Generator IPB Sizing

09/04/2010 9:49 AM

Is there any capacity(MW) limitation to consider Generator

transient reactance or subtransient reacatance to size the SC rating of IPB(insulated phase busduct). Which reactance is more appropriate?

__________________
Partha sarathi Ganguly
Register to Reply
Pathfinder Tags: generator bus duct
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3
#1

Re: Generator IPB Sizing

09/05/2010 3:48 AM

Short circuit rating = Rated full load current / X''d (subtransient reactance)

__________________
nvmani
Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2010
Location: INDIA MUMBAI
Posts: 67
#2
In reply to #1

Re: Generator IPB Sizing

09/06/2010 1:06 AM

There is no MW restriction as such .....................MW rating can be any thing, rather there is voltage restriction. Sub transient reactance shall be used to determine the contribution from the generator

__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Generator IPB Sizing

09/11/2010 10:10 PM

For Bus bar sizing you must always consider the lowest of the three reactances, X"d, X'd & Xd. Obviously, X"d is the lowest among the three and it must be considered for sizing the IPB.

Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); nvmani (1); sms149 (1)