Forced-draft Boiler Vrs Induced Draft Boiler

07/28/2010 1:29 PM

I will be replacing a boiler in a Historic Building with a high efficiency LEED certified boiler. The current boiler is located in the basement of an 8 story building. The chimney / flu exhausts to the roof. Building is approximately 100 ft tall not including the basement.

Which type of boiler is recommended:

1. Forced-Draft Boiler

2. Induced Draft Boiler.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#1

Re: Forced-draft Boiler Vrs Induced Draft Boiler

07/28/2010 2:30 PM

What does the Engineer of Record have to say?

__________________
Semper Ubi Sub Ubi
Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#7
In reply to #1

Re: Forced-draft Boiler Vrs Induced Draft Boiler

07/29/2010 11:34 AM

If it is a historical building, I suspect the "engineer of record" might be in a cemetary!

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Reply Score 1 for Good Answer
2
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#2

Re: Forced-draft Boiler Vrs Induced Draft Boiler

07/28/2010 2:38 PM

Most boilers now depend on mechanical draft equipment rather than natural draft. This is because natural draft is subject to outside air conditions and temperature of flue gases leaving the furnace, as well as the chimney height. All these factors make proper draft hard to attain and therefore make mechanical draft equipment much more economical.

There are three types of mechanical draft:

  • Induced draft: This is obtained one of three ways, the first being the "stack effect" of a heated chimney, in which the flue gas is less dense than the ambient air surrounding the boiler. The denser column of ambient air forces combustion air into and through the boiler. The second method is through use of a steam jet. The steam jet oriented in the direction of flue gas flow induces flue gasses into the stack and allows for a greater flue gas velocity increasing the overall draft in the furnace. This method was common on steam driven locomotives which could not have tall chimneys. The third method is by simply using an induced draft fan (ID fan) which removes flue gases from the furnace and forces the exhaust gas up the stack. Almost all induced draft furnaces operate with a slightly negative pressure.
  • Forced draft: Draft is obtained by forcing air into the furnace by means of a fan (FD fan) and ductwork. Air is often passed through an air heater; which, as the name suggests, heats the air going into the furnace in order to increase the overall efficiency of the boiler. Dampers are used to control the quantity of air admitted to the furnace. Forced draft furnaces usually have a positive pressure.
  • Balanced draft: Balanced draft is obtained through use of both induced and forced draft. This is more common with larger boilers where the flue gases have to travel a long distance through many boiler passes. The induced draft fan works in conjunction with the forced draft fan allowing the furnace pressure to be maintained slightly below atmospheric.

AS you see, it's not necessarily the type of boiler but the additional draft accessories you can add to increase your efficiency and SAFETY! Hope this help you to be more informed when you talk to a local, licensed boiler technician.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2010
Location: St Louis MO USA
Posts: 224
Good Answers: 7
#3
In reply to #2

Re: Forced-draft Boiler Vrs Induced Draft Boiler

07/28/2010 8:52 PM

Good answer, thanks for taking the time to share your knowledge. I also agree with Doorman ..... An engineer needs consulted <read paid> for their expertise in a complete and safe installation; public safety being paramount.

__________________
klearzen
Reply
Power-User

Join Date: Nov 2009
Posts: 296
Good Answers: 27
#4
In reply to #2

Re: Forced-draft Boiler Vrs Induced Draft Boiler

07/29/2010 4:02 AM

GA. ID fans have the added advantage that because the boiler is under a slight vacuum there is less chance of dangerous gases leaking into the confined space of a building.

The disadvantage is that they have to withstand hot gases.

__________________
I have no special talent. I am only passionately curious. Albert E
Reply
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#5

Re: Forced-draft Boiler Vrs Induced Draft Boiler

07/29/2010 5:08 AM

You did not say what the square footage of the area you intend to heat is, or the design temperature for the installation. The size of the boiler has everything to do with it.

Whether induced draft or forced draft will be a characteristic of the boiler one purchases, and the venting is pre-determined by the manufacturer.

I suspect this is a very big boiler and someone is going to have to help you.

It is unlikely you will be able to pull this job off without some municipal or State Inspector looking at it, but this does not say you will absolutely have to involve a Professional Engineer. Getting in with a competent contractor may be sufficient.

