Anonymous Poster

Starting Method for Centrifugal Blowers

08/20/2010 2:34 AM

Dear Engineers,

For centrifugal blower say 37KW, 90KW, 132KW, RPM 950, and RPM of blower reduced through belts to 345RPM are used to supply humidified air to the paint shop in Automobile industry.

Can someone guide me that variable speed drive or soft starter should be used for motor starter.

Advantages /Disadvantages of using any one these starting method with special emphasis on Electrical Energy Savings.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: Starting Method for Centrifugal Blowers

08/20/2010 8:51 AM

VFD's provide significant energy savings. The variable torque variety is recommended for fans and pumps. Ramp up and down on start and stop to avoid the effect of inrush and belt wear. If you intend to vary the speeds continually or run at less than rated voltage and frequency for lengthy periods consider using inverter duty motors.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: Starting Method for Centrifugal Blowers

08/20/2010 12:58 PM

VFDs only save energy in loads like centrifugal pumps and fans IF THE SPEED IS TURNED DOWN, and only in comparison to other methods of varying the flow. If there is no need to vary the flow rate, a VFD will actually WASTE energy.

Soft starters do not save energy on pumps and fans.

So if you want to consider the benefits of soft starting on the wear and tear of mechanical components and the motor itself, that is a good reason to consider them and in my experience a good enough reason to use them.

VFDs inherently soft start as well, but see above. The only time to consider a VFD as a "glorified soft starter" is when your starting current restrictions are so severe that a soft starter will not limit the current low enough.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Active Contributor

Join Date: Nov 2009
Location: Mumbai
Posts: 17
Good Answers: 1
#3

Re: Starting Method for Centrifugal Blowers

08/21/2010 12:35 AM

Dear Guest, If you kindly come out of the closet and reveal your e-mail id I could mail across a fair comparison of various starting methods. Generally in Asia., the other problems faced with soft starters and VFDs is deterioration of Power Quality - specifically Harmonics. Mainly because filters / chokes may or may not necessarily be installed along with these ''electronic'' devices. I would say that ATS with Korndorfer Closed Transition would be the best bet in such applications. Advantages - High Torque, Soft Starting, Reduced Inrush Current, Zero Maintenance, Marginal Energy Saving etc. Disadvantages - Bit Bulky. Cheers, RRV

__________________
Cheers, RRV
Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#4

Re: Starting Method for Centrifugal Blowers

08/23/2010 4:38 PM

A variable speed drive may allow you to operate at a lower speed than calculated which will save on your electrical consumption. Soft start is not critical on most centrifugal fan applications

Reply
Reply to Forum Thread 4 comments