Additional Switchgear

08/16/2010 1:11 AM

The distance between 11kV switchgear (in switchgear room) and 11/138.6kV grid transformer is around 200meter. which is connected through the single core cable

Question is do I need to provide additional outdoor 11kV breaker between them since the distance is long.

what is the safe distance up to which I can safely connect the switchgear and transformer through cables with out any additional switchgear in between.

It will be appreciable if anyone can help in this regard

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Mar 2010
Posts: 105
#1

Re: Additional Switchgear

08/16/2010 4:21 AM

Dear sms 149,

Better to look into the Electrical Inspectorate guide lines of the state

where you use the power. In Tamilnadu CEIG recommends 75 meters for fixing an

intermediate control to the best of my knowledge.

Manroop.Chennai.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #1

Re: Additional Switchgear

08/17/2010 11:10 AM

I remember that you had earlier also quoted "Tamilnadu Electrical Inspectorate Guidelines" on another query. As I had responded then, I repeat the same answer:

Tamilnadu Electrical Inspectorate - any other State Electrical Inspectorate for that matter - CANNOT have their own codes of practice or guidelines. Every State, I repeat - every state, MUST follow only the Indian Electricity Rules, 1956, as amended up to date.

Can you trace back your answer of 75 meters for an intermediate control to any IE Rule? Or any published documentation to authentiate your answer? Please don't misguide.

As I have told earlier too, I am a "C" License holder issued by Tamilnadu Electrical Licensing Board. And, I am a "C" license holder in its true sense - that I had applied for & got my License after 22 years of experience in the field - after I fully became confident that I can quote any IE Rule at any time. After all, that is what is expected of a "C" Licednce Holder. Isn't it?

And, with the above qualification, I can vouch that there is no IE Rule that I can recall which calls for any such intermediate switchgear, leave alone a certain distance for such a requirement.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: Additional Switchgear

08/16/2010 6:08 AM

There is no requirement for an interposing outdoor 11 KV CB.

Rather than 200M, the transformer could have been at the city supply grid station some KM's away from your HT room.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#3
In reply to #2

Re: Additional Switchgear

08/16/2010 6:15 AM

At 200meter 132kV switchyard is coming up, through which power is exported to the grid which is inside the plant premises . what is the safe distance up to which I can have cable connection between the swgr and transformer.

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Additional Switchgear

08/16/2010 8:53 AM

What is the minimum bending radius of the cable?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Anonymous Poster
#5

Re: Additional Switchgear

08/16/2010 11:07 PM

There is no rule here. There is good engineering practice, there are local engineering standards and there is a thing called a risk assessment. To do the last one answer these questions:

1. What is between the supply end and the transformer that will protect the cable from being damaged?

2. What would happen to the transformer if the cable was to fail?

3. If I open the switchgear CB how can I be sure that the transformer is completely isolated to work on it?

4. What protection relays do I have in place to protect the transformer, cable & switchgear?

I can think of many more questions but you need to start looking at what you have, assess those risks & decide if it is worth buting a CB or taking the risk.

Good luck.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#6

Re: Additional Switchgear

08/17/2010 7:27 AM

In my opinion,you should provide an indoor type 11 kV VCB switchgear within the 132kV Switchyard for facilitating local isolation for maintenance of the Transformer as well as for housing 11 kV side CTs for metering and protection including the vital differential protection of the transformer.You may appreciate that,long control cables between primary and secondary side CTs for differential protection of the equipment is not advisable.The said switchboard can be provided with necessary cable termination panel.The incoming panel of this switchboard and the 11kV terminals of the transformer can be connected through a suitable Busduct.

This arrangement will also help in getting Equipment of higher short circuit withstand ratings as compared to 11 kV Outdoor type equipments.By the way what is the MVA rating of your 11kV/138 kV transformer and what is the value of it's percentage impedence?

Hope this may help.

S PRADHAN

__________________
Learning is a never-ending process.
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#7
In reply to #6

Re: Additional Switchgear

08/17/2010 7:40 AM

transformer rating is of 12.5MVA with %Z of 10%

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#9
In reply to #7

Re: Additional Switchgear

08/18/2010 12:39 AM

With the above parameters of your Transformer you need not go for expensive indoor type 11 kV switchgear in the vicinity of the transformer.Outdoor type 11 kV VCB kiosk complete with necessary CTs & PTs for metering and protection alongwith suitable cable termination facility would be OK.

__________________
Learning is a never-ending process.
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#10
In reply to #9

Re: Additional Switchgear

08/18/2010 1:28 AM

SPRADHAN Can you please elaborate what exactly is the difference between the indoor type 11kV VCB switchgear and outdoor 11kV VCB kiosk. If both type consist of VCB as a switchgear how outtype VCB kiosk is cheaper. thanks for the help

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#11
In reply to #10

Re: Additional Switchgear

08/18/2010 4:20 AM

Indoor type 11kV switchgear board having IP-42 class of enclosure need to be housed inside a switchgear building,where as 11 kV kiosk with VCB & having IP-55 class enclosure can be installed outdoors near the transformer..The Indoor type switchgears are available with short time rating of he order of 40 kA for 3 sec whereas the outdoor type of the order of 21 kA for 3 sec.

You may visit web site of ABB & other manufacturers for further details.

__________________
Learning is a never-ending process.
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#12
In reply to #11

Re: Additional Switchgear

08/18/2010 4:25 AM

Spradhan thanks for the prompt reply then how outdoor type VCB is cheaper than indoor type

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#13

Re: Additional Switchgear

08/18/2010 7:02 AM

Dear sms149,

If you are in India,you have to follow I.E. Rules, 1956. As per clause no. 50 of I.E. Rules, a circuit breaker of requisite capacity is to be installed as near as possible to the transformer. No specific distanced is mentioned; the distance is depended on the requirements, viz; if differential protection is required for transformer(dpending on transformer rating, sanctioned cost of project),operational and maintenace facilities,safety of human and equipment,etc.

Regards,

Manindra

__________________
Manindra
Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); manindra (1); manroop (1); mountk2 (1); PWSlack (1); sms149 (4); spradhan (3)

Previous in Forum: Battery Resistance   Next in Forum: Motor Winding Heater

Advertisement