Anonymous Poster

SBW vs. GSBW Cable

09/17/2010 2:01 AM

We received 2P x 1.5 SQMM with SWB (steel wire braid) whereas our specification says that GSWB (galvanised steel wire braid) . Is it OK?

Also cable specs says flame retardant required we recived cable outer sheeth with flame resistance property is it ok?

Thanks in advance to spend a little time for me.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#1

Re: cable -urgent

09/17/2010 3:05 AM

When two different metals come in contact and moisture plus contaminants like soot is present to form a week electrolyte, that produces corrosion also called galvanic corrosion.

Change of specification from coated steel to bare can be a consideration if you have to terminate the armour outdoors in a metal gland or even indoors if your area is a tropical / humid climate.

Argument about flame retardant and flame resistance is meaningless, you have to check if the cable sheathing conforms to the relavant IEC, BSS etc. standards specified to the manufacturer/supplier.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Anonymous Poster
#2
In reply to #1

Re: cable -urgent

09/17/2010 3:19 AM

can you tell me that only IEC- 60331 is compatible with fire resistance or IEC-60332 also coplies to fire resistance

As i know IEC-60332 complies to flame retardant

For Low smoke low halogen cables ...IEC60331 and IEC-60332 are compatible?

as per our specs- IEC-60331 given only for flame resistance

IEC 60332 given only for flame retardant

Thanks for the previous reply

i will be grateful if anyone reply this mail also.As could not able to collect IEC standards.

Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3
In reply to #2

Re: cable -urgent

09/17/2010 5:28 AM

dear,

Yes.

Flame resistance does not mean Flame retardant.

Both materials are different.

Any how, Normally manufacturers use galvenised wire for braiding / armouring.

So, there may not be ant apprehensions in acceptance of the material. You may just check the sample of the cable.

__________________
Exploring the Science of Electricity
Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#4
In reply to #3

Re: cable -urgent

09/17/2010 5:30 AM

Further,

Flame resistance cable is superior to flame retardant .

As, Flame resistant cable will not allow to ignite the flame at all.

Where as, flame retardant cable will ignite the flame, but shall be extinguished quickly.

__________________
Exploring the Science of Electricity
Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#5
In reply to #2

Re: cable -urgent

09/17/2010 7:43 AM

IEC 60331 and IEC 60332 both relate to TESTS to be carried out on cables. For vital emergency services during the fire, fire resistance cables are designed to maintain circuit integrity, however at present in cable industry; Fire Retardant, Low Smoke halogen fire (LS2H) or low smoke fume (LSF), fire resistance cables are all Fire Retardant and Fire Resistance cables.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6
In reply to #5

Re: cable -urgent

09/17/2010 2:14 PM

Just to clarify some terminology used in this thread:

Flame Retardant: Flame Retardant is the property of the substance, or a treatment applied to a material, whereby the propagation of a flame is markedly retarded. The insulation and jacket of flame retardant cable is made of the substance having flame retardant property so that the cable eliminates the fire propagation.

Fire Resistant: Cable can withstand and continue service in fire. A fire resistant cable is suitable for use in critical and emergency signal paths, such as, fire alarm systems or emergency lighting.

LSZH (or LSZH or LSHF): This type of cable uses insulation and sheathing materials that do not emit more than 0.5% Halogens (poisonous gases in particular hydrogen chloride), and have reduced smoke emission properties. The IEC60754 specifies a maximum limit of 0.5% halogen acid shall be emitted in a fire for a cable to be classed as being of the LSZH type.

LSF: It produces low smoke but is not totally halogen free (can emit up to 22% hydrogen chloride). Basically it is an improved PVC cable. Obviously, it is less expensive than LSZH.

Halogens (Chlorine, Fluorine, Bromine and Iodine) are cheapest flame retardant material and are used with cable insulation (such as Chlorine in PVC) to increase its flame retardant property but cables made flame retardant by halogens produce smoke and toxic gases when it burns. Hence, the special insulation and sheathing materials are used in LSZH or LSF cables so that it is flame retardant as well as produces low smoke and low toxic gases. In most cases, the LSZH or LSF cables are flame retardant. However, they always may not be flame retardant.

Reference:

http://www.addison-tech.com/product/fiber-resistant.htm

http://www.drakact.com/dtc/files/Infoblatt_2005_01_Flammwidrigkeit_e.pdf

http://www.fscables.com/pdf_info/LSHF.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#7

Re: SBW vs. GSBW Cable

09/17/2010 10:56 PM

Is it ok? Ok for what? You really don't give us much to go on to give you an answer do you?

you don't say what environment it needs to operate in or anything about what it is being used for or how. the devil is in the details and you gave us none of them.

__________________
Who is John Galt?
Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); harry potter (2); mountk2 (2); msamad (1); Rorschach (1)