also see these threads:

http://cr4.globalspec.com/thread/53968

http://cr4.globalspec.com/thread/43708

Other useful link: http://www.schneider-electric.com/documents/technical-publications/en/shared/electrical-engineering/protection-devices-monitoring/low-voltage-minus-1kv/ect114.pdf (page p.9 for TNS configuration)

By the by, is this also your post?

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#2
In reply to #1

Re: MCCB application in TNS System

07/22/2010 11:36 PM

The rating of MCCB to be selected based on neutral current (i.e)generally 2 times load phase current.Then protection of the circuit will not be in order.It is therefore better to use 3 pole MCCBs for such circuits and provide neutral busbar connectors ,cables for neutral rated 2 times load current.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Off Topic
Member

Join Date: Jul 2010
Posts: 7
#3
In reply to #1

Re: MCCB application in TNS System

07/23/2010 1:07 AM

Thanks MS,

Considering that the connected loads in the TNS system are of combination of non-linear load( inductive loads, motors, Air conditioning unit, chillers, AHUS, lighting), there is possibility that the load currents in the system will be unbalanced. Please clarify then 4P MCCB main breaker is the best suited. How about installation of load break switch 4P in the TNS system is the load is unbalanced?

Richwin

Register to Reply