Loss of One Phase

08/23/2010 1:07 PM

Hi,

Suppose a 3-phase motor is being fed from a feeder and 300 A flows through each phase totalling 900 A,if one phase gets open(fuse blows,no earth fault) would the other two phase carry 450 A each or some other value.Please answer somebody,thanks.

Sohan

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Loss of one phase

08/23/2010 1:40 PM

A) 300A per phase is still referred to as 300A, not 900A.

B) Phase current for a motor that loses a phase increases because the effective voltage getting to the motor gets redistributed among all the windings and drops by a factor of the Sq. Rt. of 3, or 1.732. So the effective voltage drops to 58% of what you apply. Since motor torque drops by the square of the applied voltage, at 58% effective voltage, the motor torque drops to 33% of what it was. With a constant load, that makes the motor essentially 1/3 of what it is rated for and the load will cause an increase in slip, which creates a corresponding increase in current. The AMOUNT of current increase is totally dependent upon load. if for example the load is less than 1/3 of what the motor is rated for, the current stays within normal range.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Loss of One Phase

08/23/2010 2:06 PM

Additional information from Bussman to add to Jr's post

Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Loss of One Phase

08/23/2010 7:51 PM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#4

Re: Loss of One Phase

08/23/2010 8:36 PM

you would be running at a single phase state which later on burn-out your motor's winding..this is another scenario of unbalanced system..it occured in our factory where our gantry crane motor drive winding shifted colors from insulated red to burnt black..

__________________
take care of your seconds and the minute will take care of itself..
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #4

Re: Loss of One Phase

08/24/2010 10:50 AM

Damn that color shift problem... happens all too often. Someone needs to invent wire that doesn't change color like that...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Loss of One Phase

08/24/2010 1:53 AM

In a correctly-installed system, either another of the supply fuses would rupture, stopping the motor, or the motor overload device woudl operate, doing the same.

There is no excuse for burnt-out motors these days.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#6
In reply to #5

Re: Loss of One Phase

08/24/2010 3:10 AM

Or even before that the single phasing preventer circuit must act.

Provided it is not by-passed as part of cost cutting exercise.

Reply Off Topic (Score 5)
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#9
In reply to #5

Re: Loss of One Phase

08/27/2010 1:11 AM

..the incident occured at the CB terminals, the ones that supplies it...another reason for this was because that system existed longer than i am here...so all i could do is to correct it..

__________________
take care of your seconds and the minute will take care of itself..
Reply
Associate

Join Date: May 2010
Location: RSA
Posts: 33
#7

Re: Loss of One Phase

08/24/2010 3:42 AM

No, the other phase won't carry 450A each.

What will happen is that the load connected to the feeder with a blown fuse won't have electricity to pass through to the load, but the current will be flowing up until the point of the fuse and will ultimately reach infinity (maximum), and if not attended to timeously, it will cause a big damage to the cable that might lead to an explosion.

So to correct this, the fuse should be replaced asap because there is no earth fault as well.By earth fault I am under the impression that you are talking about earth fault relay.

Reply Score 1 for Off Topic
Reply to Forum Thread 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JRaef (2); msamad (1); PWSlack (1); rockraiden (2); wareagle (1); WisdomJD (1)

Previous in Forum: Short circuit Calculation   Next in Forum: Discharging Time of Capacitor

Advertisement