Slow Opening Valve

09/07/2010 1:56 AM

Hello,

Last week I posted a question related to the best way of using compressed air vessels. I wish to thank all those who sent their valued opinions on this subject. Now I am inquiring about a suitable valve for compressed air that is able to open slowly, taking at least 10 - 15 minutes to be fully open. Ideally the rate of increase in flowrate with time should be as linear as possible. Size required: 3". The purpose of this valve is to avoid the presence of moisture in the air line when an air compressor is started. Due to the way the compressor management system works, I cannot delay the automatic start of a compressor to allow a refrigerated air dryer to reach it low temperature (approx. 15 minutes). Therefore the compressor has to start with the controller signal, but the air flow will need to take 10 - 15 minutes to peak. This way as the dryer's dewpoint temperature gets lower, the airflow will increase and avoid undue moisture in the system.

A simple solution will be using a few solenoid valves in parallel, each opening at different times, but a single slow-opening valve is more elegant. Can you recommend any unit? Thanks for your help.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#1

Re: Slow Opening Valve

09/07/2010 8:25 AM

A total guess on my part, but can't you just set up your air dryer to start 10-15 minutes before the compressor kicks on, or just leave the air dryer on all of the time?

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Sep 2009
Posts: 20
#2
In reply to #1

Re: Slow Opening Valve

09/07/2010 8:45 AM

Kramarat's comment is quite fair considering (s)he is not aware of the total picture. But the air compressor is situated in a different plant room and it, together with its air dryer will normally be swtiched off. It will only be managed to run by the control system when the main energy efficient compressor fails, or is stopped for maintenance. This will happen so infrequently that it is not feasible to keep the dryer running "just in case". We want to install a failsafe system to maintain low dewpoint even when this 'emergency' compressor will start.

Register to Reply
2
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#3
In reply to #2

Re: Slow Opening Valve

09/07/2010 11:59 AM

If that's the case, why not install a desiccant type air dryer?

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Sep 2009
Posts: 20
#9
In reply to #3

Re: Slow Opening Valve

09/09/2010 4:48 AM

I am not familiar with desiccant type air dryers. do you mean that these dryers do not need some minutes after started, to commence drying?

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#10
In reply to #9

Re: Slow Opening Valve

09/09/2010 5:43 AM

Yes he does.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#12
In reply to #9

Re: Slow Opening Valve

09/09/2010 6:44 AM

These types of dryers are basically plug and play, and yes it would start drying the air immediately, without drawing unnecessary power during down time.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Score 1 for Good Answer
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Slow Opening Valve

09/07/2010 12:30 PM

A motorized ball valve could do this. Either the gearing could be slow or the opening signal could be made intermittent via a time cycling relay.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#5

Re: Slow Opening Valve

09/07/2010 3:28 PM

An instrument control valve such as what these guys sell could be used and pilot controlled by a metering valve and a 4-20 or 0-10 signal to regulate your time.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: Florida
Posts: 940
Good Answers: 28
#13
In reply to #5

Re: Slow Opening Valve

09/25/2010 12:53 AM

I am one of the developers of the PMC electro pneumatic controller line. I had to leave the company to attend to family matters in 2000 and haven't had substantial contact with them since This is a perfect application for a PMC controller. You can "dial" the speed of the system from instant full on down to full off with an amazing range of resolution. There are also optional pneumatic valve sets and configurations that can be used on very large bonnet/piston actuators or controlled remotely. Tuning of the system is a snap. For our advertising, I coined the phrase "If you can tune a radio, you can tune a PMC". Knowledge of PID is not necessary. The controls and their layout were designed to compare to a radios tuning (set point), volume (response speed) and tone (sensitivity) controls. In one of my pneumatic valve qualification tests, the eventual winner operated over 800 million cycles, at 10 cps, without leaking at a rate exceeding 1 bubble per minute at 100 psi. It was still operating satisfactorily at that point but upon inspection of its "innards", one of the three "spider leg" springs was cracked although the other two were working well enough to maintain sealing integrity. Check page 13 of their ad. Tell them BOB sent you.

__________________
Nothing exceeds like excess.
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#6

Re: Slow Opening Valve

09/08/2010 2:24 AM

Just curious, but it sounds like you have no air for 15 mins either way, so why not just plumb the emergency compressor into the main compressor output, so using it's dryer, that presumably is up and running?

(GA to "desiccant")

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Active Contributor

Join Date: Sep 2009
Posts: 20
#11
In reply to #6

Re: Slow Opening Valve

09/09/2010 6:13 AM

Our factory is so big the emergency compressor is located 250 m away from the running compressor (in a different self-contained compressor room with its own dryers, filters, vessel, etc). With the newly-purchased energy-efficient large compressor we no longer need to run this equipment unless for emergencies.

Register to Reply
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#7

Re: Slow Opening Valve

09/08/2010 8:34 AM

In the Navy we had some air compressors that needed to be free wheeling until they got to speed to reduce the motor loading. They used an unloading valve that was actuated by the system oil pressure and sized to close with normal oil pressure.

I haven't been involved with air compressors for years so I don't know if those valves are still around but it wouldn't take a lot to put a timer on this type of valve.

__________________
If you fail to follow through, you will fail.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#8

Re: Slow Opening Valve

09/08/2010 11:41 AM

I think using a proportional valve motor normally used on HVAC systems may or can be adapted, retrofitted or modified to achieve the desired effect or results? This motor valves normally drives the air ducts / vents to close, open and anywhere in-between depending on thermostat settings. It can be engineered to directly linked on a lever type of valve controlling mechanisms.

__________________
vsar
Register to Reply Score 1 for Good Answer
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!