Conduit Fitting Selection

09/14/2010 4:55 AM

Hi

We have one local control panel with bottom cable glands of (M40/M40/M20/M20) This LCP Will be connected to 6.0" Conduit

May I know what fitting or equivalent should we use to connect Multiple cable gland (04 Numbers ) to one common conduit

Note: Space is less we cannot use multiple "T"

Regards

Jose

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Conduit Fitting Selection

09/16/2010 2:50 PM

I'm not sure I am visualizing this correctly, but maybe you could put a wireway below the LCP, and then continue with conduit out of either end of the wireway. As the conduit is 6", the wireway should be at least 8" x 8" x long enough to span across all the cable glands.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#2

Re: Conduit Fitting Selection

09/18/2010 1:44 AM

Yes

Thankss

Register to Reply