There is no MW restriction as such .....................MW rating can be any thing, rather there is voltage restriction.
Sub transient reactance shall be used to determine the contribution from the generator
__________________
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
For Bus bar sizing you must always consider the lowest of the three reactances, X"d, X'd & Xd. Obviously, X"d is the lowest among the three and it must be considered for sizing the IPB.