GI Strip for Earthing??

08/18/2010 2:46 PM

Hi, I have to replace copper conductor used for lightning rod earthing by GI STRIP, I want to know, what is the Equivalent GI strip dimension for a 95mm2 copper conductor earthing?? Some people advice me 50X6mm GI...but could you please give me a solution for this? Is their any conversion table between Copper and GI??

Register to Reply
Pathfinder Tags: earthing GI strip
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: GI Strip for Earthing??

08/18/2010 8:55 PM

Generally, I don't think there is any conversion tables between Copper and GI. GI is a Galvanise Iron where the iron have different chemical composition. There can be low carbon with high silicon or low carbon with low silicon and there is many grad of iron in the market. Each of the iron grad have different conductivity for the current passing thru it.

In china GI strips is very common used for earthing but there is only one problem. When the GI is grounded in to the soil the tendency is that, these GI plate will get corroded over the years and you will have a very bad earthing for your electrical services or for your lightning rod.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Member
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Aug 2010
Location: New Delhi
Posts: 5
#2

Re: GI Strip for Earthing??

08/19/2010 12:55 AM

u can send me ur email i hv a excel sheet to calculate these things

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#3
In reply to #2

Re: GI Strip for Earthing??

08/19/2010 1:19 AM

please gives us the link it will be very useful

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Participant

Join Date: Aug 2010
Location: Chennai,India
Posts: 3
#7
In reply to #2

Re: GI Strip for Earthing??

08/20/2010 10:09 AM

From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#9
In reply to #2

Re: GI Strip for Earthing??

08/30/2010 2:56 AM

shailesh.tu@gmail.com

please send the excel file..... i have to verify design and i dont have any documents related to it.

also if you find time send data regarding substation earthing design

Register to Reply
Anonymous Poster
#10
In reply to #2

Re: GI Strip for Earthing??

02/14/2011 4:21 AM

What is the weight( Kg) of 25x3mm / meter G I Strip?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: GI Strip for Earthing??

08/19/2010 10:53 AM

S = I x Root 't' / K

Where,

I is the maximum earth fault current anticipated, in amperes

't' is the fault clearing time or the fault duration, in seconds

K is a constant (for GI it is 80 for 1 sec. fault duration and 46 for 3 seconds duration)

S = Cross section of the earthing conductor, in sq.mm

Hope now you can calculate th GI Strip size required

Register to Reply
Participant

Join Date: Aug 2010
Location: Chennai,India
Posts: 3
#6
In reply to #4

Re: GI Strip for Earthing??

08/20/2010 10:08 AM

Thank U Sir!!!

Register to Reply
Anonymous Poster
#8
In reply to #6

Re: GI Strip for Earthing??

08/20/2010 10:17 AM

sir,this is for earthing the 'Building Lightning arrestor'...is there any predetermined standards or calculation ???

Register to Reply
Member
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Aug 2010
Location: New Delhi
Posts: 5
#5

Re: GI Strip for Earthing??

08/20/2010 1:17 AM

give me ur email id i will give u

Register to Reply Off Topic (Score 5)
Register to Reply 10 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); electricalexpert65 (1); nadim7862 (2); Simon Wan (1); sms149 (1); STHALASAYANAM (2)

Previous in Forum: Motor Winding Heater Kit   Next in Forum: Problem With REL 511
You might be interested in: Metal Strip, Stock and Strip Feeders, Strip Heaters

Advertisement