132kw 3-Phase Induction Blower Motor

09/14/2010 12:35 PM

A 132kw 3-phase induction motor is run with 2 inverters/VFD. Reading on the main incoming is 100amp and and 150amp in the VFD out - which one is correct? Why? Why 2 inverters have been used instead of one?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: 132kw 3-phase induction blower motor

09/14/2010 12:42 PM

Reading the output current of a VFD with standard hand-held multimeters is a pointless exercise, the readings you get are virtually meaningless. It takes a very expensive meter to be accurate with the harmonic rich output of a VFD. it's best to trust the output current reading of the VFD display, it is already required to calculate that correctly in order to accomplish the motor protection.

No idea why someone would use two inverters. On really large systems there are some inverter mfrs that use parallel output power sections to attain the necessary current, but 132kW is nowhere near large enough to require that. Are you sure you are seeing what you think you are seeing? Are there really two inverters, or are you maybe looking at a 12 pulse inverter with two input transformers and rectifier systems? Much more likely. If someone tried to use parallel inverters using two separate VFDs, that is destined to fail in short order. There is no way to absolutely guarantee that the output firing patterns were identical unless they are both being controlled by a single firing system..

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: 132kw 3-Phase Induction Blower Motor

09/14/2010 8:47 PM

i) The input current is sinusoidal and you get an RMS Value of this wave form as the current reading in your incoming ammeter. The output current is not sinusoidal but a PWM Wave and hence its RMS would definitely not match with that of the input. Hence, you get two different redaings. Go for a true RMS Meter and measure currents at the input & output. They should match (or input current will be slightly higher than the output current).

ii) It could be two 6-Pulse Inverters. This is to reduce the Harmonics. Two 6-Pulse Inverters fed from a three winding Star-Delta-Star Transformer - nullifies the 5th & 7th Harmonics.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: 132kw 3-Phase Induction Blower Motor

09/14/2010 9:05 PM

But on a 12 pulse inverter drive, it is the converters (rectifiers) that are duplicated, not the inverters. They still only have one inverter. That's why I mentioned that he might be mistaken about what he is seeing.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#10
In reply to #3

Re: 132kw 3-Phase Induction Blower Motor

09/16/2010 11:15 AM

thanks for the detailed explanation.will pass on the electrical drawing for the inverters as soon as i get hold of them fro the factory.i am sure you will be able to find out the clue to my problem

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#11
In reply to #3

Re: 132kw 3-Phase Induction Blower Motor

09/18/2010 1:36 AM

I am attaching the start up method i.e. inverter for 132 kW motor. the drawing clearing shows that two inverters are used. Hope you will guide me accordingly.

Register to Reply
Member

Join Date: Sep 2010
Posts: 8
#4
In reply to #2

Re: 132kw 3-Phase Induction Blower Motor

09/14/2010 11:48 PM

Input current should not follow voltage on a PWM Drive: Current will flow only as needed to keep the DC Bus charged. In light load condition, current will flow only at input voltage peaks. As the drive digs in, current will flow at lower (closer to zero volts) points on the input voltage sine wave.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #4

Re: 132kw 3-Phase Induction Blower Motor

09/15/2010 2:55 AM

Agreed! Thanks for correcting me!

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#8
In reply to #2

Re: 132kw 3-Phase Induction Blower Motor

09/16/2010 10:54 AM

will electrical analyzer AR5 or you will suggest some other testing analyzer thanks

Register to Reply
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#5

Re: 132kw 3-Phase Induction Blower Motor

09/15/2010 2:39 AM

Another possibility, do you know if both inverters are on line at the same time? Being that you did not state the function of the motor, I cannot say for sure, but could one inverter be a redundant backup? Where I work, we build many tactical systems for the military, where failure is not an option. So, everything has a redundant backup system. May not apply, just brainstorming.

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#9
In reply to #5

Re: 132kw 3-Phase Induction Blower Motor

09/16/2010 11:11 AM

the function of the motor is used for humidified air for the automobile factory.

capacity (air flow) 4000 meter cube/m. static pressure 1100pa. RPM 530.

shaft power 114 B.kw.

air density 1.198kg/cube meter.

total pressure 1200pa.

total efficiency. 77%

starting method INVERTER.

frequency control range 6 hz-50Hz(50Hz base)

rating continuous'

rated current 250 amp

inspected the site today and noticed that one inverter was on and the 2nd one was not displaying Frequency on the frequency meter which shows that 1 inverter whose frequency is displaced on the panel

Register to Reply
Commentator

Join Date: Sep 2009
Location: INDIA
Posts: 92
#7

Re: 132kw 3-Phase Induction Blower Motor

09/15/2010 3:12 AM

yes i agreed with Jreaf.

Register to Reply