Flue Gas Volume

09/15/2010 10:25 PM

I have a boiler with flue gas volume (at 20 degree C and 1 bar) is 510,000m3/h. How can I calculate the volume at 400degree C and 0.5 bar?

Register to Reply
Pathfinder Tags: flue gas
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Flue Gas Volume

09/16/2010 12:12 AM

P1V1/T1 = P2V2/T2.

(1)(510,000)(273+20) = (0.5)(V2)(273+400) [Assuming bar absolute.]; or

(1+1)(510)(293) = (1+0.5)(V2)(673) [Assuming barg.]

(Said the fly, let us flee; said the flea, let us fly; so they flew through the flaw in the flue.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#2
In reply to #1

Re: Flue Gas Volume

09/16/2010 11:06 PM

(Said the fly, let us flee; said the flea, let us fly; so they flew through the flaw in the flue.)........she sells sea shells along the sea shore . Tounge twister

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply Score 1 for Off Topic
Anonymous Poster
#3

Re: Flue Gas Volume

09/17/2010 3:53 AM

If you want to calculate the gas volume of the exhaust gases, at an earlier stage (400 deg C and 0.5 bar(g), could describe the burner exit), and you want to base your calculation on the gas volume at 20 deg C and 1 bar(Abs), then you should consider also the volume of the water vapour that has been condensated.

Register to Reply