Previous in Forum: Synchronous vs Induction Motor   Next in Forum: How to Transiently Switch 2 Circuits in Opposite Phases at Same Time?
Material for Gland Plate
09/13/2010 12:29 AM
I need to connect 3 single core 300 sq mm copper XLPE armoured cables of 33 KV (E) voltage grade to my 33KV / 1150V, 5750 KVA transformer primary. The system frequency is 50 Hz. Do I need to provide gland plates of non-magnetic material like Aluminium in the transformer primary terminal box & 33 KV switchboard ? Is the eddy current loss in mild steel gland plates due to single core cables at 50 Hz level sufficient to cause heating ?
Re: Material for gland plate
09/13/2010 2:32 AM
<...the eddy current loss in mild steel gland plates due to single core cables at 50 Hz level sufficient to cause heating ?...>
Yes.
Good Answers: 181
09/13/2010 5:06 AM
Ensure the glands and nuts are brass or aluminium
09/13/2010 5:11 AM
Do you mean if brass cable glands are used, mild steel gland plates are acceptable ?
Good Answers: 181
09/13/2010 5:23 AM
You can use steel gland plates but a slot has to be cut between each hole to stop eddy currents. The slot is best filled with epoxy resin to stop ingress of dirt and creepy crawly things.
Good Answers: 170
Re: Material for Gland Plate
09/13/2010 10:25 AM
If you earth the armour of these cables only at one end, I do not foresee any circulating current.
Reply Score 1 for Off Topic
Good Answers: 181
09/13/2010 4:56 PM
Right let's start again from the beginning. If a single core cable passes through an iron loop the loop becomes a CT. So a steel gland plate with no slots or a gland with a steel locknut become CT's carrying the full current of the conductor. Use brass or aluminium to save problems. Circulating currents through armourings deserve a chapter all of there own.
Anonymous Poster (1); electricalexpert65 (1); PWSlack (1); TonyS (3)