Anonymous Poster

Emergency Power Distribution-Urgent

08/17/2010 6:51 AM

Hi, Everyone

We are planning that the power of 415V from several Diesel Generators will step up to 11KV switchgear and come back to 6.6KV switchgear through plant MV/LV transformer to start fire water pump for 6.6kV motor.

In this case, Somebody pointed out that this sceme(Step up and Step down) is not feasible and reliable. and also they told us there is a definite possibility that while starting the fire pump, LV diesel Generator will collapse.

I'm waiting any opinion from you.

Thanks,

Electrical Engineer

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Emergency Power Distribution-Urgent

08/17/2010 7:35 AM

In this case you may need to carried out the detailed study using any of the electrical software i.e ETAP/SKM/CYME etc Power flow in our case needs to be checked using the load flow module. I believe there will be a MVAR/Voltage drop issues since u r stepping up and stepping down the voltage through 2 nos of transformer and through the connected cables. Needs to DG capacity for this arrangement. Since u r back feeding the power to the system you need to check whether the transformer is designed for the bi-directional power flow and also check any other issues relating to the vector group mating. Also using transient module you can actually check the motor start issues with this arrangement.

Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#2
In reply to #1

Re: Emergency Power Distribution-Urgent

08/17/2010 7:37 AM

In this case you may need to carried out the detailed study using any of the electrical software i.e ETAP/SKM/CYME etc Power flow in our case needs to be checked using the load flow module. I believe there will be a MVAR/Voltage drop issues since u r stepping up and stepping down the voltage through 2 nos of transformer and through the connected cables. Needs to DG capacity for this arrangement. Since u r back feeding the power to the system you need to check whether the transformer is designed for the bi-directional power flow and also check any other issues relating to the vector group matching. Also using transient module you can actually check the motor start issues with this arrangement.

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Reply
Anonymous Poster
#3
In reply to #2

Re: Emergency Power Distribution-Urgent

08/17/2010 8:04 AM

In this case you may need to carried out the detailed study using any of the electrical software i.e ETAP/SKM/CYME etc Power flow in our case needs to be checked using the load flow module. I believe there will be a MVAR/Voltage drop issues since u r stepping up and stepping down the voltage through 2 nos of transformer and through the connected cables. Needs to DG capacity for this arrangement. Since u r back feeding the power to the system you need to check whether the transformer is designed for the bi-directional power flow and also check any other issues relating to the vector group matching. Also using transient module you can actually check the motor start issues with this arrangement.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #3

Re: Emergency Power Distribution-Urgent

08/17/2010 9:39 AM

Hello Department of Redundancy Department Hello,

I keep getting this echo in my head of undefined acronyms.

DRD: whaw whadda wha wha whaa

Me: What? Could you repeat that?

DRD: What? Could you repeat that?

Me: Very Funny. Oh that's right you have to be redundant.

Me: What about my undefined acronyms?

Me: What about my undefined acronyms?

DRD: You need an acronymectomy.

DRD: You need an acronymectomy.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Emergency Power Distribution-Urgent

08/17/2010 9:48 AM

<...I keep getting this echo in my head of undefined acronyms....>

One can get pills for that, these days.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Emergency Power Distribution-Urgent

08/17/2010 9:15 AM

So why not use a direct diesel drive fire pump instead and cut out all this electrickery nonsense?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Emergency Power Distribution-Urgent

08/17/2010 9:34 AM

Hire a REAL Electrical Engineer to work with Somebody on this project.

Or, do as PWSlack suggests.

Reply Score 1 for Off Topic
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#8

Re: Emergency Power Distribution-Urgent

08/17/2010 10:35 AM

If I were setting up a fire system I would be inclined to use a engine driven FM approved pump system. Several manufactures of these products are approved by Factory Mutual and meet all state and federal codes for fire protection. I would stay away from a generators for emergency power to a fire pump. Not a stable platform for 100 percent run-able condition.

You will find the most fire pump systems are designed to run no matter what, once they are brought on line and have been test to do so.

Reply
Participant

Join Date: Aug 2010
Location: SAMBALPUR,ORISSA ,INDIA
Posts: 1
#9
In reply to #8

Re: Emergency Power Distribution-Urgent

08/18/2010 1:17 AM

Diesel gen should be cused as a standby to tha main power system for auto starting the fire pump in case of power failure only.

__________________
BIBHUDATTA,HINDALCO
Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#10

Re: Emergency Power Distribution-Urgent

08/18/2010 9:50 AM

Dear,

The scheme is rather in efficient, but in principle, 100% possible, subject to proper designing / safety / protections.

We have just recently done the same thing at one of our projects. - when we met with the power crisis.

We ran 500kva * 3 no. DG sets in sync.

Fed the power thru existing PCC in reverse to secondary of Distribution Tr.

Step up to 11kv, fed to the remote sub station - 1000 Mtr. away.

There, we charged the 11kv / 433v transformer, worked well !

But, precaiutions taken.

Specially, you have to over come the starting surge of the transformer. ( which is double the rated current of Tr. )

__________________
Exploring the Science of Electricity
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11
In reply to #10

Re: Emergency Power Distribution-Urgent

08/18/2010 10:23 AM

Efficient? Who said anything about efficient. I presume that there must be some valid reason for indirectly driving a fire pump with a diesel engine through multiple electrical connections but efficiency will certainly not be a reason. The most efficient thing would be redundancy of this facility in some fashion combined with swift egress capability of all occupants and let the place burn to the ground. But to say that this proposal is true requires facts not apparent. (What does this facility do? Where is this facility? etc.)

As somebody else here pointed out, the critical factor for running a fire pump is reliability to operate during the critical condition of a building fire. Adding the multiple power translations of converting mechanical power to various electrical powers and back to mechanical seems to me to be just asking for more possible failure points from a piece of emergency equipment. Adding to my concerns is that the proposed voltages are clearly lethal voltages and this pump will likely be pushing water. Most firefighters I know want to be able to remove all electrical power from a facility easily to reduce hazards.

My point is that fire pumps are an emergency tool. The local emergency responders must know what to expect at any facility. The OP must then construct the backup power for this pump according to the local regulations, what ever they are!

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Reply to Forum Thread 11 comments