08/18/2010 4:35 AM
how to calculate the starting current of 3phase ,55kw motor,400v.
Re: starting current calculation
08/18/2010 5:10 AM
With what starter?? DOL or S/D?
08/18/2010 5:44 AM
s/d
07/25/2015 8:29 AM
You can find information on "www.moeller.es/descarga.php?file=public/142/MSC.DS..."
Regards
08/18/2010 5:11 AM
The locked rotor current is the supply voltage divided by the resistance of the supply cable and the resistance of the winding it is applied to.
08/18/2010 5:56 AM
The motor nameplate will give the FLA (full load amps) or FLC (full load current) of the motor. Another item on the nameplate will give a code letter that tells the ratio of starting current to FLA/FLC. Multiplying these values gives the starting current of the motor. What you need to do is not so much a calculation, but rather a look-up of the motor data.
Good Answers: 11
08/18/2010 6:41 AM
Why dont you use Softwares like Etap, Power Digsilent. You can find easily start current.
Reply Score 1 for Off Topic
08/18/2010 7:23 AM
Hi Guest,
The motors' starting current varies differently from motor to motor, as evidence; you sometimes find two motors of two different manufacturers with the same power ratings, but their starting current is dissimilar… in conclusion, there's no general rule…………
Regards,
Just live and .. Learn!!
08/18/2010 7:51 AM
it is normally taken as multiple of Coded letter on name plate or if you dont have any thing take 6-- 12 times FLA
08/18/2010 9:18 AM
dear ,
You want to find the starting by calculations ? not by refering the manufacturer's guide ?
Motor starting current = V line - line /1.732*Zsc
where Zsc = Impedence of the motor as referred to stator
winding.
Exploring the Science of Electricity
08/18/2010 9:23 AM
Motor starting on DOL
starting current = 4-8 times full load current. Typically taken as 7.5 times FLC
Starting Torque = approx full load torque
Motor Starting on Star-delta
starting current = 1/3 Starting current of DOL = approx 2.5 times FLC
Starting Torque = approx 33% of full load torque
Motor Soft Starting
starting current = depending on setting (>150% onwards of FLC)
Starting Torque = Depending on the current limiter setting may be as low as 6% of Full load torque.
Motor Starting on VFD
Depending upon