Earthing DC Point

08/29/2010 2:53 AM

1)In a control panel For DC voltage ( 24 VDC) where should Neagtive be connected,should it be connected to Safety Earth Or Instrument Earth .

2) Also how we calculate the size of Safety Earth wire ( From Panel to ground bar)

Regards

Jose

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Aug 2010
Posts: 13
Good Answers: 1
#1

Re: Earthing DC point

08/29/2010 8:00 AM

1. Instrument earth. Safety earth is just that, in the event the box get charged it has a path to ground and trips the breaker.

2. The maximum current of the supply will dictate the earth wire gauge to the ground bar.

__________________
aerospaced
Register to Reply
Active Contributor
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Kuwait / Iraqi border (at present)
Posts: 10
#2
In reply to #1

Re: Earthing DC point

08/29/2010 8:22 AM

2. The maximum current of the supply will dictate the earth wire gauge to the ground bar.

.....................................................................................................................

3. Also the length of the earth wire, it's material construction & it's route (I.E. in the ground, through conduit or strapped to cable tray) will determin its gauge, in an ideal situation you should keep the distance from earthing ground bar to panel as short as possible & make sure you have good clean & tight connections.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#3

Re: Earthing DC point

08/29/2010 8:26 AM

1) Please do not get distracted with the terminology, you have to connect the negative wire strictly in accordance with the wiring diagram provided by the equipment manufacturer, dedicated terminal block and respective terminal number are there in the diagram as well as in the equipment manual.

2) As a safe consideration take fault duration to be one second, accordingly minimum crossectional area of conductor in mm square can be obtained by dividing system fault current with 214 in case of copper conductor or 160 in case of alluminium conductor.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: Earthing DC point

08/29/2010 8:40 AM

as per NEC

ground wire size is dictated according to amp draw on either the load or service

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Earthing DC Point

08/31/2010 3:41 AM

<...2) Also how we calculate the size of Safety Earth wire ( From Panel to ground bar)...>

One uses British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Aerospaced (1); aerotech (1); Anonymous Poster (1); mountk2 (1); PWSlack (1)

Previous in Forum: Shutdown Valve & PST   Next in Forum: Stroke Testing a Process Control Valve
You might be interested in: DC-DC Converter Chips, AC-DC Adapters

Advertisement