Contactor Between VFD and AC 3 Phase Induction Motor

09/16/2010 11:50 AM

are contactor provided between output of vfd and AC 3 phase induction motor.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#1

Re: contactor between vfd and AC 3 phase induction motor

09/16/2010 12:38 PM

A contactor is not required for functionallity, however if this VFD contols a motor where safety is a concern two sets of contactors may be required for Safety Category 3 European Standard EN954-1 (depends on your local codes).

Newer drives are being built with a safe off functionallity that does away with the two sets of safety contactor requirement. (depends on your local codes).

One thing to remember, without a contactor between the VFD and the motor there may high voltages present at the motor leads even if the VFD is not running and can cause danger to personel when the equipment is not locked out. (depends on the drive)

Elroy

__________________
Knowledge makes what was impossible, seem easy.
Register to Reply Good Answer (Score 3)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: contactor between vfd and AC 3 phase induction motor

09/16/2010 2:13 PM

Modern transistor PWM VFDs don't leak. That was only an issue for older Current Course Inverters that used SCRs on the output. hardly anybody does that any more.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Contactor Between VFD and AC 3 Phase Induction Motor

09/16/2010 2:17 PM

Other than the safety issue mentioned above, it's generally not a good idea to put a contactor or any air-gap device on the output of the VFD because it is really easy to cause damage to the VFD transistors by opening the contactor under load. In a Safety situation you would be willing to sacrifice the VFD to protect life and limb, but for every day use it's considered a bad practice and most VFD mfrs will advise against it. If you need to do it, make sure you have control interlocks that do a Base Block shut down of the VFD before the contacts can open.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Feb 2010
Posts: 164
#6
In reply to #3

Re: Contactor Between VFD and AC 3 Phase Induction Motor

09/18/2010 1:41 AM

I am attaching the start up method i.e. inverter for 132 kW motor. You will notice that contactor is used between inverter and motor, where as it is recommended that contactor should not be used in the ckt. moreover you will notice that 2 inverters are used instead of 1 inverter.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: Contactor Between VFD and AC 3 Phase Induction Motor

09/19/2010 12:54 AM

From the looks o that, the Inverters are there for redundancy and the contactors isolate one inverter from the other. No problem with that arrangement really, other than the cost... Someone must have had some bad experiences with VFDs in the past and insisted on a back-up unit being installed and wired ready to go just in case one failed. Is the process this is controlling extremely critical?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#8
In reply to #7

Re: Contactor Between VFD and AC 3 Phase Induction Motor

09/19/2010 3:59 AM

yes! the process seems to be critical as the humidified air is used in the paint shop of the automobiles and they cant afford 132 kw blower motor to stop at any cost as this blower is suppling the humidified air to the booths and certain temperature has to be maintained when painting of the automobiles is in progress.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9
In reply to #8

Re: Contactor Between VFD and AC 3 Phase Induction Motor

09/19/2010 9:21 PM

But they still only have one blower and one motor! If it were that critical, complete redundancy would be my choice. That way you can also alternate the motors so that wear and tear is evenly distributed and each one lasts longer. This seems like a half-baked attempt.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Contactor Between VFD and AC 3 Phase Induction Motor

09/17/2010 4:37 AM

If the same VFD is controlling more than one motor, then one might have to go for individual contactors at the out of the VFD to each motor to enable to isolate only one motor for any maintenance/inspection, etc.

Otherwise, for stand-alone VFD-Motor set-up, output side contactor is not necessary. It would rather create more harm (switching surges) tahn help. I would prefer an input isolation contactor instead.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: Contactor Between VFD and AC 3 Phase Induction Motor

09/17/2010 10:56 AM

I agree, but there are specific safety regulations and/o corporate practices that insist on an output contactor, maybe because if residual energy storage in the capacitors. I actually don't like it myself, I'm just acknowledging that the requirement exists.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#10

Re: Contactor Between VFD and AC 3 Phase Induction Motor

09/30/2010 12:34 PM

Mr.Salahuddin Zia - After having gone through all your threads it seems that you are out there on Energy Audits (particularly electricity) and it seems that you have little experience in this"Energyv Audit" field and practically none in the boiler/steam field. You are out requesting electricial data / reports from members on hatchery/gum/etc., and very recently you started a couple of inter-related energy efficiency threads. Basically you are getting your homework done from us.

Who are you? What is the name of your Company?

I will appreciate you being really honest in your reply before anyone of us proceed further.

If you do not wish to disclose the name of your Company then it will not be difficult to find out too.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply