Volatge Drop Caluculation

08/20/2010 3:24 AM

10 Sqmm 1 Core cu wire is using for 35m long. intial voltage is 220V, what is the voltage drop in that?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: volatge drop caluculation

08/20/2010 4:23 AM

Insufficient information. How many amps (or how many kw/hp) of the motor?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#2

Re: volatge drop caluculation

08/20/2010 4:27 AM

Complete your question by mentioning the total demand load on this cable or total ampere.

by the way, Can you tell me the voltage drop formula?

Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#3

Re: voltage drop calculation

08/20/2010 4:29 AM

It depends on the current

let me google that for you

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
2
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#4

Re: Volatge Drop Caluculation

08/20/2010 6:34 AM

If only 1 core copper wire then voltage drop is zero.(open circuit)

Register to Reply Good Answer (Score 2)
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#5
In reply to #4

Re: Volatge Drop Caluculation

08/20/2010 4:43 PM

I was tempted to give this answer but I didn't know the frequency. If the wire were near a quarter wave length, the voltage drop would be very negative. ;)

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#6
In reply to #5

Re: Volatge Drop Caluculation

08/20/2010 5:48 PM

This can happen, if both lines are of same length or may be in grounded system and in high frequency.

Register to Reply
Participant

Join Date: Jul 2010
Posts: 1
#7

Re: Volatge Drop Caluculation

08/21/2010 12:06 AM

If it is dc voltage then the drop can be calculated by using formula:

Vd = (2*I*R*l*t) / 1000

where,

Vd= voltage drop

I = current

R = resistance of the cable per km

l = length of the cable

t = tempaerature coefficient that can be get from cable manufacturer's catalogue

If it is single phase ac supply then:

Vd = (I*R*l*t) / 1000

Thanks

Register to Reply
Participant

Join Date: Aug 2010
Posts: 4
#8

Re: Volatge Drop Caluculation

08/21/2010 12:51 AM

R = resistivity *length/area

Power = Voltage * voltage / R

Power = V* I

I =P /R

voltage drop =I R

I hope these equations are enough for you to solve the problem

Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#9

Re: Volatge Drop Caluculation

08/21/2010 4:26 AM

Kumar,

Voltage drop is R*I

R resistance of the wire

R= RoxL / S

Ro, resistivity of copper = 0.01724 where L is in meters and S in SQ mm

applying this formula you will get 0.12V drop for each amp flowing in the wire ( assuming it is single phase load, wire lenght = 35x2)

__________________
dont say it, write it
Register to Reply
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#10

Re: Volatge Drop Caluculation

08/23/2010 3:19 AM

Voltage Drop = 1.732 IFL ( R COS Ø + X SIN Ø )

KW ( Maximum Demand)

IFL ( Full Load current of Circuit in Amps.)

L ( Route Length of Cable in Km. )

R ( Resistance of Cable conductor in Ohms/ Km. )

X ( Reactance of Cable conductor in Ohms/ Km. )

COS Ø & SIN Ø can be found in Manufacturer catalogue

Register to Reply
Participant

Join Date: Jun 2010
Posts: 4
#11

Re: Volatge Drop Caluculation

08/23/2010 9:12 AM

there are online voltage drop calculators, i would use them

see mikeholt.com

there are others, google search will find them

Register to Reply Score 1 for Good Answer
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

amarnath.sn (1); anas ahammed (1); Anonymous Poster (1); jg (1); Le_Noble (1); Lspraba (2); ral8452 (1); Randall (1); Tornado (1); Turbotroll3 (1)

Previous in Forum: Starting Method for Centrifugal Blowers   Next in Forum: VFD Energy Saving

Advertisement