4-20 mA Loop Resistance

08/27/2010 5:48 AM

Hi guys i am manimaran. iam facing a problem with selecting intrinsic safe barrier because An analog input 2 wire system. what is the total load of the transmitter which i can connect with the barrier barrier. can drive the transmitter load up to 300 ohms with 15 V DC. how can i check weather the barrier can drive the transmitter or not total voltage required by the transmitter is = the total load is cable drop + 10.5 voltage for transmitter operating

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 4-20 mA Loop Resistance

08/27/2010 7:43 AM

Contact MTL (usual disclaimer) and discuss the problem with them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#2

Re: 4-20 mA Loop Resistance

08/27/2010 8:36 AM

I use one of these.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3

Re: 4-20 mA Loop Resistance

08/27/2010 11:30 AM

The barrier isn't there to drive the transmitter, Captain. The barrier is there to prevent an incendive voltage/current/spark from happening in the hazardous area. By the way, the transmitter is rated EEx i for the gas group, temperature class and zone you've mounted it in, isn't it?

15V into 300ohms is 50mA, so at first glance the system will work.

The cable drop at 20mA is going to be negligible.

__________________
Good moaning!
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#4

Re: 4-20 mA Loop Resistance

08/27/2010 6:40 PM

I don't think 15V is sufficient to drive 300 ohms in the loop.

OP did not, like usual, state a brand or model, but let's take Siemens DSIII as an example. Most quality transmitters provide a supply voltage vs loop resistance ( or maximum loop resistance) chart in their documentation. As an example, below is a Siemens DSIII pressure transmitter supply voltage vs loop resistance chart.

Where the curve crosses the bottom at zero ohms is the voltage required just to run the transmitter, with no load. Note that the Siemens transmitter takes 10.5 volts to turn on and run with zero ohm loop load, for instance, a bench test with a DC power supply connected right across the (+) and (-) terminals to see if the thing turns on.

The OP says his also takes 10.5V to run the transmitter.

If it takes 10.5V to run the transmitter, that only leaves 4.5 volts (15.0 - 10.5) to drive 300 ohms in the loop.

4.5V/300ohms = 15mA. 15mA = 68.75% of 4-20mA full scale.

15V is too little supply voltage. The Siemens chart shows that ~17V is necessary to drive 300 ohms for its DSIII.

It isn't clear whether the OP has included the IS barrier in the 300 ohms number.

Note Rosemount's explicit statement (3051 HART manual) that loop resistance INCLUDES an I/S barrier:

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#5

Re: 4-20 mA Loop Resistance

08/28/2010 6:39 AM

Your question is not very clear.

I can only say that the loop resistance should be 500Ω to convert 20mA to 10V. (since you are talking about loop...)

Otherwise, the litterature of the transmitter should be consulted .....

Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Oct 2007
Location: Sour Lake, TX 30°08'59.68"N 94°19'42.81"W
Posts: 675
Good Answers: 13
#6

Re: 4-20 mA Loop Resistance

08/28/2010 9:01 AM

If the manufacturer says that it can drive 300 Ohm with a supply voltage of 15 V, that means that he (the manufacturer) has considered the maximum voltage drop on the sensing resistor (300 Ohm)

20mA X 300 Ohm = 6V

If it says that 15 V would be enough to drive your line, that means that the electronics of that transmitter will need 9 V in order to function properly.

The barrier has nothing to do with these voltages (unless it has some resistance by itself in which case you should consider the total resistance -300 Ohm- the sum of the resistance of the barrier and your sensing resistor).

__________________
Bridge rule #1: Nobody is as good as he thinks about himself nor as dumb, as his partner thinks...
Register to Reply
Active Contributor

Join Date: Jul 2008
Location: France
Posts: 12
#7

Re: 4-20 mA Loop Resistance

08/31/2010 3:08 AM

Manimaran

Assuming you have a passive zener barrier then the power supply in your loop must be greater than the total of the voltage drops across all of the elements in the loop, ie the transmitter, the safe area load, the cable and the barrier.

If you have a 24V supply, a 250R load (=5V @20mA) and the transmitter takes 10.5V, then this leaves 8.5V (=24V-5V-10.5V) for the drop across the barrier and the cable.

From memory a typical MTL 2 channel barrier has a total voltage drop of 8.1V so you would be close to the limit. Ideally you should increase the power supply to 26V or use a semi-active barrier that will compensate for the voltage drop across the barrier.

If in doubt, contact your local MTL office or download some of the Application Notes from the MTL website (ww.mtl-inst.com)

Steve

__________________
Bad English is Bad for Business
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Carl_E (1); Crabtree (1); indel (1); LAA_Lucke (1); PWSlack (1); RDGRNR (1); steve_y (1)

Previous in Forum: Boiler Drum Level Control   Next in Forum: Some One Explain Poteniometer Operation In Measurements?

Advertisement