Melting Fuse Blocks

08/13/2010 1:28 PM

I have a fuse problem. Three fuse plastic open clip mounted in a disconnect box with Littlefuse JTD 20 fuses for a welding machine. Service is from 480VAC and the disconnect/fuse block is fed from a three phase panel with a 60 amp breaker. This is the second one where one fuse melts out the back opposite the display port (this is one of those fuses with a display to show when blown) and sets the plastic clip on fire before the circuit is interrupted. The breaker never trips. The display port is clear plastic and that is what is melting out the back of the fuse. Big glob of clear plastic out a burned through hole in the back side of the fuse body. It appears as though there is more plastic in the fuse body than just the view port judging on the quantity of melted plastic. What is going on here?

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Melting Fuse Blocks

08/13/2010 2:20 PM

Generally, if a fuse HOLDER melts but the fuse is not clearing, that is the result of a really bad fuse clip connection to the fuse ferrules, in other words your clips or the springs in them are too weak to maintain good contact with the fuse itself. That sets up a high resistance in that connection and even though the current to the load (through the fuse) is low, the heat created in the clip gets transferred to the fuse base and it melts. If the 20A fuses are not clearing, no way the 60A breaker is going to see it!

Are you sure the fuse holders are designed for Class J fuses? Just because you can jam them in there doesn't mean you should! What is the part number of the disconnect? If someone replaced the fuse holder once before, was it with the right one for that fuse or a replacement of the wrong one?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#2
In reply to #1

Re: Melting Fuse Blocks

08/13/2010 2:33 PM

Sorry for all the fuss - this is solved. I trusted my plant electrician a bit too much and fired off this question before I surveyed the site myself. I checked the machine and the builders tag clearly states 46A draw at 480VAC. The elctrician was using the info in a general manual for the line of welders and not reading the machine tag.

What is happening is we are seeing up to 46A across the fuse very sporadically. Actually, we are probably only tapping the low 30A range occasionally, due to the nature of manual tig welding, with much down time in between. The slow blow feature is allowing it heat the fuse up enough to do in the plastic view port, but not take out the fuse immediately.

Yes the clip is sized corrctly - I specified this myself. My first thought was poor connection to the clip, but the hole out the back of the fuse added to the above stated facts convinced me otherwise.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Melting Fuse Blocks

08/13/2010 2:53 PM

Yeah, probably over time the welders learned how they could "tease" the system just enough to keep operating without blowing the fuses. Still, I would think the fuses design should be such that you can't do that.