Maximum Number of PC Outlets According to BS

08/18/2010 6:09 AM

Hi,

I just need to know what is the maximum Number of PC sockets on 1 circuit according to the British Standards. I've looked for it in the Electricians Guide which is a guide to BS7671, and I didn't find anything.

I am waiting for your answer.

Many Thanks.

Marc

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: maximum number of PC outlets according to BS

08/18/2010 6:41 AM

BS7671 places no limits on the number of socket outlets that can be added to a ring circuit.

BS7671 places a maximum floor area that a ring circuit can supply.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Participant

Join Date: Oct 2009
Posts: 2
#2
In reply to #1

Re: maximum number of PC outlets according to BS

08/18/2010 6:47 AM

You are totally right about what you said.

I've already read what you said, but I was checking if it is stated in any other reference different than the Electricians Guide.

Thank you a lot.

Reply
Anonymous Poster
#3

Re: maximum number of PC outlets according to BS

08/18/2010 7:50 AM

What is the floor area limit for ring circuit i think it is adjusted as per 100w per outlet and voltage drop and other calcs.

regards

Reply
Participant

Join Date: Oct 2009
Posts: 2
#4
In reply to #3

Re: maximum number of PC outlets according to BS

08/18/2010 8:14 AM

The total floor area is 100 m2 per ring circuit

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #4

Re: maximum number of PC outlets according to BS

08/18/2010 10:04 AM

This is correct.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #3

Re: maximum number of PC outlets according to BS

08/18/2010 8:53 AM

This is incorrect.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#6
In reply to #5

Re: maximum number of PC outlets according to BS

08/18/2010 9:14 AM

then , What is correct ?

__________________
Exploring the Science of Electricity
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #6

Re: maximum number of PC outlets according to BS

08/18/2010 10:05 AM

#4 is correct.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#9

Re: Maximum Number of PC Outlets According to BS

08/19/2010 2:58 AM

hello, Go back to the basic of electrical installation. What are your total maximum load in one ring? what is the appropriate wire size for that load? What is the size of the circuit breaker you used? In Short you need to consider the safety side of the system and your machine. Then you can tell the number of outlets you can install.

Regards,

erel

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #9

Re: Maximum Number of PC Outlets According to BS

08/24/2010 2:40 AM

The total maximum load in 1 ring is 32A. The wire size for a ring is 2.5mm2 twin-and-earth. The circuit breaker is 32A. All this is given in BS7671. And BS7671 doesn't care how many sockets are attached to the ring, so long as the floor area each ring services is 100m2 or less. That's in BS7671 as well. So as long as the original poster follows BS7671, all will be well.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10

Re: Maximum Number of PC Outlets According to BS

08/19/2010 10:59 PM

The regulation mentions floor area(50/100m2),wire size(2.5/4mm2),MCB(20/32A) for ring/radial/spur circuits.The Engineer based on his experience can decide the number of sockets in a circuit provided the total leakage current in that circuit do not exceed the tripping current(30mA) of the RCD.As wiring practice varies from nation to nation one should adapt to rules followed in that country.

__________________
pnaban
Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #10

Re: Maximum Number of PC Outlets According to BS

08/24/2010 2:43 AM

4mm2 twin-and-earth is not used in rings under BS7671 as 2.5mm2 twin-and-earth is adequate for a 32A ring.

20A breakers are used for 2.5mm2 twin-and-earth radials.

32A breakers are used with 4mm2 twin-and-earth radials, though it can be difficult to get 2 x 4mm2 conductors into the terminals of some fittings.

<...provided the total leakage current in that circuit do not exceed the tripping current(30mA) of the RCD...>

BS7671 does not contain an algorithm for working this out:

  • If one had 25mA leakage in one ring and 25mA in another, would the 30mA leak trip in a split-load distribution unit support the load, or would it trip [rhetorical question]?

so the concept is absurd.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#13
In reply to #12

Re: Maximum Number of PC Outlets According to BS

08/24/2010 12:14 PM

It is always advisable to load a circuit protected by a RCD to 50% of tripping current(30mA) of the device as computers and other electrical devices manufactured in some countries may have high leakage currents.When testing RCD it should not trip for 50% of its tripping current.Further in power distribution system of an installation there is a maximum allowable leakage current expressed as a (around 5%)percentage of the current rating of the main incoming CB.Some principles have been found appropriate by experience and not by any rules or regulations.

__________________
pnaban
Reply Score 1 for Off Topic
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#17
In reply to #12

Re: Maximum Number of PC Outlets According to BS

10/11/2010 12:07 PM

If the total leakage exceeds 30mA RCD should trip.

__________________
pnaban
Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#18
In reply to #10

Re: Maximum Number of PC Outlets According to BS

10/11/2010 12:34 PM

I've re-read your comment

I'm not sure if you have not read the OP or just trying to prove how smart you are.

You've not only managed to miss the OP question, but you've also proved how stupid you are in the process.

The OP does not ask for protection details, if he's asked this question after reading the IEE guide then he can clearly read the following chapters in the guide on protection of the circuit.

Even when other poeple infom you you've got it wrong, you still come back with outlandish comments.

I suggest you read what you've written

"As wiring practice varies from nation to nation one should adapt to rules followed in that country".

The IEE 17th Edition of the Electrical Regulations is the bible for the electrical industry in the UK, by comforming to the regs you conform to BS 7671 and visevisa.

I made a comment several postings ago on another topic, saying the following.

Open it and prove it, keep it shut and let them think it. Please do the same, you really don't know what you are talking about here

__________________
The square root of nothing is what you make it!
Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#14

Re: Maximum Number of PC Outlets According to BS

10/11/2010 9:19 AM

first of all

those people who have NOT read the 17th Ed IEE reg BS 7671, not worked with 17th Ed, not from the UK need not answer. Second read the regulations and the guide and remember that you can also add as many spur outlets as there are outlets in the ring main.

PW slack has given you the correct answers, so no need for further discussion.

for my Asian friends, no offence intended, but this is a very exact question requiring no generalisations, but a defined answer that only those with experiance and the qualification in the 17th Ed IEE Regs from the UK can answer.

__________________
The square root of nothing is what you make it!
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#15
In reply to #14

Re: Maximum Number of PC Outlets According to BS

10/11/2010 10:48 AM

The "guide to the wiring regulations" by Darrell Locke published by ECA says the total leakage current in circuits protected by a 30mA RCD should not exceed 25% of the rated tripping current(30mA)

__________________
pnaban
Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#16
In reply to #15

Re: Maximum Number of PC Outlets According to BS

10/11/2010 11:33 AM

its a guide, how many ring mains have you installed in the UK?

do you have a current qualification in the 17th Ed of the Elect Regs for the UK? Have you read the 17th Ed?

Being well read is not the same a being well practiced!

__________________
The square root of nothing is what you make it!
Reply
Reply to Forum Thread 18 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); brich (3); harry potter (1); JOHNNYSAAD (2); pnaban (4); PWSlack (6)