Hydrostatic Testing For Waste Oil Tank

09/06/2010 7:38 PM

Hi, I am currently employed as a contractor repairing US Naval vessels and one job i came across requires me to perform a hydrostatic testing. none of my co-workers can really give me any guidance for they have yet to come across such work requiring to do one.

I would really appreciate it if i can get some sort of guidance on how the whole hydrostatic testing process is accomplished.

Here are the information i was given on the job specification;

"Hydrostatically test the piping affected by this work item, using clean, fresh water at 50 (+1/-0) PSIG for suction piping and 68 (+1/-0) PSIG for discharge piping for a minimum of 30minutes."

The location of the testing will be held at a oily water separator room onboard a US Naval vessel.

Thank you for your time.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#1

Re: Hydrostatic testing for waste oil tank

09/06/2010 8:07 PM

Hello Ballasttank26, In essence what hydrostatic testing is, a tank, plumbing or other enclosed combination, that is filled with a Non-flammable non-compressible liquid in a closed system. Then pressurized to an engineered specification. In your example time is included so what your looking for is any leaks be either liquid or gas escaping from the closed system that allows the pressure test gauge to drop from the set point in the time allotted.

Being this is a military job there should be guide lines in proper setup and testing.

hope this helps Charles

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Register to Reply Score 1 for Good Answer
Anonymous Poster
#7
In reply to #1

Re: Hydrostatic testing for waste oil tank

09/08/2010 12:08 AM

Just an enquiry: Need some information - If someone ever heard of Hydrostatic Testing for Cable Cores of subsea umbilicals cables?

Register to Reply
Anonymous Poster
#10
In reply to #7

Re: Hydrostatic testing for waste oil tank

09/08/2010 8:05 AM

You will normally test the hydraulic cores. There should be a procedure available. The cables will need to be able to withstand external water pressure at depth but this is not normally seen as a problem

Register to Reply
Anonymous Poster
#16
In reply to #10

Re: Hydrostatic testing for waste oil tank

09/08/2010 9:01 PM

Thanks - but I need to know further on the testing procedures; and can anyone on this site direct me to a company that can offer this type of "off the shelf" testing pressure vessel or systems? I would really appreciate it. Kind regards.

Register to Reply
Anonymous Poster
#2

Re: Hydrostatic testing for waste oil tank

09/07/2010 4:51 AM

This will involve isolating the tank and connected pipework and sealing, prior to inserting the water and test pressure. Water should be put in the tank to virtually full then air put in to the required test pressure, but check the test pressure plus liquid head pressure will not overstress the tank.

The gauges used should be calibrated to a known and accepted standard. Allow for temperature compensation when checking for pressure drop. During the period of test check all connections regularly for leaks, including the gauge connections. Soapy water brushed on the joints will show any leaks by formation of air bubbles. The EPA have procedures for testing, check their website.

Register to Reply Score 1 for Off Topic
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#12
In reply to #2

Re: Hydrostatic testing for waste oil tank

09/08/2010 9:31 AM

NO!!!!! NEVER EVER use air as the pressurization medium!!!!! Air is compressible and if the tank were to fail catastrophically you will have created a bomb. The goal is to REMOVE as much air or other compressible gas from the system as possible.

__________________
Who is John Galt?
Register to Reply Score 1 for Good Answer
4
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#3

Re: Hydrostatic testing for waste oil tank

09/07/2010 4:58 AM

Just to add to metalSmith's comments. Your heading refers to "waste oil tank", but your text refers only to the suction and discharge piping. It would surprise me if a waste oil tank would be tested to 50 or 60 psig.

Simply put (in the absence of a procedure), you need to spade off the section of piping requiring testing. Fill the line with water via suitable connection and valve and bleed off any air from the highest (or high) points. It is very important that there is no air trapped in the system. If your fresh water supply has adequate pressure then pressurise the system to the specified pressure. If not sufficient pressure then a hand pump can be used for the final pressurization. The calibrated pressure valve should be at the high point in the system if possible.

Once the pressure is established, isolate the system and ensure that the pressure is maintained for the period specified. Carry out visual inspection for leaks.

__________________
If you can't explain it simply, you don't understand it well enough. (A.E.)
Register to Reply Good Answer (Score 4)
Active Contributor

Join Date: Apr 2010
Posts: 22
#8
In reply to #3

Re: Hydrostatic testing for waste oil tank

09/08/2010 5:39 AM

Hey Prof,

Right on the head technically, though i would say 'The calibrated pressure gauge should be .......'

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#9
In reply to #8

Re: Hydrostatic testing for waste oil tank

09/08/2010 7:36 AM

Thanks - that's exactly what I think that I thought I had said - I think . Yes - gauge, definitely gauge.

__________________
If you can't explain it simply, you don't understand it well enough. (A.E.)
Register to Reply
Anonymous Poster
#4

Re: Hydrostatic Testing For Waste Oil Tank

09/07/2010 7:58 AM

thank you all for your help

one last thing, what are the items i should prepare for the hydrostatic test?

Register to Reply
3
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#5
In reply to #4

Re: Hydrostatic Testing For Waste Oil Tank

09/07/2010 8:40 AM

Comments with regard to post #2.