However, meeting the standards for LEED certification, if that is your intent, is difficult. You would be misguided to only be seeking a LEED certified boiler.

It should be the duty of our highly paid government civil servant Inspectors to assist and guide citizens, within certain limits, however they are can be joined at the hip to the local contractors - sort of a form of corruption.

If you go it alone study the fuel gas codes - NFPA 54 is the most readable. The codes are the best source on this information, although dated because they speak less to pressurized Class III and Class IV vents.

Class II, III, and IV gas utilization equipment cannot be connected to conventional chimneys meant for Class I equipment.

Basically this is how it works:

Class I Nonpositive vent pressure and above the condensation temperature

Class II Nonpositive vent pressure and below the condensation temperature

Class III Positive vent pressure and above the condensation temperature.

Class IV Positive vent pressure and below the condensation temperature.

You see, it is about the vent (or chimney), not the boiler! I am certain you have a Class I vent. Most high efficiency equipment is Class IV.

Good luck!

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2007
Location: South East of Las Vegas just far enough to see the lights but far enough to not hear the coins falling
Posts: 282
Good Answers: 8
#10
In reply to #5

Re: Forced-draft Boiler Vrs Induced Draft Boiler

04/02/2016 8:43 PM

Wrong

__________________
Rule number one; Never ask a question unless you are prepared for an answer that you may not like.
Reply
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#11
In reply to #10

Re: Forced-draft Boiler Vrs Induced Draft Boiler

04/02/2016 9:18 PM

Please explain why I am in error so we all know!

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Reply
Power-User

Join Date: Mar 2007
Location: South East of Las Vegas just far enough to see the lights but far enough to not hear the coins falling
Posts: 282
Good Answers: 8
#12
In reply to #11

Re: Forced-draft Boiler Vrs Induced Draft Boiler

04/02/2016 9:30 PM

There are induced draft Boilers and there are forced draft Boilers. The gentleman asked simply which design would we recommend. Your answer attempted to discredit his question and gave no useable answer. That's all.

__________________
Rule number one; Never ask a question unless you are prepared for an answer that you may not like.
Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#6

Re: Forced-draft Boiler Vrs Induced Draft Boiler

07/29/2010 11:33 AM

LEED does not certify boilers. IMHO, LEED does nothing but charge fees for paperwork, Certificates, and

If the building is Historical, restore the original equipment and make it part of the historic tours that you give.

If you want high efficiency, use solar panels for "free" heating.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8

Re: Forced-draft Boiler Vrs Induced Draft Boiler

02/27/2011 7:16 AM

Dear Guest,

You have not mentioned the capacity and duty meant for the boiler and the exit temp. of flue gas you intend to maintain.

If the capacity is small, your 100 Feet height of the building excluding basement is 30.48 Metres and this height should be sufficient enough to create a good draught, thereby you can save power and hence reduce operating cost.

If your LOCAL LEGISLATION allows, you can have 55 Metres height Chimney, initial cost will be high, operating cost will be less and pay-back period for this chimney may be 3 years.

DHAYANANDHAN.S

Reply
Power-User

Join Date: Mar 2007
Location: South East of Las Vegas just far enough to see the lights but far enough to not hear the coins falling
Posts: 282
Good Answers: 8
#9

Re: Forced-draft Boiler Vrs Induced Draft Boiler

04/02/2016 8:39 PM

Retrofit the old boiler. I love doing that. With your conditions you already will have a changing induced draft situation so forced draft with draft controls are appropriate. What are your emissions requirements? Steam/hot water? What type is the boiler that you are going to remove. Feel free to email me I may be able to help you shine with your customer.

__________________
Rule number one; Never ask a question unless you are prepared for an answer that you may not like.
Reply
Reply to Forum Thread 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Coldspot (2); dhayanandhan (1); Doorman (1); Kaisan (1); klearzen (1); miketheboilerguy (3); RDGRNR (1); Ried (2)

Previous in Forum: Compressor Sizing   Next in Forum: Significance of Carbon in Stainless Steel
You might be interested in: Boiler Services, Boiler Controllers, Cooling Towers

Advertisement