Based on the number of poles, the breakers are classified as
SP – Single Pole
SPN – Single Pole and Neutral
DP – Double pole
TP – Triple Pole
TPN – Triple Pole and Neutral
4P – Four Pole
The difference between TPN and 4P (or SPN and DP):
For TPN, protection applies to the current flow through only 3 poles; there is no protection for the current flow through the neutral pole. For the 4 pole breakers, protection applies to current flow through all poles. However when breaker trips or manually opened, all poles are disconnected.
Same type of difference also applies for SPN and DP.
Usage of TP, TPN and 4P in distribution panel:
For any distribution board, the protection system (either fuse and switch or breaker) must be used in the incomer. For a three phase distribution panel, either TP or TPN or 4P can be used as the incoming protection.
TP: It is most commonly used type in all ordinary cases.
TPN: It is generally used where there are dual sources of incomer to the panel (utility source and emergency generator source).
4P: It is used where is the possibility of high neutral current (due to unbalance loads and /or 3rd and multiple of 3rd harmonics current etc).
- MS
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Your explanation is very extended and useful. I used the word switch intentionally, because however they can both disconnect, the function of a breaker is not a switch and a switch is not a (fused) breaker.
Many countries require, besides a main breaker, also a main switch.
TP for delta, TPN for Y (or star) The connection between ground and neutral is in many countries not allowed. Therefore the N is also switched.