Dear sir,
There any RTD(brand) similar with ifm TA3231
Re: RTD
08/20/2010 1:33 AM
Here are the specs:
Temperature sensors
TA3231
Temperature transmitter
TA
6 mm clamp adapter
Connector
Process connection:
Ø 6 mm
Max. medium temperature
150°C / 302°F (max. 40 min.)
Analogue output
Measuring range
-10...150 °C / 14...302 °F
Made in Germany
Applicationliquids and gases
Electrical designDC
Output4...20 mA analogue
Probe length L [mm]123
Operating voltage [V]10...30 DC
Reverse polarity protectionyes
Overload protectionyes
Analogue output4...20 mA; Rmax: 500 Ω
Pressure rating [bar]50 **)
Accuracy
Analogue output [K]± 0.3
Temperature coefficients (in % of the span per 10 K)< ± 0.1 *****)
Resolution
Analogue output [K]< 0.02
Measuring element1 x Pt 1000, to DIN EN 60751, class A
Dynamic response T05 / T09 [s]1.2 / 3.5 *)
Minimum installation depth [mm]15
ifm electronic gmbh • Friedrichstraße 1 • 45128 Essen — We reserve the right to make technical alterations without prior notice. — GB — TA3231 — 02.07.2009
TA3231
Ambient temperature [°C]-25...70
Storage temperature [°C]-40...100
ProtectionIP 68 / IP 69K, III
Insulation resistance [MΩ]> 100 / 500 V DC
Shock resistance
DIN IEC 68-2-27:50 g (11 ms)
Vibration resistance
DIN EN 60068-2-6:20 g (10...2000 Hz)
EMC
EN 61000-4-2 ESD:4 kV CD / 8 kV AD
EN 61000-4-3 HF radiated:10 V/m
EN 61000-4-4 Burst:2 kV
EN 61000-4-5 Surge:0.5/1 kV
EN 61000-4-6 HF conducted:10 V
Housing materialsstainless steel 316L / 1.4404; stainless steel (304S15); stainless steel (303S22); PA
Materials (wetted parts)stainless steel 316L / 1.4404
ConnectionM12 connector; gold-plated contacts
Weight [kg]0.164
Remarks
¹) to EN50178, SELV, PELV;
referring to UL: For use on a low voltage circuit with overcurrent protection in accordance with UL873 Tab. 28.1 or Imax = 100/Ub (Ub = voltage of the circuit).
*) according to DIN EN 60751
**) only applies to the sensor; for installation in adapters the indications in the adapter data sheet shall apply
*****) In case of deviation from the reference condition 25 ± 5 °C
The values for accuracy apply to flowing water.
Wiring
_________________________________
Many if not most RTDs are 100Ω at 0°C; this one is 1000Ω, presumably for finer resolution. I think other mfrs make equivalent ones, and you can compare the spec sheets. Note that this one is more than just an RTD; it is a transmitter that converts ohms into a 4-20ma DC signal.
Re: RTD
08/20/2010 5:24 AM
For what application u r taking this one .
“Reality leaves a lot to the imagination.”