Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3

Inter Turn Fault in the Rotor

08/28/2010 2:56 AM

Inter turn fault(short) in the rotor of synchronous machine is identified by voltage drop test. Across each end of rotor winding, a fixed AC voltage is applied.Voltage drop across each pole is measured,Voltage values tabulated,and average of values is calculated. Variation of each individual value from average should be within limits (+/-10%).

But,it is possible,turns may get shorted only when rotor starts rotating,due to centrifugal force acting on rotor. How to identify such inter turn faults,not revealed in tests at standstill condition?

__________________
nvmani
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Inter turn fault in the rotor

08/28/2010 3:58 AM

i am not qualified in this particular area, but i have used the Tinsley Short-turn tester on contactor coils. Very good, even one shorted turn in more than 20000 shows up. As you may be aware, even one turn acts as a shorted secondary of a transformer and will lead to eventual failure in AC coils of contactors.

No problem if the coil is DC.

Which prompts me to ask...won't the rotor in synchronous machines see only DC? If so, what is the problem if there are shorted turns ?

i have used an impulse-voltage based shorted-turn detector for assessing probability of vulnerable insulation...you may get some help at this weblink :Impulse_Tester

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3
#3
In reply to #1

Re: Inter turn fault in the rotor

08/28/2010 12:09 PM

Thank you for the information.The weblink :Impulse_Tester suggests use of 'Winding Turns Tester'. This needs further study.

__________________
nvmani
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#2

Re: Inter Turn Fault in the Rotor

08/28/2010 8:50 AM

A "running short" can be detected with an oscilloscope.

__________________
CRTL-Z
Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3
#4
In reply to #2

Re: Inter Turn Fault in the Rotor

08/28/2010 12:46 PM

Thank you for advising specific solution: A "running short" can be detected with an oscilloscope.

In this connection, IEEE Xplore Digital library refers to a paper:

"Fault diagnosis of the inter-turn short circuit in rotor windings based on wavelet analysis"

This paper appears in: "Electrical Machines and Systems, 2008. ICEMS 2008. International Conference"

"Abstract

A new fault diagnosis method of inter-turn short circuit detection in generator rotor

windings based on wavelet transform is presented. The detection method is based on the singularity characteristics of the induced electromotive force signal of search coil in the air gap. Electromagnetism characteristic of turbo-generator rotor windings is analyzed. Wavelet transform was applied to the detection of the abruptly change signal based on detecting coil method, extracts the fault characteristics of the induced electromotive force signal and excludes noises, thus realize the detection of inter-turn short circuit fault in generator rotor windings. Simulation indicates the wavelet analysis method is suited to detecting fault of inter-turn short circuit in generator rotor windings. "

It will be useful if we can access the full text of this paper.

__________________
nvmani
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#5
In reply to #4

Re: Inter Turn Fault in the Rotor

08/28/2010 1:17 PM

I suppose the paper is talking about injecting an RF signal and observing the reflection. Sort of a "coil radar".

__________________
CRTL-Z
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#6

Re: Inter Turn Fault in the Rotor

08/29/2010 9:34 AM

The winding is held firmly in place by insulation and coatings of varnishes, epoxy and the like (orignally liquid to solidify later), it is therefore practically impossible that centrifugal force acting on rotor to have created such an event.

Hypothetically speaking if the interturn fault does occours due in rotation, the circulating current in the faulty coil section would cause arcing and weld the defective spot, when the machine is brought to a standstill the staus quo is maintained.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#7
In reply to #6

Re: Inter Turn Fault in the Rotor

08/29/2010 10:43 AM

"practically impossible" You evidently, are not familiar with real motor faults caused by damage/deterioration of this insulation system, or you are a member of BP's board of directors.

__________________
CRTL-Z
Register to Reply
4
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#8

Re: Inter Turn Fault in the Rotor

08/29/2010 11:44 AM

Rotor inter turn fault can be detected by analyzing the stator voltage wave form. Due to inter turn fault, the MMF wave form of two poles (assuming it is a 2 pole set, otherwise for that particular pole pair) would no longer remain symmetrical and therefore some second harmonic voltage would be generated in stator voltage. So by measuring the harmonic content presence of inter turn can be detected. For rotors with comparatively larger turns per pole, it may become little difficult and may need quite sensitive analyzer.

Another method is to use RSO (Recurrent Surge Oscilloscope). This instrument sends pulse of electrical signal alternatively from two end and compares the on going and the reflected wave form. In case there is no inter turn fault, then the two wave forms match otherwise not. So by comparison inter turn fault can be detected.

I have described only those method which can be used on revolving rotors where fault occur during rotation and disappear at stand still

In many sets an air gap search is pre-installed (at manufacturing stage) which makes on line checks for inter turn fault by comparing the induced voltage due to each rotor coil and comparing the same with healthy coils.

In a loaded generator having inter turn fault, rotor vibrations also increases which is an indication of earth fault which are load dependent. However, this increase in vibrations can be due to so many other reasons as well.

It is also experienced that some axial magnetization in rotor forging also takes place whenever inter turn Short take place.

Rotor impedance would also change due to inter turn fault. You may measure the rotor impedance at various speeds say at in interval of 200 RPM and then compare the same with the similar values provided by the manufacturer (generally this curve of rotor impedance versus speed is supplied by all the manufacturer.

