A/C or Ventilation

08/19/2010 8:47 AM

TO ALL,

I have 4200 s.ft of toilet and Locker room on second floor with a height of 9ft..

Should I air condition it or ventilate it as per New York mechanical code /Latest ASHRAE out side air requirements etc.

If so how much CFM for air conditioning or Ventilation. Please guide me as I am confused.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#1

Re: A/C or Ventilation

08/21/2010 2:46 PM

The need of ventilation of the space of such functionality should not even come into qwestion (and by that cannot be eliminated by an air conditioning).

Reply
Anonymous Poster
#2
In reply to #1

Re: A/C or Ventilation

08/23/2010 11:57 AM

Folks,

Need a/c cfm and exhaust cfm required for this bathroom of 4100 s.ft and 8ft clg height.

Reply
Commentator

Join Date: Oct 2009
Posts: 63
#3
In reply to #2

Re: A/C or Ventilation

08/24/2010 2:31 PM

You have to provide at least 4 air changes per hour ie 2200 cfm supply or A/C air and at least 3000cfm exhaust thru exhaust fans keeping the place at a negative pressure for a bath room.

this will suffice. hence the answer