Definition of Ir and In in MCCB

07/27/2010 4:10 AM

Please, give to know the differences between Ir and In in MCCB according to IEC recommendation 974-2.

Thank you in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Definition of Ir and In in MCCB

07/27/2010 5:24 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Definition of Ir and In in MCCB

07/27/2010 7:33 AM

Please see this comment from JRaef on another thread: http://cr4.globalspec.com/comment/561110/Re-What-is-the-Ith-Ir-at-MCCB-stand-for

Extract below for ready reference.

Voltage

  • Ue = Rated operational voltage
  • Ui = Rated insulation voltage
  • Uimp = Rated impulse withstand voltage

Current

  • In = Rated current
  • Ith = Conventional free –air thermal current
  • Ithe = Conventional enclosed thermal current

Short -Circuit

  • Icm = Rated short circuit making capacity
  • Icu = Rated ultimate short circuit breaking capacity
  • Ics = Rated service short circuit breaking capacity
  • Icw = Rated short time withstand current

Trip unit

  • Ir = Adjustable overload setting current
  • 1.05xIr = Conventional non –tripping current
  • 1.30xIr = Conventional tripping current
  • Isd = Short time delay tripping setting current
  • Ii = Instantaneous tripping setting current

i am curious. Since you mention IEC 60947-2, why did you need to ask this at all ?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Definition of Ir and In in MCCB

04/28/2020 2:43 AM

Is there a prize for getting it right?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#4

Re: Definition of Ir and In in MCCB

07/23/2020 9:30 AM

Ir: Rated current which is selected based on load current and protection settings.

In: Rated current of MCCB or frame size.

Ex: 160A MCCB with 100A TMD protection. Means 160A frame size of MCCB (In) and it has protection function for Ir:100A where you can either set the protection from 0.8..1.2xIr or fixed (i.e 100A)

__________________
You don't understand anything until you learn it more than one way.
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

kvsridhar (1); PWSlack (2); vijaymail_electrical (1)

Previous in Forum: Capicitor Bank - DG   Next in Forum: Synchronous Machines

Advertisement