Is it possible for a relay to trip due to a near aerth fault, it seems to be the case in our plant when a dissconected relay tripped when an etarh fault was present in a near line.
Re: 50BF relay tripped due to a earth near fault
09/14/2010 2:41 AM
The problem isn't the relay. The problem is the earth fault. Seek it out and eliminate it.
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member
09/14/2010 4:37 AM
yes it is possible for BF relay to trip on earth fault.......and what exactly do u mean by "disconnected relay tripped".........
anyways check out this link basler BF50
shamith gambhir, electrical engineer
Re: 50Bf Relay Tripped Due to an Earth Near Fault
09/14/2010 1:48 PM
More information may throw light on how a disconnected relay may trip. One obvious cause is the uncompensated mutual coupling -This may occur with a parallel feeder which is operating with one feeder out of service and grounded at both ends-The trip impulse may be blocked with say a breaker interlock. 50BF tripping is strange-how it was primed-is it heavy induction or lack of shielding.Perhaps the scheme may be rechecked carefully.50BF tripping can cause wide spread avoidable outage and will require involved analysis to trace out the cause.
Better not count the cent if the risk is many many dollars.