  • Hydrostatic means just that, air is not and may not be the pressure medium.
  • Looking for bubbles is not productive during a hydrostatic test as the medium is liquid.
  • Using air to pressurise is not acceptable in a test that has a hold time specified such as this one. The pressure drop will be negligible even if there is a leak. All air must be removed for the test to be valid.
  • Pneumatic testing should only be done in exceptional circumstances - it can be very dangerous.

Please check whether the intent is to test the tank or just the piping that is being worked on.

__________________
If you can't explain it simply, you don't understand it well enough. (A.E.)
Register to Reply Good Answer (Score 3)
Anonymous Poster
#15
In reply to #5

Re: Hydrostatic Testing For Waste Oil Tank

09/08/2010 12:55 PM

What is the problem if air is trapped while carrying out Hydrostatic Test ?

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#17
In reply to #15

Re: Hydrostatic Testing For Waste Oil Tank

09/08/2010 9:08 PM

Air is compressible, which means it will store energy. if the tank were to rupture, that energy would be released instantaneously, turning the vessel into a huge pipe bomb.

it also means that it is much harder to prove that you don't have a leak because of the spring effect the pressure will go up and down as you pressurize the system and as the temperature changes.

__________________
Who is John Galt?
Register to Reply Off Topic (Score 5)
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#6

Re: Hydrostatic Testing For Waste Oil Tank

09/07/2010 9:30 AM

Ask the US Navy Engineer of Record to provide you a copy of the Hydrostatic Pressure Testing Procedure since they issued the Contract Documents (including Technical Specs). They ought to have a copy handy to give to Contractors, or you may find the procedure in the DIPRA Handbook online (ditto w/ the older CIPRA Handbook).

DIPRA= Ductile Iron Producers Research Assoc.

Also, check the US Army Corp of Engineers (USACE) Guideline Specifications and Engineering Manual for the pertinent Tech Spec regarding performing Hydrostatic Pressure Testing.....they are available online......using an Army spec should really rankle the Navy personnel who should have issued the testing procedure in the Project Manual or as an Addendum Item!

or,

Issue a Request For Information (RFI) to the appropriate US Navy office (Engineer of Record) supervising the ship refit.

Good luck with your project!

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply Score 1 for Good Answer
Member

Join Date: Aug 2010
Posts: 7
#11

Re: Hydrostatic Testing For Waste Oil Tank

09/08/2010 9:02 AM

Ask any of the Navy personnel for a copy of the Joint Fleet Maintenance Manuel (JFMM) volume 5 (Quality Maintenance) chapter 7 (testing Requirements) (I'm not sure of the sub chapter on Hydrostatic tests, think it is 7.5). This will explain how, and reference you to all the documents you will need. (20 years served in the Submarine Force...) Good Luck.

Register to Reply
Member

Join Date: Aug 2010
Posts: 7
#14
In reply to #11

Re: Hydrostatic Testing For Waste Oil Tank

09/08/2010 12:38 PM

Let me clarify... All Navy ships having work performed by outside contractors liaison with a Ship's Sup or the ships 3M coordinator. Find him!!! He knows exactly what the requirements are. It is his responsibility to ensure the work is done correctly and on time. He will use the JFMM vol. 5 as a guide. He will help you identify your boundaries in the ships waste oil system. He will help you identify system gauges that can be used for the Hydrostatic testing. He will show you on the ships prints the "H" and "J" pressures. He will tell you how to do alternative testing for areas that can not be tested with a normal hydrostatic tests. He will show you the time on the prints to hold the test pressure to, and if it needs to be brought up in increments. He will have the documentation that you must sign off. Along with the associated documentation for your test rig or source of pressure, and the gauges and reliefs to document the test. He will show you how to calculate the set points of your relief valves to ensure you do not over pressurize the system. He will coordinate with the ship and get the approval for you to do the test. Use him, abuse him, he is there to make your job run smooth, on time, and hopefully under budget.

Register to Reply
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#18
In reply to #11

Re: Hydrostatic Testing For Waste Oil Tank

09/10/2010 4:10 PM

Hello Cross QA, Here an online home page to JFMM Home Page. With download for offline use.

Hope this helps Charles

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Register to Reply
Power-User
United States - Member - New Member

Join Date: May 2008
Location: Arizona
Posts: 355
Good Answers: 4
#13

Re: Hydrostatic Testing For Waste Oil Tank

09/08/2010 11:16 AM

Good morning Ballasttank26.

Completely isolate the discharge piping, by capping or spading. Allow air to escape from the high point or points. Install an air bleed nipple & (air) valve at the highest point, along with fittings for test water and recorder attachment. Now install nipples and a (water) valve to connect your test water. If the required 68 psig test pressure cannot be achieved with available water pressure, do so with a N2 bottle, then close the (water) valve, remove the N2, and cap the nipple.

After filling with water & purging of all air, close the air valve and install a 24-hour paper recorder. Open the air valve. 68 psig should register on the recorder.

Come back in 24 hours. If the paper chart shows the pressure varied but returned to the initial 68 psig, you have no leaks. If it drops but does not come back to 68 psig, find and repair the leak, and retest. Note: your client may allow you to use 30 minutes.

Repeat on the suction piping, using the required 50 psig. Submit the sucessful paper test charts to your client as proof of the inegrity of the systems.

Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: