Anonymous Poster

Difference b/w MWP and Calibration Range

08/10/2010 5:14 PM

What is the difference b/w Maximum Working pressure and Calibration range of a Transmitter. e.g. If any one says that ' I have a pressure transmitter installed at Urea Plant having : Calibration Range, 0 - 2500inH2o

and MWP: 0 to 60Kg/cm2.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Difference b/w MWP and Calibration Range

08/11/2010 9:49 AM

What is the meaning of b/w in the sentence, "What is the difference b/w"?

I've seen this before. It makes no sense. What ever happened to spelling words out?

Reply
Participant

Join Date: Jun 2009
Location: Troy, NY
Posts: 4
#2
In reply to #1

Re: Difference b/w MWP and Calibration Range

08/11/2010 10:05 AM

I believe it is a shorthand for between, but yeah I could see where the confusion would come into play not seeing it before.

__________________
dunbam2
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Difference b/w MWP and Calibration Range

08/11/2010 10:30 AM

We have become so lazy that we can't even put forth a little effort to be understood. It's a shame.

Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#4

Re: Difference b/w MWP and Calibration Range

08/11/2010 10:55 AM

2500 inches of water are equal to 6.35 kilograms /cm2. Make that conversion yourself here. As for the difference between calibration and working pressure, consult the users manual for your particular device, (you didn't tell us what it is), and consider the process application. Many apps require a narrow cal range but must withstand wide variances in process value. I hope that's vague enough for you.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply
Anonymous Poster
#5

Re: Difference b/w MWP and Calibration Range

08/11/2010 8:14 PM

Well first of all sorry for the 'B/W' the short hand for between, I must have realized that this is a professional forum... won't happen again :)

secondly as commented by RDGRNR, well this is a remote seal type pressure transmitter(yokogawa) with capillary tube installed at a vessel containing liquid urea. The normal pressure being 3 to 5 kg/cm2. The transmitter specs read, Calibration range: 0-2500inH2o and MWP : 0-60kg/cm2.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: Difference b/w MWP and Calibration Range

08/12/2010 7:50 AM

Thanks for the enlightenment. What "genius" decided that b/w could be substituted for between? And what group of lazy idiots decided that was an acceptable redefinition of the English language?

As you may have surmised, I am from the old school.

Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#7

Re: Difference b/w MWP and Calibration Range

08/12/2010 9:34 AM

Maximum Working Pressure (MWP)
The maximum total pressure permissible in a device under any circumstances during operation, at a specified temperature. It is the highest pressure to which it will be subjected in the process. It is a designed safe limit for regular use. Note: MWP can be arrived at by two methods:
1) designed, by adequate design analysis, with a safety factor and
2) tested, by rupture testing of typical samples.

from
INSTRUMENT ENGINEERS' HANDBOOK: Process Measurement and Analysis
by Bela G. Liptak, 4th Edition

The calibration range is the range over which that the unit can measure and produce a viable output signal.

If the transmitter is for a level application, the values for its scaled range (internally) might not start at zero because of the effect of the fill fluid in the capillaries (and the specific gravity of the medium). For instance, the LRV might be -1188"w.c., the URV might be 742"w.c. in order to produce an output where 4.0ma is at the zero level and 20.0ma is at the upper level.

Reply
Associate
Pakistan - Member - New Member

Join Date: Dec 2009
Posts: 29
#8

Re: Difference b/w MWP and Calibration Range

08/13/2010 1:00 PM

Dear All,

Please Note.

Maximum Working Pressure is the Maximum pressure that any equipment (Diaphragm, Manifolds and Isolating Valve, Flanges and etc.) or instrument can bear (Burst pressure =To explode), that is 60Kg/cm2. I sure that you know the Pressure rating (PN).

And the calibrated range is where you define your 4 & 20 mA points

e.g. it might be possible to set the 20 mA point for a pressure transmitter between 0 - 5Kg/cm2, but you set it at 0 - 2000inH2O or 0 - 3000inH2O and etc.

But by changing the range Please keep in mind maximum and minimum span that your instrument support.

Regard's

AUR

__________________
AUR
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Difference b/w MWP and Calibration Range

08/15/2010 8:19 AM

Logic: there would be no point in having the calibration range greater than the MWP, would there?

Ring-ring. Ring-ring. "Hello? Is that Ffarquar Instruments' technical helpline? Oh, good. I've got one of your NBG30 pressure transmitters rated MWP=100psig, and every time I try to calibrate it 0-250psig, the diaphragm blows out. Can you help?"

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856