What are the conditions of Synchronizing
Re: Synchronizing
08/09/2010 3:38 AM
There is a good article on this topic in Wikipedia.
Good Answers: 11
Re: Synchronizing
08/09/2010 4:51 AM
If you search this forum you will find a lot of good comments about this. Anyway, see below.
To synchronize AC generators several important factors must be the same.
1- The phase rotation of both generator systems must be the same.
2- The AC voltages of both generators should be equal.
3- The frequency of the incoming generators must match when synchronized ( in practice the frequency of the incoming generator is 1 to 2 Hz higher than that of the online generator. This can be observed with lights or by using a system chroscope.)
4- The speed and output voltage of the incoming generators are slightly higher to prevent it from becoming a load to the system when it is connected.
for more information see here too.
http://cr4.globalspec.com/thread/57066#newcomments
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member
Re: Synchronizing
08/09/2010 5:21 AM
two main condition to synchronize the two different system is
voltage and frequency of the system.
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation