40 Amp 24VDC Reed Switch.

08/24/2010 12:29 PM

I have searched here (Globalspec), there and everywhere, to find a magnetic reed switch capable of directly switching 40 amps @ 24vdc, inductive. and be normally closed.

The limit seems to be 5 amps.

Any suggestions?

__________________
CRTL-Z
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Commentator

Join Date: Jul 2010
Location: South Windsor, CT USA
Posts: 67
Good Answers: 2
#1

Re: 40 amp 24vdc reed switch.

08/24/2010 12:31 PM

Use the reed switch to operate a contactor

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#2
In reply to #1

Re: 40 amp 24vdc reed switch.

08/24/2010 12:39 PM

This switch will interrupt a "ground check" circuit used in mines to monitor the integrity of the equipment grounding circuit, and these requirements are what MSHA (Mine Safety and Health Administration) specifies for any switch in this circuit.

__________________
CRTL-Z
Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#3
In reply to #2

Re: 40 amp 24vdc reed switch.

08/24/2010 12:55 PM
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#4
In reply to #2

Re: 40 amp 24vdc reed switch.

08/24/2010 1:11 PM

If you use a contactor then it will be with in the circuit not the reed switch. If this switch needs to be directly in the circuit some other device will need to be use. I do not think that you will find a 40 amp reed switch. What will activate the switch?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#5

Re: 40 amp 24vdc reed switch.

08/24/2010 1:47 PM

The reed switch needs to act directly on the circuit and be activated magnetically.

__________________
CRTL-Z
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#6
In reply to #5

Re: 40 amp 24vdc reed switch.

08/24/2010 2:12 PM

Boy, there are a lot of "No Sub" requirements here.

Like you, I know of none rated for more than about 4 amp. These guys will custom manufacture, and that seems to be their limit.

Must it really be a reed switch? Mechanical limit switch is out?

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#8
In reply to #6

Re: 40 amp 24vdc reed switch.

08/24/2010 2:47 PM

I am going to "spill the beans" here, or suffer harsh criticism for failure to provide detail

This is an explosion-proof enclosure of limited space that has only enough room left for a snickers bar (mmmmm) sized component. I found that a rare earth magnet is strong enough to penetrate the 3/4" thick aluminum enclosure wall to activate a standard reed switch. I asked MSHA about the ground check system and the requirements are what they gave me. This magnetic coupling would eliminate the expense of having to penetrate the enclosure wall with a mechanical rod or linkage. The direct action would eliminate extra components for which there is no room.

__________________
CRTL-Z
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#13
In reply to #8

Re: 40 amp 24vdc reed switch.

08/24/2010 5:08 PM

Well, try using the magnet to act directly on the relay. it is after all a magnetic solenoid operated switch is it not? maybe attach another magnet to the pole piece to help it out....

__________________
Who is John Galt?
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#15
In reply to #13

Re: 40 amp 24vdc reed switch.

08/24/2010 5:20 PM

You mention of "another magnet" gives me an Idea. Suppose a pair of contacts held closed by a magnet attracted to a thin plate against the interior sidewall of the enclosure, now, if a another strong magnet (like pole) were brought up to this plate from the exterior, would this counter the attraction of the internal magnet to the plate?

__________________
CRTL-Z
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#16
In reply to #15

Re: 40 amp 24vdc reed switch.

08/24/2010 5:25 PM

yes, or you could use a spring to engage the contacts and have a relatively weak magnet (or even a steel plate for that matter) for the external magnet to act upon to overcome the spring force.

Now the question is, can you get something like this "off the shelf" and UL approved? probably not.

__________________
Who is John Galt?
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#7
In reply to #5

Re: 40 amp 24vdc reed switch.

08/24/2010 2:24 PM

Acting directly on the circuit and being in it are not the same. Magnetically operated by what?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9

Re: 40 Amp 24VDC Reed Switch.

08/24/2010 3:20 PM

You cannot get a reed switch that can directly control 40 amperes of current. The magnetic field produced by the 40 amperes of current can easily overwhelm the magnetic field used to move the reed. This is why 5 amps is the limit for this type of device. A reed's contacts could drive another contactor, a solid state contactor or some other solid state device. Very careful considerations must be made of current path geometries.

But I know my limits. Mining equipment controls, because of the combination of harsh conditions and high hazards make it very necessary to know the whole circuit conditions to be able to predict safe failure modes.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#10
In reply to #9

Re: 40 Amp 24VDC Reed Switch.

08/24/2010 3:36 PM

Thanks redfred, I knew there must be an explanation for the limited capacity.

__________________
CRTL-Z
Register to Reply
Guru

Join Date: Jan 2010
Posts: 2446
Good Answers: 60
#11

Re: 40 Amp 24VDC Reed Switch.

08/24/2010 4:04 PM

I almost thought it was a con fancy calling it a Murphy Switch

Engine Protection Products » Murphy Shutdown Products » Murphy Switches, Solenoids, Fuel Valves

117 TATTLETALE® Magnetic Switch
View Details

(117) Used to shutdown 12V through 32V distributor ignition or diesel engines. Breaks circuit when tripped. Opens distributor coil circuit to diesel run device (NC contacts). Automatically disconnects from battery after trip. Contacts 10 Amps 32V DC, 14 Amp fuse. Comes with reset button and is used on the WD300 Series shutdown panel.

Price: $59.95


14 Amp AGC Fuse
View Details

Replacement 14 Amp fuse for the Murphy magnetic switches.

Price: $4.95


518APH Magnetic Switch, 12V
View Details

(518APH-12V) This magnetic switch allows for SWICHGAGE® and/or NC contacts to be wired "closed loop" (in series). Any contact open or SWICHGAGE® contact closed in the circuit shunt trips the 518APH. 12V DC. Contacts 10 Amp 24V, 14 Amp fuse.

Price: $77.95

Engine Protection Products » Murphy Shutdown Products » Murphy Switches, Solenoids, Fuel Valves

117 TATTLETALE® Magnetic Switch
View Details

(117) Used to shutdown 12V through 32V distributor ignition or diesel engines. Breaks circuit when tripped. Opens distributor coil circuit to diesel run device (NC contacts). Automatically disconnects from battery after trip. Contacts 10 Amps 32V DC, 14 Amp fuse. Comes with reset button and is used on the WD300 Series shutdown panel.

Price: $59.95


14 Amp AGC Fuse
View Details

Replacement 14 Amp fuse for the Murphy magnetic switches.

Price: $4.95


518APH Magnetic Switch, 12V
View Details

(518APH-12V) This magnetic switch allows for SWICHGAGE® and/or NC contacts to be wired "closed loop" (in series). Any contact open or SWICHGAGE® contact closed in the circuit shunt trips the 518APH. 12V DC. Contacts 10 Amp 24V, 14 Amp fuse.

Price: $77.95

now if it was me replacing a safety critical protection device, if i was allowed to replace it, i would use a 24 volt 50 amp rated normaly open relay so if magnetic switch fails the circuit goes open. same if wires to relay are cut etc.

in fact i think i would wire the switch to act both ways ie made one circuit open one circuit closed then a change over this would ensure safe operation even if the wire was trapped as the relay would need both a live circuit and an open circuit to be safe.

so it would be doulbe safe, if wires are cut = fail if wires are trapped or crushed =fail.

if wires short out =fail.

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#12
In reply to #11

Re: 40 Amp 24VDC Reed Switch.

08/24/2010 4:50 PM

This ground check circuit continuously monitors the ground path (ground wire) from the main panel to the equipment and trips a circuit breaker in the main panel if this circuit opens. In our application there is a small manually operated control/circuit breaker box inline on the cable, through which this circuit passes. To test this function the mine inspectors must open this box (twelve 9/16 cap screws), and lift the ground check conductor from its terminal. For the benefit of these inspectors, I proposed this magnetically activated switch. If it won't work, it is not a problem for me.

Thanks for the help.

__________________
CRTL-Z
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#14
In reply to #12

Re: 40 Amp 24VDC Reed Switch.

08/24/2010 5:15 PM

Aw heck, why didn't you SAY so! =b

Dude, Killark and others make switch actuators that will mount through o-ring/grommeted holes drilled in cast explosion proof boxes, we use them all the time.

Or you could mount a momentary test switch in the panel with a spring loaded guard to prevent accidental actuation. Not unlike the "test" switch built into residential GFCI outlets.

__________________
Who is John Galt?
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17

Re: 40 Amp 24VDC Reed Switch.

08/25/2010 2:34 AM
  1. The reed switch drives a relay.
  2. The relay drives a contactor.
  3. The contactor switches 40A.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#18
In reply to #17

Re: 40 Amp 24VDC Reed Switch.

08/25/2010 4:48 AM

What you need is a 24v DC relay you dont need a reed switch at all & you can get 40 amp relays off the shelf.

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#19

Re: 40 Amp 24VDC Reed Switch.

08/25/2010 9:55 AM

The situation here is that the control is simply a manually operated motor control/circuit breaker with just enough room for the 4 pole shunt-trip breaker, a terminal strip, a trip capacitor and the wiring. Ther is no room to step down the line voltage (480 and 575v) for a control circuit. The ground and ground conductors pass through a feed-through terminal strip on their way to the equipment. The ground check circuit is effectively a loop comprised of the ground and ground check conductor. if this circuit is opened, the monitoring equipment disconnects the power source.The additional cost of another opening in the ex enclosure for a mechanical switch ( aside from the one for the existing on/off lever) would have to be born by the customer and unless it were mandatory, would not be acceptable.

__________________
CRTL-Z
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#20
In reply to #19

Re: 40 Amp 24VDC Reed Switch.

08/25/2010 10:07 AM

I still think a momentary NC pushbutton in the ground circuit with a guard to prevent accidental actuation is the answer my friend. like perhaps this one. Square-D I am told has a pretty wide selection as well, wider than Curlee.

__________________
Who is John Galt?
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#22
In reply to #20

Re: 40 Amp 24VDC Reed Switch.

08/25/2010 10:35 AM

I completely agree, in fact, in the distant past, MSHA permissible controls had this, (called a "Funka" button after the Guy that developed it) and the vendor for our enclosures will incorporate it for an additional cost.

The problem is, the mines are on extremely tight budget now and because this test button is not mandatory, the mines don't want it.

My idea was to wave a "wand" carried by the inspectors, over a designated spot on the control and trip the ground check.

__________________
CRTL-Z
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#24
In reply to #22

Re: 40 Amp 24VDC Reed Switch.

08/25/2010 11:45 AM

The enclosure would only need an additional drilled hole and an off the shelf push button switch. That can't be any more expensive than your custom reed switch. After all, you'd have to drill and tap at least one hole to mount the reed switch. So cost-wise I think the two are a wash at worst.

__________________
Who is John Galt?
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#21
In reply to #19

Re: 40 Amp 24VDC Reed Switch.

08/25/2010 10:32 AM

That terminal strip does not look like it can handle 40A. are you sure that that is the value you need?

__________________
Who is John Galt?
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#23
In reply to #21

Re: 40 Amp 24VDC Reed Switch.

08/25/2010 10:44 AM

It is a Buchanan brand rated 50 amps @ 600v.

The 40A rating is for "Any interrupting device in the ground check circuit" As mandated by 30CFR (Code of Federal Regulations). In reality, there is never amperage at this level on this circuit, we are talking about laws that were created years ago.

__________________
CRTL-Z
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#25

Re: 40 Amp 24VDC Reed Switch.

04/11/2016 7:51 PM

Use your reed switch to activate on of these Solid State Relays.

Crydom makes a good one.

They are totally encapsulated,only thing exposed is the terminals.

http://www.mouser.com/Electromechanical/Relays/Solid-State-Relays/_/N-ay0ti?P=1z0x15d

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Register to Reply 25 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Bazzer Englander (1); Doorman (1); fixitorelse (1); HiTekRedNek (1); norton850 (1); ozzb (2); peterg7lyq (1); PWSlack (1); redfred (1); Rorschach (6); Unredundant (9)

Previous in Forum: Can Doctor Offices Improve Appointment Punctuality?   Next in Forum: Granddaughter Can't Bring PB&J to School
You might be interested in: Switch Boots, Audio Switch Matrices

Advertisement