You may contact me for further details.

Register to Reply Good Answer (Score 4)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Inter Turn Fault in the Rotor

08/29/2010 11:49 AM

Excellent answer, GA.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#10
In reply to #8

Re: Inter Turn Fault in the Rotor

08/29/2010 1:14 PM

GA.

These methods can also be used to detect air gap eccentricity.

__________________
CRTL-Z
Register to Reply Score 1 for Off Topic
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11
In reply to #10

Re: Inter Turn Fault in the Rotor

08/29/2010 1:37 PM

i think you forgot to vote That's my vote up there....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 4)
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#12
In reply to #11

Re: Inter Turn Fault in the Rotor

08/29/2010 2:45 PM

OOPs! Got it.

My limited knowledge of turn defect detection came by accident with a visit to my company's factory in Sweden where they had stators failing due to the pressure required to insert them into the stator housings in production. These defects did not show up in standard tests. The r&d asked me for suggestions. I knew that RF is used by the utility companies for fault detection and could even determine the location for the fault. So, I suggested using RF and it turned out I was "guessing correctly".

I always give a GA to someone who can elaborate on something I mention, even though someone follows me around on CR4, negating my Ga's. I suspect "PP" is sill with us.

__________________
CRTL-Z
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#13

Re: Inter Turn Fault in the Rotor

08/31/2010 4:18 AM

Dear nvmani,

Interturn fault in rotor may be detected instandstill condition by using Electric Motor Checker Instrument. In case of interturn fault, by comparing % inductance value with other good one ( in defective winding the value will be less) interturn fault may be detected; also you may use TDR ( Time Domain Reflectro meter) instrument for detecting interturn fault. At the fault point, a slight inverted loop can be seen in display giving length of the conductor where fault occurs; velocity factor should be chosen very carefully and wisely to get correct result.

It is not possible turns get shorted only when rotor starts rotating, since rotor winding is comprise of conductor,insulation, and liquid insulating vernish which are put in baking oven during manufacturing process and solidify after end of process and cool down.

__________________
Manindra
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3
#14
In reply to #13

Re: Inter Turn Fault in the Rotor

08/31/2010 6:26 AM

Your suggestion on the method for detection of fault is quite informative.

Regarding such scenario of fault only at running condition, an abstract of paper presented during an IEEE conference is quoted below, which mentions of such possibilty.

Abstract

The electromagnetic characteristic and rotor vibration characteristic of turbine-generator are analyzed when rotor winding inter-turn short circuit fault has happened. This paper reveals that exciting magnetic force Ff is constant in a fixed condition whereas the exciting current If increases in case of rotor inter-turn fault. This paper also finds relevant characteristic parameters. Based on the theory, we can get training patterns without doing destructive tests. Then BP (back propagation) neural network can be adequately trained and diagnosis rotor winding inter-turn short circuit. BP neural network is independent on mathematic models and parameters of turbine-generator. Finally practically acquired dynamic experiment data of the MJF-30-6 generator, the results of verification show that the theory analysis is right and the method is efficient and accurate.

Ref: IEEE Xplore digital library "Fault diagnosis of rotor winding inter-turn short circuit in turbine-generator based on BP neural network"

__________________
nvmani
Register to Reply
2
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#15
In reply to #13

Re: Inter Turn Fault in the Rotor

08/31/2010 12:07 PM

what you said "inter turn fault not possible during rotation" may be true for small compact (heat cured) rotors but not for large high speed rotors. I have come across many such cases (what we call flying faults which could be earth fault or inter turn fault) ) during my service period.

Register to Reply Good Answer (Score 2)
Participant

Join Date: May 2012
Posts: 2
#16
In reply to #13

Re: Inter Turn Fault in the Rotor

05/02/2012 1:24 AM

hi, I would want to know if it's possible to detect short circuit with typical tdr like "canoga perkins 1401"? Below a brochure. I appreciate your help.

www.at2.com/downloads/documents/canoga/1401e.pdf

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#17
In reply to #16

Re: Inter Turn Fault in the Rotor

05/02/2012 10:10 AM

It would be necessary to have full mapping (percentage length verses slot number) of the rotor winding to locate the fault. In cylindrical rotors, the length of coil varies due to variable overhang portion. So in order to locate inter turn fault, one should know in which slot (or pole) the fault lies. Otherwise unnecessary removal of slot wedges and then lifting of the coil may result. Generally manufacturer keeps reference wave response curves (with purposely created faults in different slots) for comparison with actual fault.

Register to Reply
Participant

Join Date: May 2012
Posts: 2
#18
In reply to #17

Re: Inter Turn Fault in the Rotor

05/02/2012 12:37 PM

It means that I can detect short circuits in rotors with this tdr tester but if I'd want to know in wich pole the fault lies, I need more information. Right? Thanks for the information and your time.

Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bbaute (2); kvsridhar (3); manindra (1); mountk2 (1); nvmani (3); pcchatur (3); Unredundant (5)

Previous in Forum: Dover Elevator - Hydraulic Pump Shuts Off   Next in Forum: Which Type of Drive Suitable for Paper Mill?

Advertisement